scripting knx
Good morning,
I'm having a problem with the functions and I don't know how to solve it.
Here's the problem:
I currently have three logic machines taking KNX data from temperature, humidity, and CO2 sensors. I need them to calculate the average temperature, CO2, and humidity. But I only want to calculate this for the sensors located in rented properties.
I have the following variables.
Rented or non-rented status of 27 dwellings in group addresses from 2/0/176 to 2/0/202:
- Rented = 1
- Non-rented = 0
Temperature values delivered by each dwelling sensor:
'0/0/11','0/0/27','0/0/43','0/0/59','0/0/75','0/0/91','0/0/107',
'0/0/123','0/0/139','0/0/155','0/0/171','0/0/187','0/0/203',
'0/0/219','0/0/235','0/0/251',
'0/1/11','0/1/27','0/1/43','0/1/59','0/1/75','0/1/91','0/1/107',
'0/1/123','0/1/139','0/1/155','0/1/171'
Variable where the average building temperature will be stored:
2/0/164
And now I'll show you the code I wrote:
-- Direcciones de estado de las 27 viviendas (0=libre, 1=alquilada, 2=mantenimiento, 3=ocupada)
local estados = {}
for i = 1, 27 do
    estados[i] = '2/0/' .. (175 + i)  -- 176 → 202
-- Direcciones de temperatura individuales
local direcciones_temp = {
-- Dirección donde guardar la temperatura media
local destino1 = '2/0/164'
-- Rango válido de temperaturas
local min_temp = -20
local max_temp = 60
-- Intervalo de espera: 5 minutos (300 segundos)
local INTERVALO = 300
-- BUCLE PRINCIPAL (TU MISMO CÓDIGO, REPITIÉNDOSE PARA SIEMPRE)
while true do
    local suma = 0
    local contador = 0
    -- Recorrer las 27 viviendas
    for i = 1, 27 do
        local estado = grp.getvalue(estados[i])
        local valor = grp.getvalue(direcciones_temp[i])
        -- Solo usar temperatura si la vivienda está alquilada
        if estado == 1 then
            if valor ~= nil and type(valor) == "number" then
                if valor >= min_temp and valor <= max_temp then
                    suma = suma + valor
                    contador = contador + 1
                    log("Temperatura fuera de rango en " .. direcciones_temp[i] .. ": " .. tostring(valor))
                log("Valor de temperatura inválido o nulo en " .. direcciones_temp[i])
    -- Guardar la media si hay datos válidos
    if contador > 0 then
        local media = suma / contador
        grp.write(destino1, media)
        log("Temperatura media (solo alquilados) actualizada en " .. destino1 .. ": " .. media)
        log("No hay viviendas alquiladas con temperatura válida para calcular la media")
    -- Esperar 5 minutos antes de repetir
    os.sleep(INTERVALO)
Lo he intentado por todos los medios posibles y no me  calcula la temperatura media y cuando lo hace satura la memoria de la logic machine.
What script type are you using? The correct approach is to use a scheduled script that runs every 5 minutes and remove the while loop and os.sleep at the end.
What is the data type of rented status object. Is it boolean or 1 byte?
Buenas tardes,
Estaba ocupado con la construcción. Adjunto fotos del tipo de datos utilizado para los estados de las propiedades; es la versión 7.2.
En cuanto al script, se trata de un script basado en eventos.
It can't be an event script. Make a scheduled script as suggested earlier.
I haven't tried yet to create scripts scheduled at specific times and dates; I'm worried that the code won't understand that it needs to update the average temperature every 5 or 10 minutes.
(08.04.2026, 14:59)ALEJANDRO Wrote: I haven't tried yet to create scripts scheduled at specific times and dates; I'm worried that the code won't understand that it needs to update the average temperature every 5 or 10 minutes.
If you need to start script every 5 minutes then you can set '*/5' in minutes parameter
Are you sure this is 5 minutes?
Yes, it is. But you need to remove the while loop from the code for it to works correctly. Check the Logs tabs, you will see 5 minutes between logs from this script.
local estados = {}
for i = 1, 27 do
local max_temp = 60
local suma = 0
local contador = 0
for i = 1, 27 do
    if estado == 1 then
                suma = suma + valor
Yes, of course
I realized about that, thanks
Is it possible to create a resident script whose execution frequency is the value in hours of a group address called frequency_Test_Comms?
Can you explain what task are you trying to solve? Most likely there is simpler solution.
