	Threads: 45
		There's no direct way of doing this. You can create a scheduled script that will push values to SQL database every minute or so. A better approach is to use a database that is meant for time-series data like InfluxDB.
	Threads: 14
		 (19.11.2019, 09:49)admin Wrote:  You can create a scheduled script that will push values to SQL database every minute or so.
I need to push values every 15 minutes to the database of almost 50 objects, but I'm not a programmer. If someone could help me would be great
	Threads: 45
		Can you provide table structure and what data do you want to add there apart from object values  (group address, name, date/time etc)?
	Threads: 14
		 (19.11.2019, 12:06)admin Wrote:  Can you provide table structure and what data do you want to add there apart from object values  (group address, name, date/time etc)?
The structures could be like this:
- Table 1 "trending_definition" including [trending id, group address, object name, data type, date/time last update]
- Table 2 "trenging_values" including [value id, trending id, value, date/time]
I accept any advice or suggestion about the structure.
	Threads: 45
		Example script. Map table keys are trend ID from external database, values are group addresses to get values from. Don't forget to change access details in connect function.  Code: require('luasql.mysql')
 env = luasql.mysql()
 dbcon, err = env:connect(DB_NAME, USERNAME, PASSWORD, MYSQL_SERVER_IP, MYSQL_SERVER_PORT)
 if dbcon then
 map = {
 [1] = '1/1/1',
 [2] = '1/1/2',
 for id, addr in pairs(map) do
 value = grp.getvalue(addr)
 dbcon:execute('INSERT INTO trends_values (trend_id, value, created_at) VALUES (' .. id .. ', ' .. value .. ', NOW())')
 dbcon:execute('UPDATE trends_definition SET updated_at=NOW() WHERE id=' .. id)
 dbcon:close()
 log('mysql connection failed ' .. tostring(err))
 env:close()
	Threads: 14
		 (19.11.2019, 14:07)admin Wrote:  Example script. Map table keys are trend ID from external database, values are group addresses to get values from. Don't forget to change access details in connect function.
 if dbcon then
 map = {
 [1] = '1/1/1',
 [2] = '1/1/2',
 dbcon:close()
 env:close()
This code creates the tables (trends_values, trends_definition) automatically or I must create it manually in the database?
	Threads: 45
		You have to create tables manually and fill trends_definition table with data.
	Threads: 7
Here is a script i created a few years ago that checks for tables and if not exist it creates them, maybe this can be helpful for you (:
 Code: -- Check if MySQL connection is loaded and available otherwise perform DB connection loadingif not env or not dbcon then
 -- Setup MySQL connection
 -- Set database information and credentials, make sure remote access to MySQL server is enabled (see notes on bottom of this script)
 DB_NAME = 'WiserforKNX'
 USERNAME = 'root'
 PASSWORD = 'MyPassword'
 MYSQL_SERVER_IP = 'www.myserveraddress.com'  -- remote access host
 MYSQL_SERVER_PORT = 6033 -- remote access port (asymetric forwarding 6603 ext to 3306 internal to avoid internet MySQL known port scanning)
 TIMEOUT = 3 -- timeout to avoid blocking when MySQL server could not be reached (set timeout in seconds)
 -- Connect to MySQL database
 dbcon, err = env:connect(DB_NAME, USERNAME, PASSWORD, MYSQL_SERVER_IP, MYSQL_SERVER_PORT, TIMEOUT)
 -- Error handler
 if err then
 log(err)
 env:close()
 env = nil
 alert('Connection to MySQL could not be established, system will try to restart connection')
 return
 if dbcon then
 -- Set connected variable to true
 connected = true
 -- Set DB connection autocommit to true
 dbcon:setautocommit(true)
 -- Check if table for recording excist inside the database and holds data
 cursor = dbcon:execute('SHOW TABLES LIKE "objectdata"')
 -- Loop trough fetched data to see if rows are available
 while true do
 row = cursor:fetch({}, 'a')
 if row then
 -- do nothing
 log("Table already exist, resuming script")
 break
 -- Drop DB table first before create new one
 dbcon:execute('DROP TABLE objectdata')
 -- Create DB table
 cursor = dbcon:execute('CREATE TABLE objectdata (ID int AUTO_INCREMENT, address varchar(255) NOT NULL, name varchar(255) NOT NULL, value varchar(255) NOT NULL, updatetime int NOT NULL, timestamp varchar(255) NOT NULL, PRIMARY KEY (ID))')
 log("Table for objectdata is created, resuming script")
 break
 -- Exit script for new try
 return
