07.10.2022, 12:55
A new version of the modbus slave script where you can freely define coil/registers and even use bigger data-types and multiple slaves.
Data-types supported:
[ dt.bool ] = 1,
[ dt.bit4 ] = 1,
[ dt.int8 ] = 1,
[ dt.uint8 ] = 1,
[ dt.int16 ] = 1,
[ dt.uint16 ] = 1,
[ dt.float16 ] = 1,
[ dt.int32 ] = 2,
[ dt.uint32 ] = 2,
[ dt.float32 ] = 2,
[ dt.int64 ] = 4,
The number next to DPT is representing how many registers will be used per object. It means if int64 is used make sure to leave gap for 4 registers in the mapping table.
Only 2023 firmware and newer is supported
1. Create user library mbslave and past this code:
2a. For Modbus TCP slave create resident script with 0 interval and set object mapping in the table. Remember to create gap in registers for 32 and 64 bit objects.
2b. For Modbus RTU slave create resident script with 0 interval and set object mapping in the table. Remember to create gap in registers for 32 and 64 bit objects. Change serial port settings in mbrtu:open as needed.
[ dt.bool ] = 1,
[ dt.bit4 ] = 1,
[ dt.int8 ] = 1,
[ dt.uint8 ] = 1,
[ dt.int16 ] = 1,
[ dt.uint16 ] = 1,
[ dt.float16 ] = 1,
[ dt.int32 ] = 2,
[ dt.uint32 ] = 2,
[ dt.float32 ] = 2,
[ dt.int64 ] = 4,
local _M = {}
local byteswap, wordswap
local f16mult = 1
local mapping = {}
local exception = {}
local reply = {}
local fncodes = {
[1] = 'readcoils',
[2] = 'readdiscreteinputs',
[3] = 'readregisters',
[4] = 'readinputregisters',
[5] = 'writecoil',
[6] = 'writeregister',
[15] = 'writecoils',
[16] = 'writeregisters',
local mapfncodes = {
[1] = 'coils',
[2] = 'discreteinputs',
[3] = 'registers',
[4] = 'inputregisters',
[5] = 'coils',
[6] = 'registers',
[15] = 'coils',
[16] = 'registers',
local dtlens = {
[ dt.bool ] = 1,
[ dt.bit4 ] = 1,
[ dt.int8 ] = 1,
[ dt.uint8 ] = 1,
[ dt.int16 ] = 1,
[ dt.uint16 ] = 1,
[ dt.float16 ] = 1,
[ dt.int32 ] = 2,
[ dt.uint32 ] = 2,
[ dt.float32 ] = 2,
[ dt.int64 ] = 4,
local maxpdu = 253
local maxaddr = 0x10000
local coilon = 0xFF00
local limits = {
readbits = 2000,
writebits = 1968,
readregisters = 125,
writeregisters = 123,
local excodes = {
illegalfunction = 1,
illegaldataaddress = 2,
illegaldatavalue = 3,
serverdevicefailure = 4,
acknowledge = 5,
serverdevicebusy = 6,
negativeacknowledge = 7,
memoryparityerror = 8,
gatewaypathunavailable = 10,
gatewaytargetdevicefailed = 11,
local handlers = {}
local function touint8(buf, off)
return buf:byte(off)
local function touint16(buf, off, swap)
local b1, b2 = buf:byte(off, off + 1)
if swap then
b1, b2 = b2, b1
return b1 * 0x100 + b2
local function getmapping(slaveid, fncode)
local mapfncode = mapfncodes[ fncode ]
local slave = mapping[ slaveid ]
if not slave then
slave = mapping['*']
if slave then
return slave[ mapfncode ]
local function readbits(slaveid, fncode, data)
if #data ~= 4 then
return
local addr = touint16(data, 1)
local count = touint16(data, 3)
if count == 0 or count > limits.readbits then
return excodes.illegaldataaddress
elseif (addr + count) > maxaddr then
local map = getmapping(slaveid, fncode)
if not map then
local res = {}
local bits, byte = 0, 0
for i = 0, (count - 1) do
local mapaddr = map[ addr + i ]
if mapaddr then
local bval = grp.getvalue(mapaddr)
if toboolean(bval) then
byte = byte + bit.lshift(1, bits)
bits = bits + 1
if bits == 8 then
res[ #res + 1 ] = string.char(byte)
bits, byte = 0, 0
if bits ~= 0 then
return string.char(#res) .. table.concat(res)
local zeroreg = string.char(0, 0)
