BOOSTER CONDIZIONATO
good morning everyone, I ask for help for this script that I have tagged for the control of two variables "setpoint" and "temp", the goal is to activate a booster when the condition occurs ("delta" <= "setpoint" - "temp" ), where the "delta" is chosen by the system manager.
When changing the "setpoint", it is verified that the mathematical condition is active (sometimes for 1 pulse, other times for a few seconds) and then deactivates the two output groups. There is no perfect answer to the mathematical condition that I believe works perfectly by reading the impulse / temporary activation of the outgoing groups from the bus monitor.
value_1 = grp.getvalue ('7/0/0') - summer / winter
value_2 = grp.getvalue ('3/3/2') - set speed
value_3 = grp.getvalue ('6/0/2') - maunal command
temp = grp.getvalue ('2/2/7')
setpoint = grp.getvalue ('2/2/17')
delta = grp.getvalue ('3/1/202')
if (delta <= (setpoint-temp)) and (value_1 == true) and (value_3 == false) then
grp.write ('2/0/92', true)
grp.write ('6/0/92', value_2)
  grp.write ('2/0/92', false)
  grp.write ('6/0/92', 0) - byte to 0
I don't fully understand your question. What exactly is not working for you? You can set poll interval for an object to send KNX read request periodically if data is not sent by a KNX device automatically.
First correct your comments as they part of the code now.
value_1 = grp.getvalue ('7/0/0') -- summer / winter value_2 = grp.getvalue ('3/3/2') -- set speed value_3 = grp.getvalue ('6/0/2') -- maunal command temp = grp.getvalue ('2/2/7') setpoint = grp.getvalue ('2/2/17') delta = grp.getvalue ('3/1/202') if (delta <= (setpoint-temp)) and (value_1 == true) and (value_3 == false) then grp.write ('2/0/92', true) grp.write ('6/0/92', value_2) else   grp.write ('2/0/92', false)   grp.write ('6/0/92', 0) -- byte to 0     end
(06.03.2020, 16:26)Daniel. Wrote: First correct your comments as they part of the code now.
daniel, in the translation of the texts the second indent is missing, in fact in the script the text is correctly preceded by the double - -
(06.03.2020, 15:28)admin Wrote: I don't fully understand your question. What exactly is not working for you? You can set poll interval for an object to send KNX read request periodically if data is not sent by a KNX device automatically.
the script does not execute the command stable command on the outgoing objects of the condition, sometimes it works other not!
sorry, having put the TAG on each object, just one of these changes to relaunch the script ?? if I put the TAG only to the three objects "delta" "setpoint" and "temp" the script is activated only when these 3 objects change ??
Add log for the conditions to see if the condition was meet
how do I send a video of what's going on?
upload it somewhere and drop a link
(09.03.2020, 13:31)Daniel. Wrote: upload it somewhere and drop a link
good evening daniel,
whenever possible I need support to solve this small but incessant problem:
value_1 = grp.getvalue('32/1/41')
value_2 = grp.getvalue('3/3/1')
if (value_1==true) then
grp.write('2/0/91', true)
grp.write('6/0/91', value_2)
os.sleep(60)
grp.write('2/0/91', false)
grp.write('6/0/91', 0)
from the bus monitor I keep having the addresses cyclically, to reduce the traffic I also put the "os.sleep (60)" but it doesn't work, every second it sends me on the bu sil value at 0 / off of these two addresses:
grp.write ('2/0/91', false)
grp.write ('6/0/91', 0)
Send backup to PM
(16.04.2020, 07:22)Daniel. Wrote: Send backup to PM
good morning Daniel, let me know if you received it in the attachment, thanks.
.gz   Project-LM_PIOVESAN-2020.04.17-09.38.tar.gz (Size: 1.6 MB / Downloads: 6)
Where is this script?
