Hue Brightness feedback
#41
(31.07.2020, 07:53)Erwin van der Zwart Wrote: Hi,
I checked and line 21 is handling the response of the function getHueLights() that is located in the user.hue, so i guess you use a older version of the user lib.
Can you try to replace your user.hue with this version? A restart might be required.
Thank you, it's working nowSmile
Magnus
Hi Ervin,
since i update the user.hue to V4 i get this error message every time:
Resident script:62: attempt to perform arithmetic on a nil value
stack traceback:
this is my resident script:
-- Set name (Lookup in HUE app under light configuration) and feedback adresses (don't change statevalue, brivalue and colorvalue as they are used as memoryfield)
addressmapping = {
  -- Name                  -- On/Off FB       -- Bright FB   -- Color FB
  ['Schlafzimmer'] = {state = '10/1/27', bri = '10/1/15',  rgb = 'x/x/x', statevalue = '', brivalue = '', colorvalue = ''},
  ['Laura Wand Links'] = {state = '32/1/7', bri = '32/1/9', rgb = '32/1/16', statevalue = '', brivalue = '', colorvalue = ''},
  ['Laura Wand Rechts'] = {state = '32/1/8', bri = '32/1/10', rgb = '', statevalue = '', brivalue = '', colorvalue = ''},
  ['Küche Led'] = {state = '32/1/11', bri = '32/1/13', rgb = '10/1/5', statevalue = '', brivalue = '', colorvalue = ''},
  ['Küche indirekt'] = {state = '32/1/12', bri = '10/1/3', rgb = '32/1/14', statevalue = '', brivalue = '', colorvalue = ''},
  ['Esstisch'] = {state = '10/1/157', bri = '10/1/159', rgb = 'x/x/x', statevalue = '', brivalue = '', colorvalue = ''},
  ['Laura Zelt'] = {state = '10/1/25', bri = 'x/x/x', rgb = 'x/x/x', statevalue = '', brivalue = '', colorvalue = ''},
  ['Wohnzimmer Links'] = {state = '32/1/3', bri = '32/1/5', rgb = 'x/x/x', statevalue = '', brivalue = '', colorvalue = ''},
  ['Wohnzimmer Rechts'] = {state = '32/1/4', bri = '32/1/6', rgb = 'x/x/x', statevalue = '', brivalue = '', colorvalue = ''},
  ['Kinderzimmer Links'] = {state = '32/1/17', bri = '32/1/19', rgb = 'x/x/x', statevalue = '', brivalue = '', colorvalue = ''},
  ['Kinderzimmer Rechts'] = {state = '32/1/18', bri = '32/1/20', rgb = 'x/x/x', statevalue = '', brivalue = '', colorvalue = ''},
  ['Küche Theke'] = {state = '10/1/161', bri = '10/1/163', rgb = 'x/x/x', statevalue = '', brivalue = '', colorvalue = ''}
-- Set polling interval in seconds
interval = 1
-- Use logging
logging = true
require('user.hue')
require('json')
-- loop indefenitly
while true do
  reply = getHueLights()
  mylamps = json.decode(reply)
  for _, item in pairs(mylamps) do
    -- Check if lamp is found by bridge otherwise it make no sense to send commands
    if item.state.reachable == true then
      -- On/Off
      name = addressmapping[item.name]
      if name then
        addr = addressmapping[item.name]['state']
        if addr and addr ~= '' then
          currentvalue = addressmapping[item.name]['statevalue']
          if currentvalue ~= item.state.on then
            grp.write(addr, item.state.on)
            addressmapping[item.name]['statevalue'] = item.state.on
            if logging == true then
              log('lamp ' .. item.name .. ' state is: ' .. tostring(item.state.on))
      -- Brightness
      if name then
        addr = addressmapping[item.name]['bri']
          -- Check if lamp is on otherwise overrule BRI value to 0
          if item.state.on == false then
            item.state.bri = 0
          currentvalue = addressmapping[item.name]['brivalue']
          if currentvalue ~= item.state.bri then
            grp.write(addr, math.floor((tonumber(item.state.bri)/2.55) + 0.5))
            addressmapping[item.name]['brivalue'] = item.state.bri
              log('lamp ' .. item.name .. ' brightness is: ' .. math.floor((tonumber(item.state.bri)/2.55) + 0.5) .. ' %')
      -- Color
      if name then
        addr = addressmapping[item.name]['rgb']
          -- Check if lamp is on otherwise overrule color value to 0
             colorvalue = 0
          if item.state.colormode == 'xy' then
            currentvalue = addressmapping[item.name]['colorvalue']
            colorvalue = xy_to_rgb(item.state.xy[1],item.state.xy[2],item.state.bri)
            --colorvalue = xyz_to_rgb((item.state.xy[1] * 100), (item.state.xy[2] * 100))
            if currentvalue ~= colorvalue then
