Posts: 82
Threads: 29
Joined: Jul 2015
Reputation:
2
Hi everyone!
I want to buy this DALI device: http://www.lunatone.com/produkt/dali-2xc...dimmer-cv/
to dimm Tunable White LEDs strips.
it uses the DT8 protocol. Is it possible to run it with the new pre-release firmware of August?
How?
Cheers!
Elkin
Posts: 7328
Threads: 41
Joined: Jun 2015
Reputation:
420
We don't have ballasts to test new DALI features, but the latest FW has support for raw telegrams which can be used to send any kind of DALI telegram. There's also an updated DALI package in the works which has new commands supported. We can provide it for you if you are willing to test it.
Posts: 82
Threads: 29
Joined: Jul 2015
Reputation:
2
(08.11.2018, 08:07)admin Wrote: We don't have ballasts to test new DALI features, but the latest FW has support for raw telegrams which can be used to send any kind of DALI telegram. There's also an updated DALI package in the works which has new commands supported. We can provide it for you if you are willing to test it.
OK, will buy the latest ballasts and we can test them together
Posts: 153
Threads: 12
Joined: Sep 2015
Reputation:
10
28.11.2018, 09:19
(This post was last modified: 28.11.2018, 09:20 by AEK.)
Hi everyone!
i've made tests with Easydim DALI-MIX-DT8 dimmer and its work
you will need to install new dali package (Admin will provide soon)
to set color temp use following script
Code: require('user.dali')
colortemp = 7000 -- in kelvin
address = 47
mirek = math.floor(1000000 / colortemp)
dtr0 = bit.band(mirek, 0xFF)
dtr1 = bit.band(bit.rshift(mirek, 8), 0xFF)
dalicmd(1, 'setdtr1', { value = dtr1 })
dalicmd(1, 'setdtr0', { value = dtr0 })
dalicmd(1, 'enabledevicetype', { value = 8 })
dalicmd(1, 'setcolortemp', { addrtype = 'short', address = address })
dalicmd(1, 'enabledevicetype', { value = 8 })
dalicmd(1, 'activate', { addrtype = 'short', address = address })
to make light warmer use this
Code: require('user.dali')
dalicmd(1, 'enabledevicetype', { value = 8 })
dalicmd(1, 'colortempwarmer', { addrtype = 'short', address = 47 })
cooler
Code: require('user.dali')
dalicmd(1, 'enabledevicetype', { value = 8 })
dalicmd(1, 'colortempcooler', { addrtype = 'short', address = 47 })
Posts: 4209
Threads: 21
Joined: Aug 2017
Reputation:
176
Hi
Which DT8 control type did you use? As far I remember there are:
- color temperature in Kelvin
- XY coordinate
- RGBW
I'm guessing it is the color temperature.
BR
------------------------------
Ctrl+F5
Posts: 153
Threads: 12
Joined: Sep 2015
Reputation:
10
(28.11.2018, 10:12)Daniel. Wrote: Hi
Which DT8 control type did you use? As far I remember there are:
- color temperature in Kelvin
- XY coordinate
- RGBW
I'm guessing it is the color temperature.
BR
this dimmer has cold white and warm white output only. so I use only temp color comands
I have another device DALI-ST-DT8 (RGBW dimmer) and I will try other comands with it.
before this I will try to set color limits
Posts: 12
Threads: 0
Joined: Mar 2017
Reputation:
4
19.12.2018, 12:16
(This post was last modified: 19.12.2018, 12:17 by Snoolik.)