(17.04.2020, 08:23)Daniel. Wrote: Where is this script?
value_1 = event.getvalue()
value_3 = grp.getvalue('7/0/0') --estate / inverno
if (value_1==true) and (value_3==true) then
[color=rgba(0, 0, 0, 0.87)]you can find it in the event scripts (3/0/206)[/color]
good morning Edgard,
I ask for help for this script as it happens that the value 0 of the two group addresses 2/0/91 and 6/0/91 are sent to me on the bus
value_1 = event.getvalue ()
value_2 = grp.getvalue ('3/3/1')
value_3 = grp.getvalue ('7/0/0') - summer / winter
if (value_1 == true) and (value_3 == true) then
grp.write ('2/0/91', true)
grp.write ('6/0/91', value_2)
otherwise
grp. write ('6/0/91', 0)
otherwise
I discovered the problem that I created!
I need the way to activate a script only if there is a specific condition, I give an example:
in the summer run the script "x"
in winter run the script "y"
please help me?
please help me?
You already have this in your script:
value_3 = grp.getvalue('7/0/0') if values_3 then   -- do something when value_3 is TRUE else   -- do something when value_3 is FALSE end
thanks Edgard,
the scripts are 2 that answer on the same address, both are started by the comparison and generate two obviously contrary results, one rightly inhibits the other, if it were possible to activate the Winter in Winter script and the Summer in Summer script would be perfect.
ESTATE
value_1 = grp.getvalue('7/0/0')
value_3 = grp.getvalue('6/0/1')
temp = grp.getvalue('2/2/1')
setpoint = grp.getvalue('2/2/11')
delta = grp.getvalue('3/1/201')
if (delta<=(temp-setpoint)) and (value_1==false) and (value_3==false) then
grp.write('3/0/206', true)
grp.write('3/0/206', false)
INVERNO
if (delta<=(setpoint-temp)) and (value_1==true) and (value_3==false) then
Try this:
value_1 = grp.getvalue('7/0/0') value_3 = grp.getvalue('6/0/1') temp = grp.getvalue('2/2/1') setpoint = grp.getvalue('2/2/11') delta = grp.getvalue('3/1/201') out = false if not value_3 then   if value1 then     out = delta <= (setpoint - temp)   else     out = delta <= (temp - setpoint)   end end grp.write('3/0/206', out)
(20.04.2020, 06:54)admin Wrote: Try this:
Thanks Edgard,
before inserting your new script for which I am grateful, I would like to better understand what the result will be as, with this formula, I seem to understand that the address 3/0/206 is sent only if the two conditions are verified in turn filtered from summer / winter.
I must point out that the 3/0/206 triggers an additional event script:
WINTER
SUMMER
if (value_1 == true) and (value_3 == false) then
grp.write ('6/0/101', value_2)
grp.write ('6/0/101', 0)
Like this:
event_value = event.getvalue() summer = grp.getvalue('7/0/0') -- summer / winter if event_value then   out_value = grp.getvalue('3/3/1') else   out_value = 0 end if summer then   out_addr = '6/0/91' else   out_addr = '6/0/101' end grp.write('2/0/91', event_value) grp.write(out_addr, out_value)
Your current script will fail with an error because you have single "-" instead of double dash for a comment.
This line will be evaluated an arithmetic expression "X = A - B / C"
(20.04.2020, 11:17)admin Wrote: Like this:
Thanks Edgard,
I would never have been able to independently write a script of this type, unfortunately I never studied the programming code, I am self-taught and unfortunately I don't even know English.
I notice that there is no need to write for example:
if event_value = true then
but what you wrote is enough:
in event_value then
this means that when 7/0/0 = 1 (= summer)
(= winter) ??
event_value = event.getvalue ()
summer = grp.getvalue ('7/0/0') - summer / winter
if event_value then
out_value = grp.getvalue ('3/3/1')
out_value = 0
if summer then
out_addr = '6/0/91'
if value == true then and if value then work the same when value variable type is Boolean (true/false). If value for 7/0/0 is true then summer mode part is executed otherwise winter mode.