trend export via csv
hi
Earlier you had a example of how to export trends via ftp server as csv but now this doesnt work due to latest firmware.
Is it possible to get an working update for this?
require('socket.ftp')
require('genohm-scada.trends')
time = os.time()
date = {
  stime = time - 86400,
  etime = time,
values = trends.fetch('Effektforbruk lys', 'hour', date)
buffer = {}
count = 0
average = 0
resolution = 60 -- in minutes
row = string.format('%q,%q', "Tid", "Watt")
  table.insert(buffer, row)
for _, data in ipairs(values) do
  count = count + 1
  average = average + data[ 2 ]
  if count == resolution then
    date = os.date('%d.%b %H:%M', time -86400)
    value = average / resolution
    row = string.format('%q,%q', date, value)
    time = time + 60 * resolution
    count = 0
    average = 0
if #buffer > 0 then
  data = table.concat(buffer, '\n\r')
  res, err = socket.ftp.put({
    host = 'example.no',
    user = 'example@example.no',
    password = 'knfvkdnkd',
      argument = 'trend_dag_lys.csv',
      source = ltn12.source.string(data)
Here is a example on mailing the export from new trends as CSV, the attachment is placed on FTP first, so if you remove the mail part you have a working script.
You can find new trend log functions here: http://openrb.com/docs/trends-new.htm
--**************************************************************************-- --** Email trendlog data as CSV attachment created by Erwin van der Zwart **-- --************ For HL from FW 1.5 and SL from FW 1.2 with NGINX ************-- --**************************************************************************-- --*************************** Start of parameters **************************-- -- Version 1.1 *************************************************************-- --Gmail (smtp) username !IMPORTANT! user = 'YOUR EMAIL ADRESS' --Gmail (smtp) password !IMPORTANT! password = 'YOUR PASSWORD' --Sender for e-mail from = '<' .. user .. '>' alias_from = 'YOUR ALIAS' --Recipient for e-mail to = '<receiver@domain.com>' alias_to = 'receiver' --Subject for e-mail subjectpart1 = 'Trend export file' subjectpart2 = 'automaticly send by homeLYnk' --Message on bottom of email (will only be showed when client don't understand attachment) epilogue = 'End of message' --Set export mode (selected trend(s) or all trends) export_all = true --Set trend names if not all trends need to be exported (only used when export_all = false) trendnames = {  "Total Electric Usage",  "Total Water Usage",  "Total Gas Usage", } --**************************************************************************-- --**************************** End of parameters ***************************-- --**************************************************************************-- --****************** DON'T CHANGE ANYTHING UNDER THIS LINE *****************-- --**************************************************************************-- require('trends') -- Get all trend names from DB trends_table = db:getall('SELECT name FROM trends ORDER BY name DESC') -- Check if all trends or selection neeed to be exported if export_all == false then  -- Loop through trends_table  i = 1     for _, trend_names in ipairs(trends_table) do    delete_from_table = true    -- Loop through trendnames    for _, trendname in ipairs(trendnames) do      if trendname == trend_names.name then            delete_from_table = false      end    end    if delete_from_table == true then      table.remove(trends_table, i)      end      i = i + 1  end end -- Check if the is at least 1 trend to be exported if #trends_table < 1 then  log("No trends available, Could not export trends")  return end -- csv buffer buffer = {} -- Add to buffer table.insert(buffer, '"This file contains the export data of ' .. #trends_table .. ' trend(s) and is automaticly created on ' .. os.date("%A",os.time()) .. ' ' .. os.date("%d-%m-%y at %H:%M") .. '"') -- Add empty line table.insert(buffer, '""') -- months local months = { "Januari", "Februari", "March", "April", "May", "June", "July", "August", "September", "October", "November", "December" } -- Loop through trends_table for _, trend_names in ipairs(trends_table) do  -- Grab trend name from DB table  trend_name = trend_names.name    -- Add to buffer  table.insert(buffer, '"##### START OF TREND ' .. _ .. ': ' .. trend_name .. ' #####"')  -- Add empty line  table.insert(buffer, '""') -- Get current timestamp  timestamp = os.time()     startpoint = os.date('*t', timestamp)     endpoint = os.date('*t')     -- Reset to first of month     startpoint.sec = 0     startpoint.min = 0     startpoint.hour = 0     startpoint.yday = startpoint.yday - (startpoint.day -1)     startpoint.day = 1     startpoint.wday = 1     endpoint.sec = 0     endpoint.min = 0     endpoint.hour = 0     endpoint.yday = endpoint.yday - (endpoint.day -1)     endpoint.day = 1     endpoint.wday = 1     -- Get data for the past month     dates = {}  dates['start'] = startpoint    if dates['start'].month == 1 then      dates['start'].month = 12    dates['start'].year = dates['start'].year - 1  else    dates['start'].month = dates['start'].month - 1  end     dates['end'] = endpoint  dates['end'].month = dates['start'].month + 1    -- Set resolution to dayly data  resolution = 86400    -- Get last month for data by each days in this month  trenddatamonth = trends.fetch(trend_name, dates, resolution)    -- Get last month total avarage data  trenddatamonthavg = trends.fetchone(trend_name, dates, resolution)    -- Add to buffer  table.insert(buffer, '"Export of the average usage of the month ' .. months[dates['start'].month] .. ' from trend ' .. trend_name .. '"')  -- Add empty line  table.insert(buffer, '""')  -- Add header  table.insert(buffer, '"Start date","End Date","Average month value"')  -- Add to buffer  table.insert(buffer, '"01-' .. string.format("%02d", dates['start'].month) .. "-" .. dates['start'].year .. '","' .. #trenddatamonth .. '-' .. string.format("%02d", dates['start'].month) .. "-" .. dates['start'].year .. '","' .. trenddatamonthavg .. '"')  -- Add empty line  table.insert(buffer, '""')  -- Add to buffer  table.insert(buffer, '"Detailed export of the daily usage of the month ' .. months[dates['start'].month] .. ' from trend ' .. trend_name .. '"')  -- Add empty line  table.insert(buffer, '""')  -- Add header  table.insert(buffer, '"Weekday","Date","Average day value"')  for _, row in ipairs(trenddatamonth) do    stamp = dates['start'].year .. '-' .. dates['start'].month .. '-' .. string.format("%02d", _)         local y, m, d = stamp:match("(%d+)%-(%d+)%-(%d+)")         local t = { year = y, month = m, day = d}      -- format csv row    csv = string.format('%q,%q,%q', os.date("%A",os.time(t)), "" .. string.format("%02d", _) .. "-" .. string.format("%02d", dates['start'].month) .. "-" .. dates['start'].year, row)    -- add to buffer    table.insert(buffer, csv)  end  -- Add empty line  table.insert(buffer, '""')  -- Add header  table.insert(buffer, '"##### END OF TREND ' .. _ .. ': ' .. trend_name .. ' #####"')  -- Add empty line  table.insert(buffer, '""') end --Create table to include mail settings local settings = {    from = from,    rcpt = to,    user = user,    password = password,    server = 'smtp.gmail.com',    port = 465,    secure = 'sslv23', } --Create attachment inside FTP server src = 'Trend Export '.. os.date('%Y-%m-%d %H#%M#%S') .. '.csv' dst = '/home/ftp/' .. src io.writefile(dst, buffer) --Create subject subject = subjectpart1 .. ": " .. src .. " " .. subjectpart2 --Load required modules to send email with attachment local smtp = require("socket.smtp") local mime = require("mime") local ltn12 = require("ltn12") --Create e-mail header settings.source = smtp.message{ headers = {          from = '' .. alias_from .. ' ' .. from .. '',          to = '' .. alias_to .. ' ' .. to .. '',          subject = subject }, --Load attachment inside body     body = { preamble = "", [1] = {          headers = {           ["content-type"] = 'text/plain',           ["content-disposition"] = 'attachment; filename="'..src..'"',           ["content-description"] = '.. src ..',           ["content-transfer-encoding"] = "BASE64",        },        body = ltn12.source.chain(          ltn12.source.file(io.open(dst, "rb")),          ltn12.filter.chain(          mime.encode("base64"),          mime.wrap()        )      )    },      epilogue = epilogue  } } --Send the email r, e = smtp.send(settings) --Create alert when sending gives an error with error message if (e) then  log (e)  log (r)  alert("Could not send email: ", e, "\n") end --Delete created backup file from ftp folder inside HL os.remove(dst)
Sample above has a complex date range selector as we wanted to grab a full month at any moment, here is the easy way to select a range (sample for a week selection):
-- Get current timestamp timestamp = os.time() enddate = os.date('*t', timestamp) startdate =  os.date('*t', (timestamp - 604800)) -- 1 week dates = {} dates['start'] = startdate dates['end'] = enddate
Erwin van der Zwart
Thanks for the reply and all the answers you are helping with on this forumSmile
I have tried that script earlier but I get the following error
Line 144: attempt to get length of global 'trenddatamonth' ( a nil value)
Any idea what makes this?