              grp.write(addr, colorvalue)
              addressmapping[item.name]['colorvalue'] = colorvalue
                log('lamp ' .. item.name .. ' color is: ' .. colorvalue)
          elseif item.state.colormode == 'ct' then
            --colortemp = math.floor((item.state.ct / 0.0769) + 0.5)  --0.0769230769230769
            colortemp = math.abs((item.state.ct - 500) / 2)
            colortemp = math.floor(colortemp + 0.5)
            colortemp = 80 + colortemp
            if colortemp > 255 then
              colortemp = 255
            r = lmcore.inttohex(255, 1)
            g = lmcore.inttohex(255, 1)
            b = lmcore.inttohex(colortemp, 1)
            rgb = r .. g .. b
            colortemp = lmcore.hextoint(rgb,3)
            if currentvalue ~= colortemp then
              --colortempconverted = ct_to_rgb(colortemp)
              grp.write(addr, colortemp)
              addressmapping[item.name]['colorvalue'] = colortemp
                log('lamp ' .. item.name .. ' color is: ' .. colortemp)
    --log('manufacturername = ' .. item.manufacturername)
    --log('swversion = ' .. item.swversion)
    --log('type = ' .. item.type)
    --log('ct = ' .. item.state.ct)
    --log('reachable = ' .. item.state.reachable)
    --log('alert = ' .. item.state.alert)
    --log('on = ' .. item.state.on)
      --log('bri = ' .. item.state.bri)
    --log('colormode = ' .. item.state.colormode)
    --log('hue = ' .. item.state.hue)
    --log('sat = ' .. item.state.sat)
    --log('effect = ' .. item.state.effect)
    --log('x = ' .. item.state.xy[1])
    --log('y = ' .. item.state.xy[2])
    --log('uniqueid = ' .. item.uniqueid)
    --log('modelid = ' .. item.modelid)
    --log('name = ' .. item.name)
    -- Delay loop
    os.sleep(interval)
line 62 is the grp.write, before i used your script in V3.
HW is an HL V1 running LM Firmware 202007 RC2.
Lars
Try this: (I added a check to be sure the device supports BR, CT or XY)
addressmapping = {
interval = 1
-- Use logging
logging = false
-- Load needed lib's
require('user.hue')
require('json')
-- loop indefenitly
while true do
      -- On/Off
      if name then
            grp.checkwrite(addr, item.state.on)
      --Brightness
      if item.state.bri then
        if name then
              item.state.bri = 0
            currentvalue = addressmapping[item.name]['brivalue'] or 0
              grp.checkwrite(addr, math.floor((tonumber(item.state.bri)/2.55) + 0.5))
      --Color
      if item.state.ct or item.state.xy then
        if name then
               colorvalue = 0
                grp.checkwrite(addr, colorvalue)
                colortemp = 255
              rgb = r .. g .. b
                grp.checkwrite(addr, colortemp)
  -- Delay loop
  os.sleep(interval)
Thank you Erwin. No more errors. Big Grin
I saw in the user.hue an Line send to Group. Have you any scripts to controll an entire Hue Group ?
At the moment i control a Group that each Light has an own event based script wich is triggerd by the same tag behind the KNX Group adress.
Yes you can do that, in the user.hue there are already 2 functions to use for group commands, getHueGroups() and sendToGroup()
First you have to get the groups by this command:
--Get all group information
require('user.hue')
-- get all lights from bridge
result = getHueGroups()
log(result)
When you know the group ID you can control it with:
require('user.hue')
value = event.getvalue()
group_id = 1 -- change this ID to your actual group, see getHueGroups() result
if value == true then
  body_msg = '{"on":true}'
  sendToGroup(group_id,body_msg)
  body_msg = '{"on":false}'
Hi Ervin,
thank you for your help. The Script for group switching works perfect. I tried the same with brigtness but had no luck. Just change the script from lampID to GroupID didn´t work.
Do you have any scripts for controlling the Brightness, RGB an CT for Group´s with Feedback ?
Is there a chance that upcomming releases of W4K Firmware have an nativ integration of Philips HUE ?
Lars
Did you also called the function sendToGroup?
No I don’t think so, i have not seen any development in that direction, they work on speech control and new mobile app at this moment. Maybe i will start a new project to build a app for HUE this winter, but I don’t have time until November this year..