 -- Init client for listening to all KNX events
 if not client then
 --handler for all event types
 eventhandler = function(event)
 objectinfo = grp.find(event.dst)
 -- fix for auto discovered objects without a name
 if objectinfo.name == nil then
 objectinfo.name = "unknown"
 -- fix for new created objects without a having set value once
 if objectinfo.value == nil then
 objectinfo.value = "no value"
 objectinfo.value = tostring(objectinfo.value)
 -- fix for time object
 if type(objectinfo.value) == "table" then
 objectinfo.value = string.format("%02d", objectinfo.value.hour) .. ":" .. string.format("%02d", objectinfo.value.minute) .. ":" ..  string.format("%02d", objectinfo.value.second)
 -- fix for boolean object
 if type(objectinfo.value) == "boolean" then
 -- calculate human readable timestamp
 timestamp = os.date("%Y-%m-%d %H:%M:%S", objectinfo.updatetime)
 -- write data to MySQL database
 cursor, err = dbcon:execute('INSERT INTO objectdata (address, name, value , updatetime, timestamp) VALUES ("' .. objectinfo.address .. '", "' .. objectinfo.name .. '", "' .. objectinfo.value .. '", ' .. objectinfo.updatetime .. ', "' .. timestamp .. '")')
 -- Get result of transaction
 result = dbcon:commit()
 -- Error handler
 if not result or err then
 if connected == true then
 alert('Connection to MySQL is broken or data is not processed correct, system will buffer data until connection is restored')
 connected = false
 if not connected then
 connected = true
 -- Create client
 client = eibdgm:new()
 -- Set group communication handlers
 client:sethandler('groupread', eventhandler)
 client:sethandler('groupwrite', eventhandler)
 client:sethandler('groupresponse', eventhandler)
 -- Next cycle
 client:step()
	Threads: 14
		17.05.2020, 08:18
(This post was last modified: 17.05.2020, 08:56 by pentadom.)
		 (20.11.2019, 11:25)Erwin van der Zwart Wrote:  Hi,
 USERNAME = 'root'
 -- Error handler
 if err then
 log(err)
 env:close()
 env = nil
 return
 if dbcon then
 connected = true
 while true do
 if row then
 -- do nothing
 break
 -- Create DB table
 break
 return
 if not client then
 -- Error handler
 connected = false
 connected = true
 -- Create client
 -- Next cycle
 client:step()
Dear Erwin,
How would be the code to create automatically the tables I need.
This is my code now:
 if dbcon then
 map = {
 [1] = '1/1/1',
 [2] = '1/1/2',
 dbcon:close()
 env:close()
  (19.11.2019, 14:07)admin Wrote:  Example script. Map table keys are trend ID from external database, values are group addresses to get values from. Don't forget to change access details in connect function. I dont't want to modify the code every time I create a new object.
 if dbcon then
 map = {
 [1] = '1/1/1',
 [2] = '1/1/2',
 dbcon:close()
 env:close()
Is there any way to fill the map automatically when I create new objects in LM?
  (19.11.2019, 09:49)admin Wrote:  There's no direct way of doing this. You can create a scheduled script that will push values to SQL database every minute or so. A better approach is to use a database that is meant for time-series data like InfluxDB.
But if I push values directly from the objects and the connection with the database fails, this values will be lost. It's important to know that my database is in the cloud.
Can I push values from the trends. In this case I always have the values recorded locally in the LM and I do a backup once a day for example.
	Threads: 7
 Yes you can, you have seen the script for fetching the values from a trend, combine it with this script and modify the sql queries and you have what you need, it’s just a matter of creating a script with the samples you have..
	Threads: 14
		17.05.2020, 14:57
(This post was last modified: 17.05.2020, 14:58 by pentadom.)
		 (17.05.2020, 11:52)Erwin van der Zwart Wrote:  Hi,
Thanks Erwin, it's difficult for me because I'm not a programmer but I'll try
I did a test fetching values from a trend with the next code:
 Code: require('trends')
 name = 'testswitch'
 dates = {}
 dates['start'] = { year = 2020, month = 5, day = 17 }
 dates['end'] = { year = 2020, month = 5, day = 18 }
 -- resolution (in seconds) is optional
 -- default trend resolution is used when not set
 resolution = nil
 res = trends.fetch(name, dates, resolution)
 log(res)
but I have an error when I run script:
 ![[Image: rmKISet.jpg]](https://i.imgur.com/rmKISet.jpg)
	Threads: 29
		Does this trend testswitch exist?
