Help me creat feedbacks
Hello, I have a problem with Logic Machine 5 Lite. The devices I have in my KNX bus system are very old and do not have group addresses for feedbacks. As a result, the objects I create do not have feedbacks. This means that the status of a luminaire or other switch object is not updated, so I do not have in my management the actual condition of the house. If I am in a remote area I can not know what the real condition of my house is. Is there a way to create virtual feedbacks?
You should do it in ETS and configure your knx devices to send feedback. After that you can import it to LM.
You can make simple status mapping via a single script. Add feedback tag to all control objects and map an event script to this tag.
Fill mapping table as needed. Table key (1/1/1, 1/1/3 etc) is the control address, key value is either a single status object address or a table containing multiple addresses.
123456789101112131415161718
mapping = {   ['1/1/1'] = { '1/1/2', '1/1/9' },     ['1/1/3'] = '1/1/4',   ['1/1/5'] = '1/1/6', } status = mapping[ event.dst ] if type(status) == 'string' then   status = { status } end if type(status) == 'table' then   value = event.getvalue()      for _, addr in ipairs(status) do     grp.checkupdate(addr, value)       end end
You will need additional scripts for more complex situations like setting light value to 0% should set binary status to Off.