I Tried this with no effect
--Control HUE from byte object (brightness) (use as event based script)
require('user.hue')
value = event.getvalue()  -- 1 byte unsigned integer scale 0 - 100
group_id = 1 -- change this ID to your actual light, see getHueLights() result for lamps or use your app to resolve them
setBrightness(group_id,value)
then i added a function in user.hue with also no luck.
function setBrightness(Group_id,brightness)
  if brightness == 0 then
      response = sendToGroup(group_id,body_msg)
    return response
    brightness = math.floor((brightness / 1) + 0.5)
    brightness = math.floor((brightness * 2.54) + 0.5)
    --HTTP request send
    body_msg = '{"on":true,"bri":'..brightness..'}'
    response = sendToGroup(Group_num,body_msg)
    return response
You have 2 mistakes in your script:
should be
response = sendToGroup(Group_id,body_msg)
and
should be
I just tested with my latest user lib and this command and works perfect
require('user.hue')
require('json')
--log(json.pdecode(getHueGroups())) -- enable to check group number
--setBrightnessGroup(1,100) -- Group, brightness in %
setBrightnessCTGroup(1,60,2000) -- Group, brightness in %, CT in Kelvin
.lua   user.hue v5.lua (Size: 11.17 KB / Downloads: 72)
Hi Erwin,
I just configured a group and i can control the group via the group-script. However i can not get the status of this group to update.
addressmapping = {
  ['Led terras'] = {state = '20/0/1', bri = '20/1/1', rgb = '20/2/1', ct = '20/3/1', statevalue = '', brivalue = '', colorvalue = ''},
  ['Keuken Eiland'] = {state = '20/0/2', bri = '20/1/2', rgb = '20/2/2', statevalue = '', brivalue = '', colorvalue = ''},
  ['Keuken Werkblad R'] = {state = '20/0/3', bri = '20/1/3', rgb = '20/2/3', statevalue = '', brivalue = '', colorvalue = ''},
  ['Keuken Werkblad L'] = {state = '20/0/4', bri = '20/1/4', rgb = '20/2/4', statevalue = '', brivalue = '', colorvalue = ''},
  ['Douche L'] = {state = '20/0/5', bri = '20/1/5', rgb = '20/2/5', statevalue = '', brivalue = '', colorvalue = ''},
  ['Douche R'] = {state = '20/0/6', bri = '20/1/6', rgb = '20/2/6', statevalue = '', brivalue = '', colorvalue = ''},
  ['Keuken Werkblad'] = {state = '20/0/7', bri = '20/1/7', rgb = '20/2/7', statevalue = '', brivalue = '', colorvalue = ''},
It's the last line in the code "Keuken Werkblad" The individual lamps "Keuken Werkblad L" & "Keuken Werkblad R" get updated in both "state", "bri" and "rgb"
Can you help me out?
Novice DIY with a HL and KNX basics trying to ...
Erwin's script uses getHueLights() which does not include groups. Try this to get info for both lights and groups together (replace the relevant script part with this):
-- loop indefenitly
while true do
  -- get groups start
  reply = getHueGroups()
  groups = json.pdecode(reply)
  if type(groups) == 'table' then
    for k, v in pairs(groups) do
      mylamps[ k ] = v
  -- get groups end
Dear Admin,
I've added these lines to the resident Hue script. Now none of the Hue lamp statusses are updated, neither the brightness nor the rgb. These worked before i added the lines. I do not get log's when switching lamps on or off. No error logs as well. I'm using the v5 user.hue library.
addressmapping = {
interval = 1
-- Use logging
logging = true
require('user.hue')
require('json')
-- loop indefenitly
while true do
  -- get groups start
      mylamps[ k ] = v
  -- get groups end
      -- On/Off
      if name then
            grp.update(addr, item.state.on)
      -- Brightness
      if name then
            item.state.bri = 0
            grp.update(addr, math.floor((tonumber(item.state.bri)/2.55) + 0.5))
      -- Color
      if name then
             colorvalue = 0
              grp.update(addr, colorvalue)
              colortemp = 255
            rgb = r .. g .. b
              grp.update(addr, colortemp)
    -- Delay loop
    os.sleep(interval)
Kind regards
Can it be that there's a typo in the lines?
-- get groups start
  groups = json.pdecode(reply) -- ==>json.decode(reply) ???
      mylamps[ k ] = v
  -- get groups end
Try this (change line 31): mylamps[ #mylamps +1 ] = v
pdecode is needed for safe deciding in case there's no reply or it is malformed.
Admin,
Individual lamp statusses are updated again, but still no update on the group status, brightness and rgb. Log's are also back now.
