Writing to multiple objects
Hello
Is there a way for me to write for example a "3" to several objects in one script? Se attatchment.
Let say I tag all the objects I want to adress with "Modus", and I want to write this if another object (Lets say 32/0/3) is "True".
Like this:
objs = grp.tag('my_tag') objs:write(123)
Why won't it write the value of the group-adress 32/1/10 to tag "Modus"?
This is wrong. You should add tag 'Modus' to object 32/1/10 and instead of the address in your script put a value you want to write. If you want to write to single object then use single command.
But the value i want to write comes from group-adress 32/1/10
I am trying to write the value that 32/1/10 holds to all objects with the tag "Modus".
The value 32/1/10 is being written from a PLC via BACnet.
Do it like this
value = grp.getvalue('32/1/10') objs = grp.tag('Modus') objs:write(value)
Then you need an event script, not a resident script:
value = event.getvalue() objs = grp.tag('Modus') objs:write(value)
christian.troen@haaland.no
Hi.
In the heading you write that you want all object with tag "Modus", to recive the value of "3" if (32/0/3) is True. If this is still what you want, then you can use this as Event-based script.
This sends the value "3" to all "Modus" taged objects, but only when 32/0/3 gets True.
value = event.getvalue() objs = grp.tag('Modus') if value == true then objs:write(3) end