Hello.
A few months ago, I integrated Philips Hue lighting fixtures that support dimming, color temperature change, and RGB. Everything works perfectly, except I hadn't set up the feedback for the light fixture's state if you change it from the Philips Hue app. Before posting on the forum, I carefully reviewed all topics related to this issue. I am using "user.hue v5.lua" and "resident hue feedback v2.lua". The on/off, dimming, and RGB feedback work perfectly. However, neither the color temperature change itself nor its feedback are working correctly. For example, I set 2000K from W4K, and in the Hue app, it shows a completely different color. The feedback also doesn't work. When I disable the feedback script, the color temperature control works correctly. I am using the following script. Please help me find where I am going wrong. I have spent over 2 days on this problem without a resolution.
Regards,
Nayden
Code: -- Set name (Lookup in HUE app under light configuration) and feedback adresses (don't change statevalue, brivalue and colorvalue as they are used as memoryfield)
addressmapping = {
-- Name -- On/Off FB -- Bright FB -- Color FB
['Cove lighting-cr'] = {state = '1/0/9', bri = '32/2/9', rgb = '32/3/9', ct = '32/4/9', statevalue = '', brivalue = '', colorvalue = '', ctvalue = ''}
}
-- Set polling interval in seconds
interval = 1
-- Use logging
logging = false
-- Load needed lib's
require('user.hue')
require('json')
-- loop indefenitly
while true do
reply = getHueLights()
mylamps = json.decode(reply)
for _, item in pairs(mylamps) do
-- Check if lamp is found by bridge otherwise it make no sense to send commands
if item.state.reachable == true then
-- On/Off
name = addressmapping[item.name]
if name then
addr = addressmapping[item.name]['state']
if addr and addr ~= '' then
currentvalue = addressmapping[item.name]['statevalue']
if currentvalue ~= item.state.on then
grp.write(addr, item.state.on)
addressmapping[item.name]['statevalue'] = item.state.on
if logging == true then
log('lamp ' .. item.name .. ' state is: ' .. tostring(item.state.on))
end
end
end
end
--Brightness
if item.state.bri then
name = addressmapping[item.name]
if name then
addr = addressmapping[item.name]['bri']
if addr and addr ~= '' then
-- Check if lamp is on otherwise overrule BRI value to 0
if item.state.on == false then
item.state.bri = 0
end
currentvalue = addressmapping[item.name]['brivalue'] or 0
if currentvalue ~= item.state.bri then
grp.write(addr, math.floor((tonumber(item.state.bri)/2.55) + 0.5))
addressmapping[item.name]['brivalue'] = item.state.bri
if logging == true then
log('lamp ' .. item.name .. ' brightness is: ' .. math.floor((tonumber(item.state.bri)/2.55) + 0.5) .. ' %')
end
end
end
end
end
-- Color temperature
name = addressmapping[item.name]
if name and item.state.ct then
addr = addressmapping[item.name]['ct']
if addr and addr ~= '' then
newvalue = math.floor(1000000 / item.state.ct)
currentvalue = addressmapping[item.name]['ctvalue']
if currentvalue ~= newvalue then
grp.update(addr, newvalue)
addressmapping[item.name]['ctvalue'] = newvalue
if logging == true then
log('lamp ' .. item.name .. ' color temperature is: ' .. newvalue .. ' K')
end
end
end
end
--Color
if item.state.ct or item.state.xy then
name = addressmapping[item.name]
if name then
addr = addressmapping[item.name]['rgb']
if addr and addr ~= '' then
-- Check if lamp is on otherwise overrule color value to 0
if item.state.on == false then
colorvalue = 0
end
if item.state.colormode == 'xy' then
currentvalue = addressmapping[item.name]['colorvalue']
colorvalue = xy_to_rgb(item.state.xy[1],item.state.xy[2],item.state.bri)
--colorvalue = xyz_to_rgb((item.state.xy[1] * 100), (item.state.xy[2] * 100))
if currentvalue ~= colorvalue then
