function from timer
Dear readers,
I have a timer that receives a virtual group address via a value of 0-100%.
As soon as this value exceeds 1 percent, the timer's value must be sent to 1/0/1, and I also need to activate a switching actuator on group addresses 1/1/1 through 1/1/7.
As soon as the timer's value reaches 0%, the switching actuator must also turn off.
Can someone help me with this?
Can you explain the 1% logic? If the timer value is 1 then nothing should happen or should it turn on the actuators?
If 0 = off, 1..100 = on then the following script should do what you need.
value = event.getvalue() on = value > 0 if on then   grp.checkwrite('1/0/1', value) end for i = 1, 7 do   grp.checkwrite('1/1/' .. i, on) end
Thanks for this script;
I modified it slightly because I don't need to send commands to consecutive group addresses.
The script works with the switching commands, but when I send 0%, it doesn't transmit that value—though it does transmit anything above 1%.
value = event.getvalue() on = value > 0 if on then   grp.checkwrite('1/0/1', value) end addresses = {   '1/1/1',   '1/1/2',   '1/1/4',   '1/1/5',     '1/1/7',   '1/1/8',   '1/1/10',   '1/1/11',   '1/1/13',   '1/1/14',   '1/1/16',   '1/1/17',   '1/1/19',   '1/1/20' } for _, address in ipairs(addresses) do   grp.checkwrite(address, on) end
If you always want to write the timer value then replace these lines (5-7):
With this: