Modbus - AEROTEMPER
Attached you'll find a MODBUS RTU manual for an AEROTEMPER.
I did integrate a couple of Modbus devices before but the register list for this device is different from what I'm used to.
Can you advise on how I can determine the function of each register, whether it's a coil, discrete input, holding register, or input register? Additionally, can you provide information on the address of each register?
Thankful in advance
.pdf   r674008-manual_volcano_wing_modbus_hy_en.pdf (Size: 788.5 KB / Downloads: 23)
Holding register with uint16 data type. Use Read test to check that the values that you read are correct. You might need to do address - 1 for each register.
(12.05.2023, 07:18)admin Wrote: Holding register with uint16 data type. Use Read test to check that the values that you read are correct. You might need to do address - 1 for each register.
The read test works fine and I can read the registers but when i added the device  the lm5 show it as its not found, please see attached
Provide your profile and check what you get in Modbus Error log.
(21.06.2023, 10:25)admin Wrote: Provide your profile and check what you get in Modbus Error log.
No errors , attached the profile
.json   mittet.json (Size: 1.42 KB / Downloads: 12)
What parameters did you use in Read test, it is not visible due to result.
(21.06.2023, 10:34)Daniel Wrote: What parameters did you use in Read test, it is not visible due to result.
Are you sure about the Error log? There's a log specific to Modbus, not global Error log.
(21.06.2023, 10:37)admin Wrote: Are you sure about the Error log? There's a log specific to Modbus, not global Error log.
Oups, this is the errors then
Map only the first register to an object and see if you get a reading.
(21.06.2023, 10:43)admin Wrote: Map only the first register to an object and see if you get a reading.
yes it worked
See this: https://forum.logicmachine.net/showthread.php?tid=4718
(21.06.2023, 11:01)admin Wrote: See this: https://forum.logicmachine.net/showthread.php?tid=4718
I increased the pool interval to 20s and timeout to 5 also add read_delay to all the register by 0.1 . nothing helped
read_delay is a global setting: https://forum.logicmachine.net/showthrea...3#pid13343
(21.06.2023, 11:46)admin Wrote: read_delay is a global setting: https://forum.logicmachine.net/showthrea...3#pid13343
Thanks a lot