grp.checkwrite(addr, colorvalue)
addressmapping[item.name]['colorvalue'] = colorvalue
if logging == true then
log('lamp ' .. item.name .. ' color is: ' .. colorvalue)
end
end
elseif item.state.colormode == 'ct' then
currentvalue = addressmapping[item.name]['colorvalue']
--colortemp = math.floor((item.state.ct / 0.0769) + 0.5) --0.0769230769230769
colortemp = math.abs((item.state.ct - 500) / 2)
colortemp = math.floor(colortemp + 0.5)
colortemp = 80 + colortemp
if colortemp > 255 then
colortemp = 255
end
r = lmcore.inttohex(255, 1)
g = lmcore.inttohex(255, 1)
b = lmcore.inttohex(colortemp, 1)
rgb = r .. g .. b
colortemp = lmcore.hextoint(rgb,3)
if currentvalue ~= colortemp then
--colortempconverted = ct_to_rgb(colortemp)
grp.write(addr, colortemp)
addressmapping[item.name]['colorvalue'] = colortemp
if logging == true then
log('lamp ' .. item.name .. ' color is: ' .. colortemp)
end
end
end
end
end
end
end
end
-- Delay loop
os.sleep(interval)
end
Posts: 8256
Threads: 44
Joined: Jun 2015
Reputation:
476
Log the status reply and post what you have there.
Posts: 28
Threads: 4
Joined: Oct 2022
Reputation:
0
(23.07.2025, 13:06)admin Wrote: Log the status reply and post what you have there.
Hello,
I'm noticing that when I change the color temperature, the RGB parameter also changes.
Regards,
Nayden
Curent logs:
apit3 (app daemon) 23.07.2025 16:11:39
* arg: 1
* string: [DEBUG]
* arg: 2
* string: publish_message(): response=
* arg: 3
* number: 2092
* arg: 4
* string: , err=
* arg: 5
* nil
apit3 (app daemon) 23.07.2025 16:11:39
* arg: 1
* string: [DEBUG]
* arg: 2
* string: Sending message #_publishDatapointsValues succed: 2092
apit3 (app daemon) 23.07.2025 16:14:02
* arg: 1
* string: [DEBUG]
* arg: 2
* string: publish_message(): response=
* arg: 3
* number: 2092
* arg: 4
* string: , err=
* arg: 5
* nil
apit3 (app daemon) 23.07.2025 16:14:02
* arg: 1
* string: [DEBUG]
* arg: 2
* string: Sending message #_publishDatapointsValues succed: 2092
apit3 (app daemon) 23.07.2025 16:14:03
* arg: 1
* string: [DEBUG]
* arg: 2
* string: publish_message(): response=
* arg: 3
* number: 2092
* arg: 4
* string: , err=
* arg: 5
* nil
apit3 (app daemon) 23.07.2025 16:14:03
* arg: 1
* string: [DEBUG]
* arg: 2
* string: Sending message #_publishDatapointsValues succed: 2092
apit3 (app daemon) 23.07.2025 16:14:19
* arg: 1
* string: [DEBUG]
* arg: 2
* string: publish_message(): response=
* arg: 3
* number: 2092
* arg: 4
* string: , err=
* arg: 5
* nil
apit3 (app daemon) 23.07.2025 16:14:19
* arg: 1
* string: [DEBUG]
* arg: 2
* string: Sending message #_publishDatapointsValues succed: 2092
apit3 (app daemon) 23.07.2025 16:14:20
* arg: 1
* string: [DEBUG]
* arg: 2
* string: publish_message(): response=
* arg: 3
* number: 2092
* arg: 4
* string: , err=
* arg: 5
* nil
apit3 (app daemon) 23.07.2025 16:14:20
* arg: 1
* string: [DEBUG]
* arg: 2
* string: Sending message #_publishDatapointsValues succed: 2092
Current errors:
23 23.07.2025 15:55:20
Resident script:143: attempt to perform arithmetic on local 'current_color_value' (a string value)
stack traceback:
123 23.07.2025 15:55:30
Resident script:143: attempt to perform arithmetic on local 'current_color_value' (a string value)
stack traceback:
123 23.07.2025 15:55:41
Resident script:143: attempt to perform arithmetic on local 'current_color_value' (a string value)
stack traceback:
123 23.07.2025 15:55:53
Resident script:143: attempt to perform arithmetic on local 'current_color_value' (a string value)
stack traceback:
123 23.07.2025 15:56:06
Resident script:143: attempt to perform arithmetic on local 'current_color_value' (a string value)
stack tracebac
Posts: 8256
Threads: 44
Joined: Jun 2015
Reputation:
476
Post your whole script. What is at line 143? Log the current_color_value variable value.
