This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Schneider Energy Meters Modbus Readings
#1
Trying to read data from 7 Schneider Energy Meters (1 no. is EM1200 & 6 nos. are EM6436). EM1200 giving proper readings but none EM6436 not giving the readings. Its readings are changing constantly. This has been tried with resident script and profile as well. Please help. Attached are both meters manuals.

Attached Files
.pdf   EM - 1000 & 1200.pdf (Size: 25.56 KB / Downloads: 10)
.pdf   EM6400 V03.02.01.00 Regmap.pdf (Size: 38.36 KB / Downloads: 11)
Reply
#2
Hi,

Have you tried to -1 the registers?

BR,

Erwin
Reply
#3
(23.10.2017, 15:03)Erwin van der Zwart Wrote: Hi,

Have you tried to -1 the registers?

BR,

Erwin

Yes.
Btw, the data reading is proper when communicated with Modscan software.
Reply
#4
Looks like -1 is required, try changing read swap parameter in RTU read test.
Reply
#5
RTU read test is successful. But, the data is read different every time it is requested. However, this is not the case in Modscan software.
Reply
#6
In RTU read test set address to 43914 (frequency) and data type to float32. Then try reading values with different read swap parameters. When you find correct read swap value set it in profile as stated here: http://openrb.com/docs/modbus.htm

Quote:Possible string values: n (no swap), w (word swap), b (byte swap), bw (byte and word swap)
Reply
#7
Thank you, it worked with n (no swap).
Reply