------------------------------Ctrl+F5
	Threads: 45
		Have you tried clicking Save before Run script?
	Threads: 14
		18.05.2020, 07:55
(This post was last modified: 18.05.2020, 07:57 by pentadom.)
		 (18.05.2020, 07:38)Daniel. Wrote:  Does this trend testswitch exist?
Yes, here it is:
 ![[Image: 20zjQ9l.jpg]](https://i.imgur.com/20zjQ9l.jpg)
  (18.05.2020, 07:50)admin Wrote:  Have you tried clicking Save before Run script?
Yes. I tried "save" and "save and close"
I'm testing on the demo LM from openrb web. You can see all the configuration there if you want. The script called "SQL" is in the scheduled scripts.
	Threads: 45
		Some features are disabled on demo LM so this might not work. Do you have another LM to test this?
	Threads: 14
		 (18.05.2020, 07:58)admin Wrote:  Some features are disabled on demo LM so this might not work. Do you have another LM to test this?
No at the moment, I have it in my workplace. I'm confined because of the COVID-19
I supposed then it's because of a disabled feature really?
	Threads: 29
		On my LM this script works fine.
	Threads: 14
		 (18.05.2020, 08:06)Daniel. Wrote:  On my LM this script works fine.
Thank you so much for the information Daniel. I must test it on another LM.
	Threads: 14
I did some tests with the next code. I want to insert all the trending values in my SQL database. When I run the script all the code executes correctly without errors in the logs but in the database I don't see the new values..     Code: require('trends')require("luasql.mysql");
 --Get a list of all trendings
 names = db:getlist('SELECT name FROM trends')
 log (names)
 --Defines a period of the last day
 dates = {}
 dates['start'] = os.date('*t')
 dates['start'].day = dates['start'].day - 1
 dates['end'] = os.date('*t')
 env = luasql.mysql();
 --DATABASE CONNECTION -> (DB_NAME, USERNAME, PASSWORD, MYSQL_SERVER_IP, MYSQL_SERVER_PORT)
 dbcon, err = env:connect('CONFIDENTIAL', 'admin','CONFIDENTIAL', 'lm-database.CONFIDENTIAL.us-east-1.rds.amazonaws.com', '3306');
 log(dbcon, err)
 if dbcon then
 -- Iterates all the trendings
 for _, name in ipairs(names) do
 -- Get all the trending values
 data = trends.fetch(name, dates)
 -- Iterates all the trending values
 for id, val in pairs(data) do
 -- Insert the trending values in the database.
 dbcon:execute('INSERT INTO trending-definition (id, value) VALUES (id,val)')
 dbcon:close()
 env:close()
I'm not a programmer and It's my first time doing a script with LUA so I apologize in advance for the posible errors.
	Threads: 45
		Use this table structure for data. trend_id will be the same id as in LM. Code: CREATE TABLE `trends_data` (`trend_id` int(11) NOT NULL,
 `dt` datetime NOT NULL,
 `value` double DEFAULT NULL,
 PRIMARY KEY (`trend_id`,`dt`)
 ) ENGINE=InnoDB DEFAULT CHARSET=utf8;
Updated script:
 Code: require('trends')require('luasql.mysql')
 dbcon, err = env:connect('CONFIDENTIAL', 'admin', 'CONFIDENTIAL', 'lm-database.CONFIDENTIAL.us-east-1.rds.amazonaws.com', 3306)
 if dbcon then
 items = db:getall('SELECT id, name FROM trends')
 trends.NaN = 'NULL'
 dates = {
 ['start'] = os.date('*t'),
 ['end'] = os.date('*t'),
 dates.start.day = dates.start.day - 1
 date = string.format('%04d-%02d-%02d',
 dates.start.year, dates.start.month, dates.start.day)
 for _, item in ipairs(items) do
 id = item.id
 data = trends.fetch(item.name, dates)
 values = {}
 if data and #data > 0 then
 step = 1440 / #data -- in minutes
 for i, val in ipairs(data) do
 mins = (i - 1) * step
 datetime = string.format('%s %02d:%02d:00',
 date, math.floor(mins / 60), mins % 60)
 values[ #values + 1 ] = string.format('(%d,"%s",%s)',
 id, datetime, tostring(val))
 if #values > 0 then
 query = 'INSERT INTO trends_data (trend_id, dt, value) VALUES ' .. table.concat(values, ',')
 dbcon:execute(query)
 dbcon:close()
 env:close()