Posts: 28
Threads: 4
Joined: Oct 2022
Reputation:
0
(23.07.2025, 13:38)admin Wrote: Post your whole script. What is at line 143? Log the current_color_value variable value.
Apologies, but those errors were from the previous script I was testing. I uploaded the new one at 4:10 PM, and its last line is number 132.
Posts: 8256
Threads: 44
Joined: Jun 2015
Reputation:
476
In this case log mylamps variable value after line 20.
Posts: 28
Threads: 4
Joined: Oct 2022
Reputation:
0
(23.07.2025, 13:45)admin Wrote: In this case log mylamps variable value after line 20.
Apologize in advance, but I'm not sure I understood exactly what I need to do.
Posts: 5102
Threads: 28
Joined: Aug 2017
Reputation:
231
add log(mylamps) after line 20 in your script
------------------------------
Ctrl+F5
Posts: 28
Threads: 4
Joined: Oct 2022
Reputation:
0
(23.07.2025, 14:25)Daniel Wrote: add log(mylamps) after line 20 in your script
Hello,
After I inserted log(mylamps) after line 20 in my script, the result is:
Code: Hue feedback 24.07.2025 11:17:24
* table:
["23"]
* table:
["swversion"]
* string: 1.122.8
["swconfigid"]
* string: 24EB3638
["uniqueid"]
* string: 00:17:88:01:0c:a0:12:e7-0b
["capabilities"]
* table:
["control"]
* table:
["colorgamut"]
* table:
[1]
* table:
[1]
* number: 0.6915
[2]
* number: 0.3083
[2]
* table:
[1]
* number: 0.17
[2]
* number: 0.7
[3]
* table:
[1]
* number: 0.1532
[2]
* number: 0.0475
["ct"]
* table:
["min"]
* number: 153
["max"]
* number: 500
["colorgamuttype"]
* string: C
["maxlumen"]
* number: 350
["mindimlevel"]
* number: 200
["streaming"]
* table:
["renderer"]
* bool: true
["proxy"]
* bool: true
["certified"]
* bool: true
["swupdate"]
* table:
["state"]
* string: noupdates
["lastinstall"]
* string: 2025-07-17T11:37:04
["productid"]
* string: Philips-LCG002-3-GU10ECLv2
["manufacturername"]
* string: Signify Netherlands B.V.
["productname"]
* string: Hue Centris spot
["modelid"]
* string: 5060730P7_02
["state"]
* table:
["ct"]
* number: 369
["reachable"]
* bool: true
["alert"]
* string: select
["on"]
* bool: false
["bri"]
* number: 254
["mode"]
* string: homeautomation
["colormode"]
* string: ct
["hue"]
* number: 8401
["sat"]
* number: 142
["effect"]
* string: none
["xy"]
* table:
[1]
* number: 0.459
[2]
* number: 0.4103
["type"]
* string: Extended color light
["name"]
* string: Centris spot 1
["config"]
* table:
["startup"]
* table:
["mode"]
* string: safety
["configured"]
* bool: true
["function"]
* string: mixed
["archetype"]
* string: huecentris
["direction"]
* string: omnidirectional
["28"]
* table:
["swversion"]
* string: 1.122.8
["swconfigid"]
* string: 49730BB6
["uniqueid"]
* string: 00:17:88:01:0b:f3:74:80-0b
["capabilities"]
* table:
["control"]
* table:
["colorgamut"]
* table:
[1]
* table:
[1]
* number: 0.6915
[2]
* number: 0.3083
[2]
* table:
[1]
* number: 0.17
[2]
* number: 0.7
[3]
* table:
[1]
* number: 0.1532
[2]
* number: 0.0475
["ct"]
* table:
["min"]
* number: 153
["max"]
* number: 500
["colorgamuttype"]
* string: C
["maxlumen"]
* number: 1600
["mindimlevel"]
* number: 40
["streaming"]
* table:
["renderer"]
* bool: true
["proxy"]
* bool: true
["certified"]
* bool: true
["swupdate"]
* table:
["state"]
* string: noupdates
["lastinstall"]
* string: 2025-07-17T11:37:00
["productid"]
* string: Philips-LCL001-1-LedStripsv4
["manufacturername"]
* string: Signify Netherlands B.V.
