This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Error - Operation in progress - MODBUS TCP/IP
#1
Hi,

I received the attached error when I tried to use the read-test or using profiles

 Do you have any idea how to solve it?

Attached Files Thumbnail(s)
       
Reply
#2
Enable persistent connection mode in the device settings. This error is caused by the Modbus device supporting only a small number of open TCP connections. You can also try rebooting the Modbus device if the error persists.
Reply
#3
(20.06.2024, 11:40)admin Wrote: Enable persistent connection mode in the device settings. This error is caused by the Modbus device supporting only a small number of open TCP connections. You can also try rebooting the Modbus device if the error persists.

I still have the same error (I rebooted the LM5),  I get the same error even when I try to read data from an invalid IP.

The communication was okay until the Modbus device went offline for 1 month.
Reply
#4
Reboot the Modbus slave device. Rebooting LM won't solve this issue.
Reply
#5
(20.06.2024, 11:52)admin Wrote: Reboot the Modbus slave device. Rebooting LM won't solve this issue.

Same
Reply
#6
Then it seems your slave is broken
------------------------------