Trenddatamonth is the result of the trend.fetch on line 133 and this is (or should be) a table you get back from the trend.
Are you sure you have used the correct trend name?
See line 30 to 37:
export_all = true
trendnames = {
  "Total Gas Usage",
If export_all = false then the table trendnames will be used, so those should match your trend names
I have this working but i want to use this to get daily data and also the max value for the day for a few trends, what would i need to change in this script
Many Thanks
Can you confirm that this script by erwin Van der Zwart that i adapted allows you to send all the trends to a remote FTP server?
--**************************************************************************-- --** Email trendlog data as CSV attachment created by Erwin van der Zwart **-- --************ For HL from FW 1.5 and SL from FW 1.2 with NGINX ************-- --**************************************************************************-- --*************************** Start of parameters **************************-- -- Version 1.1 *************************************************************-- --Mettre la valeur true pour exporter l'ensemble des courbes : export_all = true -- mettre le noms de chaque courbes que vous souhaitez exporter (Seulement utilisé quand : export_all = false) trendnames = {   "Total Electric Usage",   "Total Water Usage",   "Total Gas Usage", } require('trends') trends_table = db:getall('SELECT name FROM trends ORDER BY name DESC') if export_all == false then     i = 1     for _, trend_names in ipairs(trends_table) do     delete_from_table = true         for _, trendname in ipairs(trendnames) do       if trendname == trend_names.name then             delete_from_table = false       end     end     if delete_from_table == true then       table.remove(trends_table, i)       end       i = i + 1   end end if #trends_table < 1 then   log("No trends available, Could not export trends")   return end buffer = {} table.insert(buffer, '"This file contains the export data of ' .. #trends_table .. ' trend(s) and is automaticly created on ' .. os.date("%A",os.time()) .. ' ' .. os.date("%d-%m-%y at %H:%M") .. '"') table.insert(buffer, '""') local months = { "Januari", "Februari", "March", "April", "May", "June", "July", "August", "September", "October", "November", "December" } for _, trend_names in ipairs(trends_table) do     trend_name = trend_names.name       table.insert(buffer, '"##### START OF TREND ' .. _ .. ': ' .. trend_name .. ' #####"')     table.insert(buffer, '""')   timestamp = os.time()     startpoint = os.date('*t', timestamp)     endpoint = os.date('*t')         startpoint.sec = 0     startpoint.min = 0     startpoint.hour = 0     startpoint.yday = startpoint.yday - (startpoint.day -1)     startpoint.day = 1     startpoint.wday = 1     endpoint.sec = 0     endpoint.min = 0     endpoint.hour = 0     endpoint.yday = endpoint.yday - (endpoint.day -1)     endpoint.day = 1     endpoint.wday = 1         dates = {}   dates['start'] = startpoint     if dates['start'].month == 1 then       dates['start'].month = 12     dates['start'].year = dates['start'].year - 1   else     dates['start'].month = dates['start'].month - 1   end     dates['end'] = endpoint   dates['end'].month = dates['start'].month + 1       resolution = 86400       trenddatamonth = trends.fetch(trend_name, dates, resolution)       trenddatamonthavg = trends.fetchone(trend_name, dates, resolution)       table.insert(buffer, '"Export of the average usage of the month ' .. months[dates['start'].month] .. ' from