["productname"]
* string: Hue lightstrip plus
["modelid"]
* string: LCL001
["state"]
* table:
["ct"]
* number: 156
["reachable"]
* bool: true
["alert"]
* string: select
["on"]
* bool: false
["bri"]
* number: 254
["mode"]
* string: homeautomation
["colormode"]
* string: ct
["hue"]
* number: 41432
["sat"]
* number: 75
["effect"]
* string: none
["xy"]
* table:
[1]
* number: 0.3143
[2]
* number: 0.3301
["type"]
* string: Extended color light
["name"]
* string: Hue lightstrip plus dining
["config"]
* table:
["startup"]
* table:
["mode"]
* string: safety
["configured"]
* bool: true
["function"]
* string: decorative
["archetype"]
* string: huelightstrip
["direction"]
* string: omnidirectional
["10"]
* table:
["swversion"]
* string: 1400-0001
["uniqueid"]
* string: 00:15:8d:00:08:1d:b9:80-01
["capabilities"]
* table:
["control"]
* table:
["ct"]
* table:
["min"]
* number: 153
["max"]
* number: 370
["streaming"]
* table:
["renderer"]
* bool: false
["proxy"]
* bool: false
["certified"]
* bool: false
["swupdate"]
* table:
["state"]
* string: notupdatable
["lastinstall"]
* string: 2023-06-10T09:10:45
["manufacturername"]
* string: Paulmann Licht
["productname"]
* string: Color temperature light
["modelid"]
* string: 500.46
["state"]
* table:
["ct"]
* number: 255
["reachable"]
* bool: true
["alert"]
* string: select
["mode"]
* string: homeautomation
["colormode"]
* string: ct
["on"]
* bool: false
["bri"]
* number: 254
["type"]
* string: Color temperature light
["name"]
* string: Celling light 3
["config"]
* table:
["function"]
* string: functional
["archetype"]
* string: ceilingsquare
["direction"]
* string: omnidirectional
["5"]
* table:
["swversion"]
* string: 10751203
["uniqueid"]
* string: a4:c1:38:39:f7:b3:aa:56-0b
["capabilities"]
* table:
["control"]
* table:
["ct"]
* table:
["min"]
* number: 158
["max"]
* number: 495
["streaming"]
* table:
["renderer"]
* bool: false
["proxy"]
* bool: false
["certified"]
* bool: false
["swupdate"]
* table:
["state"]
* string: notupdatable
["lastinstall"]
* string: 2023-04-23T16:37:15
["manufacturername"]
* string: GLEDOPTO
["productname"]
* string: Color temperature light
["modelid"]
* string: GL-C-006P
["state"]
* table:
["ct"]
* number: 255
["reachable"]
* bool: true
["alert"]
* string: select
["mode"]
* string: homeautomation
["colormode"]
* string: ct
["on"]
* bool: false
["bri"]
* number: 254
["type"]
* string: Color temperature light
["name"]
* string: Cove lighting
["config"]
* table:
["function"]
* string: mixed
["archetype"]
* string: huelightstrip
["direction"]
* string: omnidirectional
["9"]
* table:
["swversion"]
* string: 1400-0001
["uniqueid"]
* string: 00:15:8d:00:08:1d:bf:a2-01
["capabilities"]
* table:
["control"]
* table:
["ct"]
* table:
["min"]
* number: 153
["max"]
* number: 370
["streaming"]
* table:
["renderer"]
* bool: false
["proxy"]
* bool: false
["certified"]
* bool: false
["swupdate"]
* table:
["state"]
* string: notupdatable
["lastinstall"]
* string: 2023-06-10T09:10:43
["manufacturername"]
* string: Paulmann Licht
["productname"]
* string: Color temperature light
["modelid"]
* string: 500.46
["state"]
* table:
["ct"]
* number: 255
["reachable"]
* bool: true
["alert"]
* string: select
["mode"]
* string: homeautomation
["colormode"]
* string: ct
["on"]
* bool: false
["bri"]
* number: 254
["type"]
* string: Color temperature light
["name"]
* string: Celling light 1
["config"]
* table:
["function"]
* string: functional
["archetype"]
* string: ceilingsquare
[...