local function readvalue(res, value, dpt)
if dpt == dt.float16 then
value = value * f16mult
dpt = dt.int16
local enc = busdatatype.encode(value, dpt)
if not enc.dataraw then
return
local raw = enc.dataraw
if #raw % 2 == 1 then
raw = string.char(0) .. raw
local words = #raw / 2
local offset = #res
for i = 1, words do
local word = raw:sub(i * 2 - 1, i * 2)
if byteswap then
word = word:sub(2, 2) .. word:sub(1, 1)
if wordswap then
res[ offset + i ] = word
res[ offset + 1 + words - i ] = word
return true
local function readregisters(slaveid, fncode, data)
if #data ~= 4 then
return
if count == 0 or count > limits.readregisters then
if not map then
local res = {}
local max = count - 1
while #res <= max do
local mapobj = map[ addr + #res ]
local success
if mapobj then
local value = grp.getvalue(mapobj.address)
if type(value) == 'boolean' then
value = value and 1 or 0
if type(value) ~= 'number' then
alert('invalid value ' .. mapobj.address .. ' ' .. tostring(value))
value = 0
success = readvalue(res, value, mapobj.dpt)
if not success then
res[ #res + 1 ] = zeroreg
if #res ~= count then
return string.char(count * 2) .. table.concat(res)
local function writevalue(obj, data, offset)
local words = obj.len
local len = words * 2
local raw = data:sub(offset, offset + len - 1)
if #raw < len then
return
local buf = {}
for i = 1, words do
local word = touint16(raw, i * 2 - 1, byteswap)
local hex = string.format('%04X', word)
if wordswap then
buf[ #buf + 1 ] = hex
table.insert(buf, 1, hex)
local hexval = table.concat(buf)
local dpt = obj.dpt == dt.float16 and dt.int16 or obj.dpt
local value = busdatatype.decode(hexval, dpt)
if obj.dpt == dt.float16 then
value = value / f16mult
grp.write(obj.address, value)
handlers.readcoils = readbits
handlers.readdiscreteinputs = readbits
handlers.readregisters = readregisters
handlers.readinputregisters = readregisters
handlers.writecoil = function(slaveid, fncode, data)
if #data ~= 4 then
return
if not map or not map[ addr ] then
local bval = touint16(data, 3) == coilon
grp.write(map[ addr ], bval, dt.bool)
return data
handlers.writeregister = function(slaveid, fncode, data)
if #data ~= 4 then
return
local mapobj = map[ addr ]
if mapobj.len ~= 1 then
writevalue(mapobj, data, 3)
return data
handlers.writecoils = function(slaveid, fncode, data)
if #data < 5 then
return
local bytes = touint8(data, 5)
if #data ~= (bytes + 5) then
return
if count == 0 or count > limits.writebits or bytes ~= math.ceil(count / 8) then
if not map then
local offset = 6
local byte = data:byte(offset)
local bits = 0
local bval = bit.band(bit.rshift(byte, bits), 1)
if mapaddr then
grp.write(mapaddr, bval, dt.bool)
bits = bits + 1
if bits == 8 then
bits = 0
offset = offset + 1
return data:sub(1, 4)
handlers.writeregisters = function(slaveid, fncode, data)
if #data < 5 then
return
return
if count == 0 or count > limits.writeregisters or bytes ~= count * 2 then
if not map then
local mapobj = map[ addr + i ]
if mapobj and not mapobj.readonly then
local offset = 6 + i * 2
writevalue(mapobj, data, offset)
exception.tcp = function(sock, hdr, excode)
local fncode = bit.bor(0x80, hdr:byte(8))
local resp = hdr:sub(1, 4) ..
string.char(0, 3) ..
hdr:sub(7, 7) ..
string.char(fncode, excode)
return sock:send(resp)
exception.rtu = function(mbrtu, hdr, excode)
local fncode = bit.bor(0x80, hdr:byte(2))
local resp = hdr:sub(1, 1) ..
return mbrtu:send(resp)
reply.tcp = function(sock, hdr, data)
string.char(0, #data + 2) ..