trend ' .. trend_name .. '"')     table.insert(buffer, '""')     table.insert(buffer, '"Start date","End Date","Average month value"')     table.insert(buffer, '"01-' .. string.format("%02d", dates['start'].month) .. "-" .. dates['start'].year .. '","' .. #trenddatamonth .. '-' .. string.format("%02d", dates['start'].month) .. "-" .. dates['start'].year .. '","' .. trenddatamonthavg .. '"')     table.insert(buffer, '""')     table.insert(buffer, '"Detailed export of the daily usage of the month ' .. months[dates['start'].month] .. ' from trend ' .. trend_name .. '"')     table.insert(buffer, '""')     table.insert(buffer, '"Weekday","Date","Average day value"')   for _, row in ipairs(trenddatamonth) do     stamp = dates['start'].year .. '-' .. dates['start'].month .. '-' .. string.format("%02d", _)         local y, m, d = stamp:match("(%d+)%-(%d+)%-(%d+)")         local t = { year = y, month = m, day = d}          csv = string.format('%q,%q,%q', os.date("%A",os.time(t)), "" .. string.format("%02d", _) .. "-" .. string.format("%02d", dates['start'].month) .. "-" .. dates['start'].year, row)         table.insert(buffer, csv)   end     table.insert(buffer, '""')     table.insert(buffer, '"##### END OF TREND ' .. _ .. ': ' .. trend_name .. ' #####"')     table.insert(buffer, '""') end src = 'Trend Export '.. os.date('%Y-%m-%d %H#%M#%S') .. '.csv' dst = '/home/ftp/' .. src io.writefile(dst, buffer) local ftp = require("socket.ftp") local ltn12 = require("ltn12") -- Indiquer le dossier du serveur FTP dans lequel vous souhaitez mettre le fichier CSV des courbes target = '/EXPORT/Courbes/' .. src --Indiquer HOST / USER / PASSWORD f, e = ftp.put{   host = "192.168.54.246",   user = "FTP-User",   password = "my_password",   type = "i",   argument = target,   source = ltn12.source.file(io.open(dst, "rb"))   } if (e) then   log (e)   log (f)   alert("Could not ftp: ", e, "\n") end log("ftp_trends") os.remove(dst)
Thank you for your understanding.
Best regards.
(19.09.2022, 07:43)Gadjoken Wrote: Hello,
Best regards.
I am doing the same here on an ftp I have set up. I can modify the directories and add files from remote computer with the user I have set up, but when I try to write from SL I get "550 Permission denied". Any idea why?
I have disabled the FW on the remote computer. I get no error when connecting (tried with wrong user/pw, and then I get the expected login-failure).
Have you checked that you can upload files to the same directory that the script puts files to? You can also try changing type = "i", to command = "appe",
(16.01.2023, 14:12)admin Wrote: Have you checked that you can upload files to the same directory that the script puts files to? You can also try changing type = "i", to command = "appe",
Still get Permission denied.
I see that the supported types are I, I N, A, A N and L 8. What does the different mean? I tried A, thinking it means "append" and A N, thinking it means "Append new", but that might not be correct.
Try uploading to the root directory and check that the user has all required permissions. You can start by giving all permissions to check if it works at all.
(16.01.2023, 14:20)admin Wrote: Try uploading to the root directory and check that the user has all required permissions. You can start by giving all permissions to check if it works at all.
Not entirely sure what I had wrong, but it works now. It might have been some misspelling in the script, but I did a lot of copy/paste now when testing, so not sure what I had to start with.
Anyway, it works now.