Universal script
Hi, I'm not very knowledgeable about Lua programming. I have several of the same scripts that are different in group addresses. The latter shifts by 1, for example 1/3/10, 1/3/11 etc. Is it possible to write one universal script that would adjust the other addresses in it according to the incoming address and execute?
thanks
example:
roofopenclose = grp.getvalue('2/3/10') --address coming from basalte
roofopen = grp.getvalue ('2/3/200') --address for the actuator
roofclose = grp.getvalue ('2/3/201') -- address for the actuator
if roofopenclose == false then
  grp.write('2/3/200',1) --command OPEN for ROOF 1 actuator
  os.sleep(1) --long push
  grp.write('2/3/200',0) --command for actuator
elseif roofopenclose == true then
  grp.write('2/3/201',1) --command CLOSE for ROOF 1 actuator
  grp.write('2/3/201',0) --command for actuator
Add to Common functions:
function longpress(event, shift)   local dst = event.dstraw + shift   if event.getvalue() then     dst = dst + 1   end   grp.write(dst, true)   os.sleep(1)   grp.write(dst, false)   end
Add event script to 2/3/10:
longpress(event, 190)
If you have a fixed address shift of 190 (2/3/10 -> 2/3/200 and 2/3/201) then you can add a common tag to all source objects (2/3/10, 2/3/11, 2/3/12 etc) and map a single event script to this tag.
Thank you admin, but I didn't express myself accurately. Group address 2/3/10 triggers the event script with addresses 2/3/200 and 2/3/201. Group address 2/3/11 runs an event script with addresses 2/3/202 and 2/3/203, address 2/3/12 runs an event script with addresses 2/3/204 and 2/3/205 ...etc. Is it possible to have one script?
The calculation was wrong in the previous example.
Add a common tag to input objects (2/3/10, 2/3/11, 2/3/12 etc) and map an event script to this tag (no need to add anything to Common functions).
basein = buslib.encodega('2/3/10') baseout = buslib.encodega('2/3/200') dst = baseout + 2 * (event.dstraw - basein) if event.getvalue() then   dst = dst + 1 end grp.write(dst, true) os.sleep(1) grp.write(dst, false)
