Posts: 270
Threads: 72
Joined: May 2017
Reputation:
0
Hi, I have to interrogate and command about fifty modbus devices, spread over different floors of a building.
How many LMs would I need to optimize loads and how can I implement a single supervision interface for all equipment?
Any suggestion is welcome
Thanks
Peppe
Posts: 4646
Threads: 24
Joined: Aug 2017
Reputation:
207
One LM would do but via two lines, one can have up to 31 devices. Do not expect this to work fast.
------------------------------
Ctrl+F5
Posts: 4646
Threads: 24
Joined: Aug 2017
Reputation:
207
Yes
------------------------------
Ctrl+F5
Posts: 7764
Threads: 42
Joined: Jun 2015
Reputation:
447
Use one LM for visualization and exchange data with other LMs via KNX/IP. No extra configuration is needed for this but adjust filtering tables is recommended to lower the system load.
On Modbus side make sure that GND is connected between all devices and that bus topology is used.
Posts: 270
Threads: 72
Joined: May 2017
Reputation:
0
20.09.2023, 07:12
(This post was last modified: 20.09.2023, 07:43 by gdimaria.)
ok thank you so much
Peppe
Just a doubt: currently the LM "master" is in TP UART with KNX IP features on. The other LMs with modbus devices are also in TP UART with KNX IP feature off. Do you mean I have to activate it? Thanks again
Posts: 7764
Threads: 42
Joined: Jun 2015
Reputation:
447
If several LMs are connected to the same TP line then IP features must only be enabled on one LM. Otherwise you should enable IP features on all LMs and it's recommended to enable encryption as well. If LM does not have TP connection then switch connection mode to IP routing.