Hue feedback 24.07.2025 11:17:25
* table:
["23"]
* table:
["swversion"]
* string: 1.122.8
["swconfigid"]
* string: 24EB3638
["uniqueid"]
* string: 00:17:88:01:0c:a0:12:e7-0b
["capabilities"]
* table:
["control"]
* table:
["colorgamut"]
* table:
[1]
* table:
[1]
* number: 0.6915
[2]
* number: 0.3083
[2]
* table:
[1]
* number: 0.17
[2]
* number: 0.7
[3]
* table:
[1]
* number: 0.1532
[2]
* number: 0.0475
["ct"]
* table:
["min"]
* number: 153
["max"]
* number: 500
["colorgamuttype"]
* string: C
["maxlumen"]
* number: 350
["mindimlevel"]
* number: 200
["streaming"]
* table:
["renderer"]
* bool: true
["proxy"]
* bool: true
["certified"]
* bool: true
["swupdate"]
* table:
["state"]
* string: noupdates
["lastinstall"]
* string: 2025-07-17T11:37:04
["productid"]
* string: Philips-LCG002-3-GU10ECLv2
["manufacturername"]
* string: Signify Netherlands B.V.
["productname"]
* string: Hue Centris spot
["modelid"]
* string: 5060730P7_02
["state"]
* table:
["ct"]
* number: 369
["reachable"]
* bool: true
["alert"]
* string: select
["on"]
* bool: false
["bri"]
* number: 254
["mode"]
* string: homeautomation
["colormode"]
* string: ct
["hue"]
* number: 8401
["sat"]
* number: 142
["effect"]
* string: none
["xy"]
* table:
[1]
* number: 0.459
[2]
* number: 0.4103
["type"]
* string: Extended color light
["name"]
* string: Centris spot 1
["config"]
* table:
["startup"]
* table:
["mode"]
* string: safety
["configured"]
* bool: true
["function"]
* string: mixed
["archetype"]
* string: huecentris
["direction"]
* string: omnidirectional
["28"]
* table:
["swversion"]
* string: 1.122.8
["swconfigid"]
* string: 49730BB6
["uniqueid"]
* string: 00:17:88:01:0b:f3:74:80-0b
["capabilities"]
* table:
["control"]
* table:
["colorgamut"]
* table:
[1]
* table:
[1]
* number: 0.6915
[2]
* number: 0.3083
[2]
* table:
[1]
* number: 0.17
[2]
* number: 0.7
[3]
* table:
[1]
* number: 0.1532
[2]
* number: 0.0475
["ct"]
* table:
["min"]
* number: 153
["max"]
* number: 500
["colorgamuttype"]
* string: C
["maxlumen"]
* number: 1600
["mindimlevel"]
* number: 40
["streaming"]
* table:
["renderer"]
* bool: true
["proxy"]
* bool: true
["certified"]
* bool: true
["swupdate"]
* table:
["state"]
* string: noupdates
["lastinstall"]
* string: 2025-07-17T11:37:00
["productid"]
* string: Philips-LCL001-1-LedStripsv4
["manufacturername"]
* string: Signify Netherlands B.V.