Some functions for Type 8 temperature control
Code: function getCurrentTc(gateway, addr)
code = 2 -- parameter code to get current Tc
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = code })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'querycolorvalue', { addrtype = 'short', address = addr })
if err then return nil, 'querycolorvalue error: ' .. err end
hb = res:byte()
res, err = dalicmd(gateway, 'querydtr0', { addrtype = 'short', address = addr })
if err then return nil, 'querydtr0 error: ' .. err end
lb = res:byte()
mirek = bit.lshift(hb, 8) + lb
tc = 1000000 / mirek
return tc
end
function getCoolestTcLimit(gateway, addr)
code = 128 -- parameter code to get coolest Tc limit
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = code })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'querycolorvalue', { addrtype = 'short', address = addr })
if err then return nil, 'querycolorvalue error: ' .. err end
hb = res:byte()
res, err = dalicmd(gateway, 'querydtr0', { addrtype = 'short', address = addr })
if err then return nil, 'querydtr0 error: ' .. err end
lb = res:byte()
mirek = bit.lshift(hb, 8) + lb
tc = 1000000 / mirek
return tc
end
function getCoolestTcLimitPhys(gateway, addr)
code = 129 -- parameter code to get coolest Tc physical limit
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = code })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'querycolorvalue', { addrtype = 'short', address = addr })
if err then return nil, 'querycolorvalue error: ' .. err end
hb = res:byte()
res, err = dalicmd(gateway, 'querydtr0', { addrtype = 'short', address = addr })
if err then return nil, 'querydtr0 error: ' .. err end
lb = res:byte()
mirek = bit.lshift(hb, 8) + lb
tc = 1000000 / mirek
return tc
end
function getWarmestTcLimit(gateway, addr)
code = 130 -- parameter code to get warmest Tc limit
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = code })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'querycolorvalue', { addrtype = 'short', address = addr })
if err then return nil, 'querycolorvalue error: ' .. err end
hb = res:byte()
res, err = dalicmd(gateway, 'querydtr0', { addrtype = 'short', address = addr })
if err then return nil, 'querydtr0 error: ' .. err end
lb = res:byte()
mirek = bit.lshift(hb, 8) + lb
tc = 1000000 / mirek
return tc
end
function getWarmestTcLimitPhys(gateway, addr)
code = 131 -- parameter code to get warmest Tc physical limit
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = code })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'querycolorvalue', { addrtype = 'short', address = addr })
if err then return nil, 'querycolorvalue error: ' .. err end
hb = res:byte()
res, err = dalicmd(gateway, 'querydtr0', { addrtype = 'short', address = addr })
if err then return nil, 'querydtr0 error: ' .. err end
lb = res:byte()
mirek = bit.lshift(hb, 8) + lb
tc = 1000000 / mirek
return tc
end
function setWarmestTcLimit(gateway, addr, tc)
code = 1 -- parameter code to set warmest Tc limit
res, err = dalicmd(gateway, 'setdtr2', { addrtype = 'short', address = addr, value = code })
if err then return nil, 'setdtr2 error: ' .. err end
mirek = math.floor(1000000 / tc)
dtr0 = bit.band(mirek, 0xff)
dtr1 = bit.rshift(bit.band(mirek, 0xff00), 8)
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = dtr0 })
if err then return nil, 'setdtr2 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr1', { addrtype = 'short', address = addr, value = dtr1 })
if err then return nil, 'setdtr2 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'storecolortemplimit', { addrtype = 'short', address = addr })
if err then return nil, 'storecolortemplimit error: ' .. err end
res, err = dalicmd(gateway, 'storecolortemplimit', { addrtype = 'short', address = addr })
return res, err
end
function setCoolestTcLimit(gateway, addr, tc)
code = 0 -- parameter code to set coolest Tc limit
res, err = dalicmd(gateway, 'setdtr2', { addrtype = 'short', address = addr, value = code })
if err then return nil, 'setdtr2 error: ' .. err end
mirek = math.floor(1000000 / tc)
dtr0 = bit.band(mirek, 0xff)
dtr1 = bit.rshift(bit.band(mirek, 0xff00), 8)
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = dtr0 })
if err then return nil, 'setdtr2 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr1', { addrtype = 'short', address = addr, value = dtr1 })
if err then return nil, 'setdtr2 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'storecolortemplimit', { addrtype = 'short', address = addr })
if err then return nil, 'storecolortemplimit error: ' .. err end
res, err = dalicmd(gateway, 'storecolortemplimit', { addrtype = 'short', address = addr })
return res, err
end
function saveSceneTc(gateway, addr, tc, arc_level, scene)
-- Save scene with saved Tc and Arc level
mirek = math.floor(1000000/tc)
dtr0 = bit.band(mirek, 0xff)
