This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus value_delta
#1
We believe we have a problem related to the "value_delta" parameter when reading modbus registers.
Is this coefficient evaluated after the multiplication factor?
For example, if I read a power value in W and convert it to kW with a "value_multiplier" of 0.001, is the default/minimum factor 0.2 applied to the kW value? In this case the minimum value of 0.2 may be too large.

Thanks
Reply
#2
Delta check happens after all calculations are done. The difference between the current object value and the new value is checked.
Reply
#3
Ok, but if I enter a "value_delta" value less than 0.2 in the modbus profile, which one will be used?

Thaks
Reply
#4
Right now it cannot be set lower than 0.2. This will be changed in the next version. We'll publish an updated Modbus package once it's ready.
Reply
#5
Install updated Package via System config-System-Package
https://dl.openrb.com/pkg/genohm-scada-m...1_imx6.ipk
https://dl.openrb.com/pkg/genohm-scada-m...1_imx6.sig

Clear browser cache after installation.
------------------------------
Ctrl+F5