["productname"]
* string: Hue lightstrip plus
["modelid"]
* string: LCL001
["state"]
* table:
["ct"]
* number: 156
["reachable"]
* bool: true
["alert"]
* string: select
["on"]
* bool: false
["bri"]
* number: 254
["mode"]
* string: homeautomation
["colormode"]
* string: ct
["hue"]
* number: 41432
["sat"]
* number: 75
["effect"]
* string: none
["xy"]
* table:
[1]
* number: 0.3143
[2]
* number: 0.3301
["type"]
* string: Extended color light
["name"]
* string: Hue lightstrip plus dining
["config"]
* table:
["startup"]
* table:
["mode"]
* string: safety
["configured"]
* bool: true
["function"]
* string: decorative
["archetype"]
* string: huelightstrip
["direction"]
* string: omnidirectional
["10"]
* table:
["swversion"]
* string: 1400-0001
["uniqueid"]
* string: 00:15:8d:00:08:1d:b9:80-01
["capabilities"]
* table:
["control"]
* table:
["ct"]
* table:
["min"]
* number: 153
["max"]
* number: 370
["streaming"]
* table:
["renderer"]
* bool: false
["proxy"]
* bool: false
["certified"]
* bool: false
["swupdate"]
* table:
["state"]
* string: notupdatable
["lastinstall"]
* string: 2023-06-10T09:10:45
["manufacturername"]
* string: Paulmann Licht
["productname"]
* string: Color temperature light
["modelid"]
* string: 500.46
["state"]
* table:
["ct"]
* number: 255
["reachable"]
* bool: true
["alert"]
* string: select
["mode"]
* string: homeautomation
["colormode"]
* string: ct
["on"]
* bool: false
["bri"]
* number: 254
["type"]
* string: Color temperature light
["name"]
* string: Celling light 3
["config"]
* table:
["function"]
* string: functional
["archetype"]
* string: ceilingsquare
["direction"]
* string: omnidirectional
["5"]
* table:
["swversion"]
* string: 10751203
["uniqueid"]
* string: a4:c1:38:39:f7:b3:aa:56-0b
["capabilities"]
* table:
["control"]
* table:
["ct"]
* table:
["min"]
* number: 158
["max"]
* number: 495
["streaming"]
* table:
["renderer"]
* bool: false
["proxy"]
* bool: false
["certified"]
* bool: false
["swupdate"]
* table:
["state"]
* string: notupdatable
["lastinstall"]
* string: 2023-04-23T16:37:15
["manufacturername"]
* string: GLEDOPTO
["productname"]
* string: Color temperature light
["modelid"]
* string: GL-C-006P
["state"]
* table:
["ct"]
* number: 255
["reachable"]
* bool: true
["alert"]
* string: select
["mode"]
* string: homeautomation
["colormode"]
* string: ct
["on"]
* bool: false
["bri"]
* number: 254
["type"]
* string: Color temperature light
["name"]
* string: Cove lighting
["config"]
* table:
["function"]
* string: mixed
["archetype"]
* string: huelightstrip
["direction"]
* string: omnidirectional
["9"]
* table:
["swversion"]
* string: 1400-0001
["uniqueid"]
* string: 00:15:8d:00:08:1d:bf:a2-01
["capabilities"]
* table:
["control"]
* table:
["ct"]
* table:
["min"]
* number: 153
["max"]
* number: 370
["streaming"]
* table:
["renderer"]
* bool: false
["proxy"]
* bool: false
["certified"]
* bool: false
["swupdate"]
* table:
["state"]
* string: notupdatable
["lastinstall"]
* string: 2023-06-10T09:10:43
["manufacturername"]
* string: Paulmann Licht
["productname"]
* string: Color temperature light
["modelid"]
* string: 500.46
["state"]
* table:
["ct"]
* number: 255
["reachable"]
* bool: true
["alert"]
* string: select
["mode"]
* string: homeautomation
["colormode"]
* string: ct
["on"]
* bool: false
["bri"]
* number: 254
["type"]
* string: Color temperature light
["name"]
* string: Celling light 1
["config"]
* table:
["function"]
* string: functional
["archetype"]
* string: ceilingsquare
[...