dtr1 = bit.rshift(bit.band(mirek, 0xff00), 8)
res, err = dalicmd(gateway, 'setdtr1', { addrtype = 'short', address = addr, value = dtr1 })
if err then return nil, 'setdtr1 tc error: ' .. err end
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = dtr0 })
if err then return nil, 'setdtr0 tc error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'setcolortemp', { addrtype = 'short', address = addr })
if err then return nil, 'setcolortemp error: ' .. err end
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = arc_level })
if err then return nil, 'setdtr0 arc_level error: ' .. err end
res, err = dalicmd(gateway, 'storescene', { addrtype = 'short', address = addr, value = scene })
if err then return nil, 'storescene error: ' .. err end
res, err = dalicmd(gateway, 'storescene', { addrtype = 'short', address = addr, value = scene })
if err then return nil, 'storescene error: ' .. err end
return res, err
end
function getSupportedColorTypeFeatures(gateway, addr)
-- Get supported color type features
-- Return pattern:
-- If successful:
-- xy - 0/1, unsupported/supported
-- tc - 0/1, unsupported/supported
-- direct - 0-5, how much channels support direct control
-- rgbwaf - 0-5, how much rgbwaf channels
-- else: nil, Command name with error
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'querycolorfeatures', { addrtype = 'short', address = addr })
if err then return nil, 'querycolorfeatures error: ' .. err end
res = res:byte()
xy = bit.band(res, 0x01)
tc = bit.rshift(bit.band(res, 0x02), 1)
direct = bit.rshift(bit.band(res, 0x1c), 2)
rgbwaf = bit.rshift(bit.band(res, 0xe0), 5)
return xy, tc, direct, rgbwaf
end
function getSceneTc(gateway, addr, scene)
res, err = dalicmd(gateway, 'queryscene', { addrtype = 'short', address = addr, value = scene })
if err then return nil, 'queryscene error: ' .. err end
arc_level = res:byte()
code = 226 -- parameter code to get scene Tc
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = code })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'querycolorvalue', { addrtype = 'short', address = addr })
if err then return nil, 'querycolorvalue error: ' .. err end
hb = res:byte()
res, err = dalicmd(gateway, 'querydtr0', { addrtype = 'short', address = addr })
if err then return nil, 'querydtr0 error: ' .. err end
lb = res:byte()
mirek = bit.lshift(hb, 8) + lb
tc = 1000000 / mirek
return arc_level, tc
end
Posts: 12
Threads: 0
Joined: Mar 2017
Reputation:
4
26.12.2018, 12:22
(This post was last modified: 10.01.2020, 07:26 by Snoolik.)
Function for RGBW/RGBWAF Type 8 dimmer
Code: function setRGBWAF(gateway, addr, r, g, b, w, a, f)
if r == nil then r = 0 end
if g == nil then g = 0 end
if b == nil then b = 0 end
if w == nil then w = 0 end
if a == nil then a = 0 end
if f == nil then f = 0 end
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = math.min(r, 254) })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr1', { addrtype = 'short', address = addr, value = math.min(g, 254) })
if err then return nil, 'setdtr1 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr2', { addrtype = 'short', address = addr, value = math.min(b, 254) })
if err then return nil, 'setdtr2 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'setrgbdimlevel', { addrtype = 'short', address = addr })
if err then return nil, 'setrgbdimlevel error: ' .. err end
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = math.min(w, 254) })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr1', { addrtype = 'short', address = addr, value = math.min(a, 254) })
if err then return nil, 'setdtr1 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr2', { addrtype = 'short', address = addr, value = math.min(f, 254) })
if err then return nil, 'setdtr2 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'setwafdimlevel', { addrtype = 'short', address = addr })
if err then return nil, 'setwafdimlevel error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'activate', { addrtype = 'short', address = addr })
return res, err
end
function saveSceneRGBWAF(gateway, addr, scene, arc_level, r, g, b, w, a, f)
if r == nil then r = 0 end
if g == nil then g = 0 end
if b == nil then b = 0 end
if w == nil then w = 0 end
if a == nil then a = 0 end
if f == nil then f = 0 end
if arc_level == nil then arc_level = 254 end
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = math.min(r, 254) })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr1', { addrtype = 'short', address = addr, value = math.min(g, 254) })
if err then return nil, 'setdtr1 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr2', { addrtype = 'short', address = addr, value = math.min(b, 254) })
if err then return nil, 'setdtr2 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'setrgbdimlevel', { addrtype = 'short', address = addr })
if err then return nil, 'setrgbdimlevel error: ' .. err end
