FAN Coil Control
Hi Admin ;
  I'm using KNX switch acuators to control FCU in a project.Each fan coil has three fan stages.
My customer wants an additional PID control.KNX termostats do the PID works on itself outputs in percintiles.
The problem is there is 81 FCU on field and i'm writing 5 scripts for every fancoil ( for on/off status , fan status , auto status and selecting the right fan step with PID output.)  There is 553 event script on Logic Machine i know it's not efficient.
 Logic machine CPU I/O values are 1.38 / 1.35 / 1.49 and connected KNX bus over IP router , group monitor calculated 28.9 telegrams per second.
 What is the best approach for controlling these FCU for you ?
12345678910111213141516171819202122232425262728293031
value = event.getvalue() oto = grp.getvalue('24/0/22') heat1 = grp.getvalue('24/0/20') if ( oto == true ) and ( heat1 == true ) and ( value > 0 ) and ( value <= 33 ) then   grp.write('24/0/45', 9) end if ( oto == true ) and ( heat1 == true ) and ( value > 33 ) and ( value <= 66 ) then   grp.write('24/0/45', 10)   end if ( oto == true ) and ( heat1 == true ) and ( value > 66 ) then   grp.write('24/0/45', 11) end if ( oto == true ) and ( heat1 == true ) and ( value == 0 ) then   grp.write('24/0/45', 8) end
I think you just asking LM for too much and should spread this logic over more LMs.