hdr:sub(7, 8) .. data
reply.rtu = function(mbrtu, hdr, data)
local resp = hdr:sub(1, 2) .. data
local function handler(mode, ctx, hdr, data)
local slaveid, fncode = hdr:byte(#hdr - 1, #hdr)
local fnname = fncodes[ fncode ]
if not fnname then
return exception[ mode ](ctx, hdr, excodes.illegalfunction)
local res = handlers[ fnname ](slaveid, fncode, data)
if type(res) == 'number' then
return exception[ mode ](ctx, hdr, res)
elseif type(res) == 'string' then
return reply[ mode ](ctx, hdr, res)
_M.tcphandler = function(sock)
local hdr, err = sock:receive(8)
if not hdr then
return nil, err
local len = touint16(hdr, 5) - 2
local data
if len <= 0 or len > maxpdu then
err = 'protocol error'
data, err = sock:receive(len)
if not data then
return nil, err
return handler('tcp', sock, hdr, data)
_M.rtuhandler = function(mbrtu)
local data, err = mbrtu:receive()
if not data then
return nil, err
local slaveid = data:byte(1)
if not mapping[ slaveid ] then
return
return handler('rtu', mbrtu, data:sub(1, 2), data:sub(3, #data - 2))
_M.setswap = function(swap)
byteswap = swap:find('b') ~= nil
wordswap = swap:find('w') ~= nil
_M.setfloat16precision = function(prec)
prec = tonumber(prec) or 0
f16mult = math.pow(10, prec)
local function initobject(obj, dbobj)
local dpt = obj.datatype or dbobj.datatype
if type(dpt) == 'string' then
dpt = dt[ dpt ] or 0
if type(dpt) == 'number' and dpt >= 1000 then
dpt = math.floor(dpt / 1000)
obj.dpt = dpt
obj.len = dtlens[ dpt ]
obj.address = dbobj.address
if not obj.len then
alert('invalid data type ' .. obj.address .. ' ' .. tostring(dpt))
return
return obj
local function initobjects(objects)
if type(objects) ~= 'table' then
return
for addr, obj in pairs(objects) do
if type(obj) == 'string' then
obj = { address = obj }
local dbobj = grp.find(obj.address)
if dbobj then
obj = initobject(obj, dbobj)
alert('missing object ' .. obj.address)
obj = nil
objects[ addr ] = obj
_M.setmapping = function(map)
for _, smap in pairs(map) do
initobjects(smap.registers)
initobjects(smap.inputregisters)
mapping = map
return _M2a. For Modbus TCP slave create resident script with 0 interval and set object mapping in the table. Remember to create gap in registers for 32 and 64 bit objects.
local mb = require('user.mbslave')
local copas = require('copas')
local address = '*'
local port = 502
local server = assert(socket.bind(address, port))
mb.setmapping({
coils = {
[0] = '0/0/1',
[1] = '1/1/1',
[2] = '1/1/2',
registers = {
[0] = '1/1/4',
[1] = '1/1/10',
[3] = '32/1/6',
[5] = '32/1/13',
mb.setswap('w')
mb.setfloat16precision(2)
local function handler(sock)
copas.setErrorHandler(log)
sock = copas.wrap(sock)
sock:settimeout(60)
while true do
local res, err = mb.tcphandler(sock)
if not res then
break
sock:close()
copas.addserver(server, handler, 60)
copas.loop()2b. For Modbus RTU slave create resident script with 0 interval and set object mapping in the table. Remember to create gap in registers for 32 and 64 bit objects. Change serial port settings in mbrtu:open as needed.
local mbrtu = require('luamodbus').rtu()
mbrtu:open('/dev/RS485-1', 9600, 'E', 8, 1, 'H')
mbrtu:connect()
mbrtu:setslave('*') -- '*' handles multiple RTU slave IDs
mb.setmapping({
[1] = {
coils = {
[0] = '0/0/1',
[1] = '1/1/1',
[2] = '1/1/2',
registers = {
[0] = '1/1/4',
[1] = '1/1/10',
[3] = '32/1/6',
[5] = '32/1/13',
mb.setswap('w')
while true do
mb.rtuhandler(mbrtu)
This is slave script, it does not read anything. Your master is responsible for reading. In there you define how it reads. Nothing to do with LM.