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = math.min(w, 254) })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr1', { addrtype = 'short', address = addr, value = math.min(a, 254) })
if err then return nil, 'setdtr1 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr2', { addrtype = 'short', address = addr, value = math.min(f, 254) })
if err then return nil, 'setdtr2 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'setwafdimlevel', { addrtype = 'short', address = addr })
if err then return nil, 'setwafdimlevel error: ' .. err end
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = arc_level })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'storescene', { addrtype = 'short', address = addr, value = scene })
if err then return nil, 'storescene error: ' .. err end
res, err = dalicmd(gateway, 'storescene', { addrtype = 'short', address = addr, value = scene })
return res, err
end
Posts: 12
Threads: 0
Joined: Mar 2017
Reputation:
4
Functions to get current RGBWAF:
Code: function getChannel(gateway, addr, code)
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = code })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'querycolorvalue', { addrtype = 'short', address = addr })
return res, err
end
function getRGBWAF(gateway, addr)
-- codes for RGBWAF could be 233-237 or 227-232
res_t = {}
for i = 233, 237, 1 do
res, err = getChannel(gateway, addr, i)
if res then table.insert(res_t, res:byte()) end
end
return res_t
end
Posts: 296
Threads: 69
Joined: Jan 2021
Reputation:
0
(26.12.2018, 12:22)Snoolik Wrote: Function for RGBW/RGBWAF Type 8 dimmer
Code: function setRGBWAF(gateway, addr, r, g, b, w, a, f)
if r == nil then r = 0 end
if g == nil then g = 0 end
if b == nil then b = 0 end
if w == nil then w = 0 end
if a == nil then a = 0 end
if f == nil then f = 0 end
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = math.min(r, 254) })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr1', { addrtype = 'short', address = addr, value = math.min(g, 254) })
if err then return nil, 'setdtr1 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr2', { addrtype = 'short', address = addr, value = math.min(b, 254) })
if err then return nil, 'setdtr2 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'setrgbdimlevel', { addrtype = 'short', address = addr })
if err then return nil, 'setrgbdimlevel error: ' .. err end
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = math.min(w, 254) })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr1', { addrtype = 'short', address = addr, value = math.min(a, 254) })
if err then return nil, 'setdtr1 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr2', { addrtype = 'short', address = addr, value = math.min(f, 254) })
if err then return nil, 'setdtr2 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'setwafdimlevel', { addrtype = 'short', address = addr })
if err then return nil, 'setwafdimlevel error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'activate', { addrtype = 'short', address = addr })
return res, err
end
function saveSceneRGBWAF(gateway, addr, scene, arc_level, r, g, b, w, a, f)
if r == nil then r = 0 end
if g == nil then g = 0 end
if b == nil then b = 0 end
if w == nil then w = 0 end
if a == nil then a = 0 end
if f == nil then f = 0 end
if arc_level == nil then arc_level = 254 end
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = math.min(r, 254) })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr1', { addrtype = 'short', address = addr, value = math.min(g, 254) })
if err then return nil, 'setdtr1 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr2', { addrtype = 'short', address = addr, value = math.min(b, 254) })
if err then return nil, 'setdtr2 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'setrgbdimlevel', { addrtype = 'short', address = addr })
if err then return nil, 'setrgbdimlevel error: ' .. err end
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = math.min(w, 254) })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr1', { addrtype = 'short', address = addr, value = math.min(a, 254) })
if err then return nil, 'setdtr1 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr2', { addrtype = 'short', address = addr, value = math.min(f, 254) })
if err then return nil, 'setdtr2 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'setwafdimlevel', { addrtype = 'short', address = addr })
if err then return nil, 'setwafdimlevel error: ' .. err end
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = arc_level })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'storescene', { addrtype = 'short', address = addr, value = scene })
if err then return nil, 'storescene error: ' .. err end
res, err = dalicmd(gateway, 'storescene', { addrtype = 'short', address = addr, value = scene })
return res, err
end
Hello and thanks for your efforts.