Add log(groups) after pdecode and post what you get in Logs tab.
this is the log:
* table:
["4"]
  * table:
   ["action"]
    * table:
     ["ct"]
      * number: 153
     ["alert"]
      * string: select
     ["on"]
      * bool: true
     ["bri"]
      * number: 254
     ["colormode"]
      * string: xy
     ["hue"]
      * number: 41435
     ["sat"]
      * number: 77
     ["effect"]
      * string: none
     ["xy"]
      * table:
       [1]
        * number: 0.3129
       [2]
        * number: 0.3291
   ["sensors"]
    * table:
   ["recycle"]
    * bool: false
   ["state"]
    * table:
     ["all_on"]
      * bool: true
     ["any_on"]
      * bool: true
   ["lights"]
    * table:
     [1]
      * string: 4
     [2]
      * string: 3
   ["class"]
    * string: Kitchen
   ["name"]
    * string: Keuken Werkblad
   ["type"]
    * string: Room
["1"]
  * table:
   ["action"]
    * table:
     ["ct"]
      * number: 331
     ["alert"]
      * string: none
     ["on"]
      * bool: false
     ["bri"]
      * number: 254
     ["colormode"]
      * string: xy
     ["hue"]
      * number: 58281
     ["sat"]
      * number: 142
     ["effect"]
      * string: none
     ["xy"]
      * table:
       [1]
        * number: 0.4359
       [2]
        * number: 0.2811
   ["sensors"]
    * table:
   ["recycle"]
    * bool: false
   ["state"]
    * table:
     ["all_on"]
      * bool: false
     ["any_on"]
      * bool: false
   ["lights"]
    * table:
     [1]
      * string: 1
   ["class"]
    * string: Terrace
   ["name"]
    * string: Tuin
   ["type"]
    * string: Room
["2"]
  * table:
   ["action"]
    * table:
     ["on"]
      * bool: false
     ["alert"]
      * string: none
   ["sensors"]
    * table:
   ["recycle"]
    * bool: false
   ["state"]
    * table:
     ["all_on"]
      * bool: false
     ["any_on"]
      * bool: false
   ["lights"]
    * table:
   ["class"]
    * string: Bathroom
   ["name"]
    * string: Badkamer
   ["type"]
    * string: Room
["6"]
  * table:
   ["action"]
    * table:
     ["ct"]
      * number: 343
     ["alert"]
      * string: select
     ["on"]
      * bool: false
     ["bri"]
      * number: 254
     ["colormode"]
      * string: xy
     ["hue"]
      * number: 8597
     ["sat"]
      * number: 121
     ["effect"]
      * string: none
     ["xy"]
      * table:
       [1]
        * number: 0.4452
       [2]
        * number: 0.4068
   ["sensors"]
    * table:
   ["recycle"]
    * bool: false
   ["state"]
    * table:
     ["all_on"]
      * bool: false
     ["any_on"]
      * bool: false
   ["lights"]
    * table:
     [1]
      * string: 5
     [2]
      * string: 6
   ["class"]
    * string: Bathroom
   ["name"]
    * string: Douche
   ["type"]
    * string: Room
["3"]
  * table:
   ["action"]
    * table:
     ["ct"]
      * number: 156
     ["alert"]
      * string: select
     ["on"]
      * bool: true
     ["bri"]
      * number: 254
     ["colormode"]
      * string: ct
     ["hue"]
      * number: 41432
     ["sat"]
      * number: 75
     ["effect"]
      * string: none
     ["xy"]
      * table:
       [1]
        * number: 0.3146
       [2]
        * number: 0.3304
   ["sensors"]
    * table:
   ["recycle"]
    * bool: false
   ["state"]
    * table:
     ["all_on"]
      * bool: true
     ["any_on"]
      * bool: true
   ["lights"]
    * table:
     [1]
      * string: 2
   ["class"]
    * string: Kitchen
   ["name"]
    * string: Keuken Eiland
   ["type"]
    * string: Room
Try this:
v.state = v.action
There's no full state response for groups, only the last sent values.
No change. Group doesn't get updated
How do you get CT state in the resident Script ??
I tried adding , ct = x/x/x , after the RGB state valeu but nothing happens.
Try adding this to the script before -- Color:
-- color temperature
      if name and item.state.ct then
        addr = addressmapping[item.name]['ct']
          newvalue = math.floor(1000000 / item.state.ct)
          currentvalue = addressmapping[item.name]['ctvalue']
          if currentvalue ~= newvalue then
            grp.update(addr, newvalue)
            addressmapping[item.name]['ctvalue'] = newvalue
              log('lamp ' .. item.name .. ' color temperature is: ' .. newvalue .. ' K')