Script to calculate how many
Hi guys,
Please, I need help with a script that should calculate how many thermostats are on a specific mode (Comfort,Economy,Away), I have about 120 thermostat and each thermostat have a 1byte unsigned integer DPT for the HVAC Mode (1 == Comfort, 2 == Away, 3 == Economy)
What I want to display is,
Thermostats on Comfort Mode: 44
Thermostats on Away Mode: 22
etc...
Also, is there any way to block the change temp in the LM5 if the Mode is not on Comfort?
To change temp the user should write a value between -3,+3  and its 2byte floating, you can see the picture attached
You need to tag all thermostat mode objects with therm-mode tag then the total count per mode can be calculated like this (either event script attached to this tag or a resident script with at least 5 second sleep time):
counters = {} objects = grp.tag('therm-mode') for _, obj in ipairs(objects) do   value = obj.value   counters[ value ] = (counters[ value ] or 0) + 1 end grp.checkupdate('32/1/1', counters[ 1 ] or 0) -- comfort grp.checkupdate('32/1/2', counters[ 2 ] or 0) -- away grp.checkupdate('32/1/3', counters[ 3 ] or 0) -- economy
There are several options for blocking writes. One option is to use Custom JavaScript to block certain UI elements based on an object value. Another option is to add additional objects with event scripts which pass the value to the control object only when the mode object has a specific value.
(11.04.2022, 12:27)admin Wrote: You need to tag all thermostat mode objects with therm-mode tag then the total count per mode can be calculated like this (either event script attached to this tag or a resident script with at least 5 second sleep time):
Thank you so much for the script,
Could you give one solution for blocking the writing?
Here's an example of blocking via a script and an additional virtual object. Single script can be used for multiple objects when mapped to a tag.
All objects must follow a fixed addressing scheme where the last group address part matches for all three objects.
In this example thermostat mode is 32/1/X, output is 33/1/X, this can be changed as needed.
addr = event.dst:split('/')[3] mode = grp.getvalue('32/1/' .. addr) -- write input value to output only when mode is comfort (1) if mode == 1 then   value = event.getvalue()     grp.checkwrite('33/1/' .. addr, value) end
Thank you admin, but it didn't work for me,
All of my objects is already following a fixed address,
14/4/x is for HVAC Mode, 14/3/X is for Shift set Point
That's what I did
- I added a tag named "shift" for 14/3/12 and created an event-based script with the tag shift
addr = event.dstConfusedplit('/')[3]
mode = grp.getvalue('14/4/' .. addr)
-- write input value to output only when the mode is comfort (1)
if mode == 1 then
grp.checkwrite('14/3/' .. addr, value)
then went to the visulasation and changed the mode to away, and tried to change the temp and it changed
Have I done something wrong?
You need additional virtual objects for this script to work as you cannot block the write that has already happened. For example, 32/1/X that will be used in the visualization and will have the event script attached to it. Depending on the HVAC mode the value will be passed to 14/3/X or not.
(12.04.2022, 11:37)admin Wrote: You need additional virtual objects for this script to work as you cannot block the write that has already happened. For example, 32/1/X that will be used in the visualization and will have the event script attached to it. Depending on the HVAC mode the value will be passed to 14/3/X or not.
Thank you so much  Big Grin