We are working on a project with 4 lines, 4 IP Routers and 1 LM.
When we configure LM with the following settings*(attached photo), the multicast connection is interrupted and the IP routers are not shown in ETS- KNX Connections. No filters are active.
Why this happens?
Can you run Wireshark on your PC and provide traffic capture for both cases - when LM is connected or not?
Use this filter: _ws.col.protocol=="KNXnet/IP"
Export using File > Export Specified Packats, make sure that only [b]Displayed" packets are exported.
(22.07.2024, 08:33)admin Wrote: Can you run Wireshark on your PC and provide traffic capture for both cases - when LM is connected or not?
OK, thank you for the response.
The project is far away, so we will try it when we are there.
Tunneling allows only one-to-one connections while Routing (multicast) allows communication between multiple KNX/IP devices on the same network. If you have more than 2 KNX/IP devices then multicast must be used.
Hello!
The issue we had, has been solved.
The router, by default, didn't allow multicast communication. That was the reason.
Thank you for your time and responses.