I don't see the light fixture 'Cove lighting-cr' with ID number 12 in the log file at all.
Best regards,
Nayden
Posts: 8256
Threads: 44
Joined: Jun 2015
Reputation:
476
To log a particular lamp modify the script around line 18:
Code: while true do
reply = getHueLights()
mylamps = json.decode(reply)
for _, item in pairs(mylamps) do
if item.name == 'Cove lighting-cr' then
log(item)
end
Posts: 28
Threads: 4
Joined: Oct 2022
Reputation:
0
(24.07.2025, 08:39)admin Wrote: To log a particular lamp modify the script around line 18:
Code: while true do
reply = getHueLights()
mylamps = json.decode(reply)
for _, item in pairs(mylamps) do
if item.name == 'Cove lighting-cr' then
log(item)
end
The result is:
Code: Feedback 24.07.2025 12:08:48
* table:
["swversion"]
* string: 1.122.8
["swconfigid"]
* string: 49730BB6
["uniqueid"]
* string: 00:17:88:01:0b:f3:14:ae-0b
["capabilities"]
* table:
["control"]
* table:
["colorgamut"]
* table:
[1]
* table:
[1]
* number: 0.6915
[2]
* number: 0.3083
[2]
* table:
[1]
* number: 0.17
[2]
* number: 0.7
[3]
* table:
[1]
* number: 0.1532
[2]
* number: 0.0475
["ct"]
* table:
["min"]
* number: 153
["max"]
* number: 500
["colorgamuttype"]
* string: C
["maxlumen"]
* number: 1600
["mindimlevel"]
* number: 40
["streaming"]
* table:
["renderer"]
* bool: true
["proxy"]
* bool: true
["certified"]
* bool: true
["swupdate"]
* table:
["state"]
* string: noupdates
["lastinstall"]
* string: 2025-07-17T11:36:44
["productid"]
* string: Philips-LCL001-1-LedStripsv4
["manufacturername"]
* string: Signify Netherlands B.V.
["productname"]
* string: Hue lightstrip plus
["modelid"]
* string: LCL001
["state"]
* table:
["ct"]
* number: 285
["reachable"]
* bool: true
["alert"]
* string: select
["on"]
* bool: false
["bri"]
* number: 58
["mode"]
* string: homeautomation
["colormode"]
* string: xy
["hue"]
* number: 24225
["sat"]
* number: 18
["effect"]
* string: none
["xy"]
* table:
[1]
* number: 0.3675
[2]
* number: 0.3982
["type"]
* string: Extended color light
["name"]
* string: Cove lighting-cr
["config"]
* table:
["startup"]
* table:
["mode"]
* string: powerfail
["configured"]
* bool: true
["function"]
* string: decorative
["archetype"]
* string: huelightstrip
["direction"]
* string: omnidirectional
Posts: 8256
Threads: 44
Joined: Jun 2015
Reputation:
476
The reported color temp is 3500K (1000000 / 285). Is it correct?
Have you applied this change? https://forum.logicmachine.net/showthrea...9#pid19499
Posts: 28
Threads: 4
Joined: Oct 2022
Reputation:
0
Posts: 8256
Threads: 44
Joined: Jun 2015
Reputation:
476
Do you use the same object for control and status? What is the event script attached to this object? Why do you use string data type instead of 2 byte unsigned?
Posts: 28
Threads: 4
Joined: Oct 2022
Reputation:
0
(24.07.2025, 12:54)admin Wrote: Do you use the same object for control and status? What is the event script attached to this object? Why do you use string data type instead of 2 byte unsigned?
