BOOSTER CONDIZIONATO
#21
(20.04.2020, 16:00)admin Wrote: if value == true then and if value then work the same when value variable type is Boolean (true/false). If value for 7/0/0 is true then summer mode part is executed otherwise winter mode.
Thanks Edgard,
I understand, now I try it and let you know if it works as expected, good evening
(20.04.2020, 06:54)admin Wrote: Try this:
value_1 = grp.getvalue('7/0/0')
value_3 = grp.getvalue('6/0/1')
temp = grp.getvalue('2/2/1')
setpoint = grp.getvalue('2/2/11')
delta = grp.getvalue('3/1/201')
out = false
if not value_3 then
  if value1 then
    out = delta <= (setpoint - temp)
    out = delta <= (temp - setpoint)
grp.write('3/0/206', out)
sorry Edgard,
in this first script:
value_1 = grp.getvalue ('7/0/0')
value_3 = grp.getvalue ('6/0/1')
temp = grp.getvalue ('2/2/1')
setpoint = grp.getvalue ('2/2/11')
delta = grp.getvalue ('3/1/201')
out = false
if not value_3 then
if value1 then
out = delta <= (setpoint - temp) - I need this in winter
out = delta <= (temp - setpoint) - I need this in the summer
grp.write ('3/0/206', out)
in WINTER (7/0/0 = 1)
3/0/206 = 1 when the setpoint <temp
3/0/206 = 0 when the setpoint> temp
WORKS IN THE OPPOSITE
I had to do this:
out = false
if not value_3 then
   if not value1 then
out = false
if not value_3 then
  if value1 then
sorry Edgard,
out = false
if not value_3 then
if value1 then
I had to do this:
out = false
if not value_3 then
   if not value1 then
ok Edgard works correctly, if you have something to think about the previous message, according to me it is now perfect and for this I thank you very much, I have been trying for months and I couldn't have done it.
I salute you