correct math for energy metering
how correctly make math for my power meter device's data:
I receive 2 byte sighned integer 2083 kWh. But real is 208.3kWh. If I use value myltiplayer for modbus mapper I have only integer part - 208 kWh.
If I just divide 2083 /10 anyway I have only 208.
So how correctly convert value to floating point to have integer and 2 digits after point for more accurate power metering data??
Alex
Set bus_datatype to float32, value_multiplier to 0.1. Then make sure that your object also has 4 byte floating point data type.
Hi Admin,
unfortunatelly such way not working for me :Sad
In attachment pictures with different datatypes I used with modbus LM reader... As I think my device - Gavazzi PM 340 gives out int32 format - as example 2341 (this is L1 phase voltage, real should be 234.1V). If I use float32 type I see something wrong...
But from documentation - I see smething not correct, in real received data should be divided by 10 not multiplied..
300001 0000h 2 V L1-N INT32 Value weight: Volt*10
What you can recommend?
Alex
.pdf   3-phase Modbus serial protocol EM and ET-rev.2.11.pdf (Size: 164.62 KB / Downloads: 16)
Set datatype to int32
Daniel,
big thanks, I did so. But I receive only integer part of whole meaning. But customer wants see also data after point - I need as example have 243.1. But I don't know how correctly rearrange received 2341 int32 type to 234.1 (float32??). If I just divide 2341 /10 I have only integer part = 234 (customer wants see 234.1 Sad )
In simple math foolish question, but not so easy with datatype formats for me Sad
Alex
datatype and bus_datatype are two different things. Set datatype to int32 and bus_datatype to float32. First one is modbus dpt and second KNX
Daniel,
so bus datatype should be : 13. 4 byte signed integer = int32 ??
Alex
No Smile
"datatype": "int32", "bus_datatype": 14,
http://openrb.com/docs/modbus.htm
AAA my brains Smile
Anyway I am wrong somewhere..
part of my .json file:
    "product_code": "Gavazzi EM-340",
    "mapping": [
            "bus_datatype": 14,
            "address": 0,
            "type": "register",
            "units": "V",
            "value_multiplier": 0.1,
            "name": "Voltage L1-N",
            "datatype": "int32"
            "bus_datatype": 14,
            "address": 2,
            "type": "register",
            "units": "V",
            "name": "Voltage L2-N",
            "datatype": "int32"
            "bus_datatype": 14,
            "address": 4,
            "type": "register",
            "units": "V",
            "name": "Voltage L3-N",
            "datatype": "int32"
            "bus_datatype": 14,
            "address": 6,
            "type": "register",
            "units": "V",
            "name": "Voltage L1-L2",
            "datatype": "int32"
but at modbus mapper again formats not correct.. Maybe because from register 0 I need read 2 words by length??
Alex
This is already happening.
Do you have any errors?
No, no any errors.
I think it could be modbus speed, but I use middle - 38.4 and now only one device. So may be just try to do changes mathematically? By the way, what is last modbus lua library? I using this:
genohm-scada-modbus 20180822
You need to set correct read_swap field value. Use RTU read test to find correct swap value when reading registers using int32 data type.
Admin,
thanks, but how correctly to add read_swap to .json:
Is it right way: "read_swap": "0xCDAB",
And where in between I should insert additional arguments??
Alex
0xCDAB is swap w which is the default, you probably need swap type n.
Here you have read correct value via read test:
[Image: attachment.php?aid=1367]
{     "product_code": "Gavazzi EM-340",     "read_swap": "n",     "mapping": ...
After updating the profile you need to delete the device and create it again.
Thanks,
will check today later.
Alex