1. I used the same object for control and status. I removed the status part for testing.
2. I'm applying the script as an event script.
3. I changed it to 2-byte unsigned. After these changes, the problem remains.
Code: --Control HUE from TW object (color temperature) (use as event based script)
require('user.hue')
lamp_id = 12
bri = grp.getvalue('32/2/9') -- 0..100%
ct = grp.getvalue('32/4/9') -- 2000K..6500K
setBrightnessCT(lamp_id, bri, ct)
Posts: 8256
Threads: 44
Joined: Jun 2015
Reputation:
476
You should use separate objects for control and status. Otherwise you might get a loop because color temperature value is not exact due to recalculation.
Posts: 54
Threads: 2
Joined: Mar 2019
Reputation:
1
28.07.2025, 05:45
(This post was last modified: 28.07.2025, 05:45 by Sral1987.)
(24.07.2025, 14:29)NKereshki Wrote: (24.07.2025, 12:54)admin Wrote: Do you use the same object for control and status? What is the event script attached to this object? Why do you use string data type instead of 2 byte unsigned?
1. I used the same object for control and status. I removed the status part for testing.
2. I'm applying the script as an event script.
3. I changed it to 2-byte unsigned. After these changes, the problem remains.
Code: --Control HUE from TW object (color temperature) (use as event based script)
require('user.hue')
lamp_id = 12
bri = grp.getvalue('32/2/9') -- 0..100%
ct = grp.getvalue('32/4/9') -- 2000K..6500K
setBrightnessCT(lamp_id, bri, ct)
Change your Code to
Code: --Control HUE from TW object (color temperature) (use as event based script)
require('user.hue')
lamp_id = 12
--bri = grp.getvalue('32/2/9') -- 0..100%
ct = grp.getvalue('32/4/9') -- 2000K..6500K
setBrightnessCT(lamp_id, bri, ct)
Now you controll only the Colortemperature, for brightness use a seperate Event
Posts: 28
Threads: 4
Joined: Oct 2022
Reputation:
0
(28.07.2025, 05:45)Sral1987 Wrote: (24.07.2025, 14:29)NKereshki Wrote: (24.07.2025, 12:54)admin Wrote: Do you use the same object for control and status? What is the event script attached to this object? Why do you use string data type instead of 2 byte unsigned?
1. I used the same object for control and status. I removed the status part for testing.
2. I'm applying the script as an event script.
3. I changed it to 2-byte unsigned. After these changes, the problem remains.
Code: --Control HUE from TW object (color temperature) (use as event based script)
require('user.hue')
lamp_id = 12
bri = grp.getvalue('32/2/9') -- 0..100%
ct = grp.getvalue('32/4/9') -- 2000K..6500K
setBrightnessCT(lamp_id, bri, ct)
Change your Code to
Code: --Control HUE from TW object (color temperature) (use as event based script)
require('user.hue')
lamp_id = 12
--bri = grp.getvalue('32/2/9') -- 0..100%
ct = grp.getvalue('32/4/9') -- 2000K..6500K
setBrightnessCT(lamp_id, bri, ct)
Now you controll only the Colortemperature, for brightness use a seperate Event
Hello,
First, I want to thank you for your help. Unfortunately, when I remove the brightness line from the script, the color temperature also stops being controlled. I'm using the script you showed me.
Best regards,
Nayden
Posts: 28
Threads: 4
Joined: Oct 2022
Reputation:
0
(25.07.2025, 07:06)admin Wrote: You should use separate objects for control and status. Otherwise you might get a loop because color temperature value is not exact due to recalculation.
Hi Admin,
Sincere thanks for your help. After separating the group address for color temperature control and feedback, everything is working perfectly.
Should I do this separation for the other group objects too: on/off, dimming, and RGB change? I just want to clarify that I also have a physical KNX button through which I turn the lights on/off and dim them. If I separate all controls from feedback, I can't synchronize the KNX button and sometimes I have to press it twice. What occurred to me is if it also "listens" to the feedback group address.
What would you advise, and what do you think is the best practice?
Best regards,
N. Kereshki
Posts: 5102
Threads: 28
Joined: Aug 2017
Reputation:
231
In general any KNX system is done in a way that there is one object for control and another for status.
------------------------------