Energy calculation and data saving
Dear all,
I manage some energy counters (energy produced by photovoltaic, energy sold to the network) and in the meanwhile I calculate the self-consumption energy. Daily and total. Here below is shown the script I did and I would like to ask you if there's a best way to improve it.
The system works fine but I would like to know if there's a better way to manage this process.
1. Scheduled script to read the value of energy instrument at the beginning of the day (energy counter of instrument cannot be reset). Hence I find this method to obtain daily data.
-- script run every day at 0:0 am. -- script to get value from instrument of photovoltaic energy and energy sold. evenduta = grp.getvalue('3/4/16') -- read from the instrument value of energy sold grp.write('32/1/10', evenduta) -- write to morning_energy_sold which has address 32/1/10 -- evenduta_mattino = grp.getvalue('32/1/10') ftv = grp.getvalue('3/4/28') -- read from the instrument value of energy produced by photovoltaic grp.write('32/1/11', ftv) -- write to morning_energy_photovoltaic which has address 32/1/11
2. Scheduled script to calculate energy product by photovoltaic and self-consumption energy.
-- script runs every day, every hour at 59 minutes -- script to calculate the daily energy product by photovoltaic and self-consumption energy. The last script of the day will give the result of the day. ftv = grp.getvalue('3/4/28') -- energy read by instrument of photovoltaic. ftv_mattino = grp.getvalue('32/1/11') -- photovoltaic energy read by morning script. evenduta = grp.getvalue('3/4/16') -- energy read by instrument of energy sold. evenduta_mattino = grp.getvalue('32/1/10') -- energy-sold read by morning script. delta_ftv = ftv - ftv_mattino -- difference to calculate daily photovoltaic energy. delta_evenduta = evenduta - evenduta_mattino -- difference to calculate daily energy sold. grp.write('32/1/12', delta_ftv) grp.write('32/1/13', delta_evenduta) energia_autoconsumata = delta_ftv - delta_evenduta -- difference to calculate self-consumption energy grp.write('32/1/15', energia_autoconsumata) -- daily value of self-consumption energy autoconsumo_perc = (energia_autoconsumata / delta_ftv) * 100 -- % value of daily self-consumption energy grp.write('32/1/14', autoconsumo_perc)
3. Scheduled script to calculate the total self-consumption energy.
-- script runs all days, at 11 pm at 59 minutes. -- script to calculate total self-consumption energy. daily = grp.getvalue('32/1/15') -- read daily self-consumption energy os.sleep(2) total = storage.get('autoconsumo_totale') -- get from system self-consumption energy os.sleep(2) total = daily + total -- add to total the daily value os.sleep(2) grp.write('32/1/16', total) -- write to "Total self-consumption energy" address storage.set('autoconsumo_totale', total) -- save on system new "Total self-consumption energy"
Looks good to me. It can also be done without the third script by adding this to the end of the second script that runs every hour at 59 minutes:
-- run only on the last hour of the day hour = os.date('*t').hour if hour == 23 then   total = energia_autoconsumata + grp.getvalue('32/1/16')   grp.write('32/1/16', total) end
(29.04.2021, 07:57)admin Wrote: Looks good to me. It can also be done without the third script by adding this to the end of the second script that runs every hour at 59 minutes:
Thank you. Further to save the data do you suggest to NOT use the "storage"?
Group address is data retain in any case?
There's no big difference which method to use. Object values are synced the same way as storage is. Just make sure that the object data type can store the value without overflowing. Use either 4 byte floating point or 8 byte signed integer depending on your data.