Let me explain. I have a series of IP addresses that I need to check:
- Portal 1 IP: 192.168.0.11 on 32/3/14
- Portal 2 IP: 192.168.0.12 on 32/3/15
- Portal 3 IP: 192.168.0.13 on 32/3/16
- Garage IP: 192.168.0.16 on 32/3/17
If a ping is successful and there is communication, the idea is to set IP addresses 32/3/14, 15, 16, and 17 to 1.
If there is no communication after the ping, the idea is to trigger alarms stored on the following addresses by setting these addresses to 1:
- Portal 1_Alarm IP on 32/3/27
- Portal 2_Alarm IP on 32/3/28
-ip portal 3_Alarma on 32/3/29
-ip Garaje_Alarma on 32/3/30
This IP monitoring process depends on two variables:
frec_test_comms 32/3/40 = 1
Enable_Test_IP 32/3/41 = 1
Well you can make os.delay(3600) 3600=1h but why do you want to make it configurable?
I'm being asked to do this in the project, I'll try to explain. The project tells me that the LMs (4 in total) and the gateways connected to each logic machine should have their IPs monitored based on whether an enabler variable, enable_test_ip = 1 and frec_test_comms = 1. enable_test_ip is boolean, frec_test_comms can be in a range from 1 hour to 23 hours.
Create a scheduled script that runs once every hour.
Use the following settings:
Minute: 0
Hour: *
Day of the month: *
Month of the year: Every month of the year
Day of the week: Every day of the week
Add your test sequence to the end of this script:
test_enabled = grp.getvalue('32/3/41')
test_freq = grp.getvalue('32/3/40')
if not test_enabled then
  return
key = 'prev_test_time'
curr_time = os.time()
prev_time = storage.get(key, 0)
elapsed_hours = math.round((curr_time - prev_time) / 3600)
if elapsed_hours < test_freq then
  return
storage.set(key, curr_time)
-- perform test sequence
Okay, I copied and pasted the script.
But it's not running every hour. I know the function works:
return
return
-- IP MONITORING (PING) - Simplified Version
-- Logic:
-- 1) Ping all IPs
-- 2) Send status (1/0)
-- 3) Send alarm (1 if no communication)
-- Execution: This script runs when you call it
-- Devices: REAL IP + GA status (bool) + GA alarm (bool)
local devices = {
{ real_ip = "192.168.0.11", ga_status = "32/3/14", ga_alarm = "32/3/27" },
{ real_ip = "192.168.0.12", ga_status = "32/3/15", ga_alarm = "32/3/28" },
{ real_ip = "192.168.0.13", ga_status = "32/3/16", ga_alarm = "32/3/29" },
{ real_ip = { 192.168.0.16, ga_estado = "32/3/17", ga_alarma = "32/3/30" },
{ ip_real = "192.168.0.111", ga_estado = "32/3/18", ga_alarma = "32/3/31" },
{ ip_real = "192.168.0.112", ga_estado = "32/3/19", ga_alarma = "32/3/32" },
{ ip_real = "192.168.0.113", ga_estado = "32/3/20", ga_alarma = "32/3/33" },
{ ip_real = "192.168.0.121", ga_estado = { ip_real = "32/3/21", ga_alarma = "32/3/34" },
{ ip_real = "192.168.0.122", ga_estado = "32/3/22", ga_alarma = "32/3/35" },
{ ip_real = "192.168.0.123", ga_estado = "32/3/23", ga_alarma = "32/3/36" },
{ ip_real = "192.168.0.131", ga_estado = "32/3/24", ga_alarma = "32/3/37" },
{ ip_real = "192.168.0.132", ga_estado = "32/3/25", ga_alarma = "32/3/38" }, },
{ real_ip = "192.168.0.133", status_ga = "32/3/26", alarm_ga = "32/3/39" },
{ real_ip = "192.168.0.161", status_ga = "32/3/43", alarm_ga = "32/3/44" }
-- Function: ping
local function test_device(ip)
local cmd = "ping -c 1 -W 1 " .. ip .. " >/dev/null 2>&1"
local result = os.execute(cmd)
return (result == true or result == 0)
-- Function: run test (only once)
local function run_test()
for _, dev in ipairs(devices) do
local ok = test_device(dev.ip_real)
local estado = ok and 1 or 0
local alarma = ok and 0 or 1
grp.write(dev.ga_estado, estado)
grp.write(dev.ga_alarma, alarma)
-- Direct execution of the test
ejecutar_test()
I think everything is correct, thanks.
Check LM Error log. Why do you need two group addresses for status?