first in the setRGBWAF function what are ( gateway, addr), and how to convert the 251.600 6 byte DALI RGBW data type to fit the function (r,g,b,w,a,f)
regards,
Best Regards,
Posts: 7328
Threads: 41
Joined: Jun 2015
Reputation:
420
Use this, change gateway number and short address as needed:
Code: gateway = 'internal'
addr = 12
require('user.dali')
value = event.getvalue()
function setRGBWAF(gateway, addr, r, g, b, w, a, f)
if r == nil then r = 0 end
if g == nil then g = 0 end
if b == nil then b = 0 end
if w == nil then w = 0 end
if a == nil then a = 0 end
if f == nil then f = 0 end
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = math.min(r, 254) })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr1', { addrtype = 'short', address = addr, value = math.min(g, 254) })
if err then return nil, 'setdtr1 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr2', { addrtype = 'short', address = addr, value = math.min(b, 254) })
if err then return nil, 'setdtr2 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'setrgbdimlevel', { addrtype = 'short', address = addr })
if err then return nil, 'setrgbdimlevel error: ' .. err end
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = math.min(w, 254) })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr1', { addrtype = 'short', address = addr, value = math.min(a, 254) })
if err then return nil, 'setdtr1 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr2', { addrtype = 'short', address = addr, value = math.min(f, 254) })
if err then return nil, 'setdtr2 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'setwafdimlevel', { addrtype = 'short', address = addr })
if err then return nil, 'setwafdimlevel error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'activate', { addrtype = 'short', address = addr })
return res, err
end
setRGBWAF(gateway, addr, value.red, value.green, value.blue, value.white)
Posts: 296
Threads: 69
Joined: Jan 2021
Reputation:
0
06.07.2021, 11:25
(This post was last modified: 06.07.2021, 11:28 by khalil.)
(06.07.2021, 10:58)admin Wrote: Use this, change gateway number and short address as needed:
Code: gateway = 'internal'
addr = 12
require('user.dali')
value = event.getvalue()
function setRGBWAF(gateway, addr, r, g, b, w, a, f)
if r == nil then r = 0 end
if g == nil then g = 0 end
if b == nil then b = 0 end
if w == nil then w = 0 end
if a == nil then a = 0 end
if f == nil then f = 0 end
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = math.min(r, 254) })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr1', { addrtype = 'short', address = addr, value = math.min(g, 254) })
if err then return nil, 'setdtr1 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr2', { addrtype = 'short', address = addr, value = math.min(b, 254) })
if err then return nil, 'setdtr2 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'setrgbdimlevel', { addrtype = 'short', address = addr })
if err then return nil, 'setrgbdimlevel error: ' .. err end
res, err = dalicmd(gateway, 'setdtr0', { addrtype = 'short', address = addr, value = math.min(w, 254) })
if err then return nil, 'setdtr0 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr1', { addrtype = 'short', address = addr, value = math.min(a, 254) })
if err then return nil, 'setdtr1 error: ' .. err end
res, err = dalicmd(gateway, 'setdtr2', { addrtype = 'short', address = addr, value = math.min(f, 254) })
if err then return nil, 'setdtr2 error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'setwafdimlevel', { addrtype = 'short', address = addr })
if err then return nil, 'setwafdimlevel error: ' .. err end
res, err = dalicmd(gateway, 'enabledevicetype', { addrtype = 'short', address = addr, value = 8 })
if err then return nil, 'enabledevicetype error: ' .. err end
res, err = dalicmd(gateway, 'activate', { addrtype = 'short', address = addr })
return res, err
end
setRGBWAF(gateway, addr, value.red, value.green, value.blue, value.white)
thank you, admin
Great
can I read the RGBW Status?
Best Regards,
Posts: 7328
Threads: 41
Joined: Jun 2015
Reputation:
420
Posts: 296
Threads: 69
Joined: Jan 2021
Reputation:
0
07.07.2021, 14:37
(This post was last modified: 07.07.2021, 14:39 by khalil.)
(06.07.2021, 11:35)admin Wrote: See this example: https://forum.logicmachine.net/showthrea...2#pid12902
thank you admin for your great help and effort.
I do it like this and its wok
if you have any comments
RgbwSts = getRGBWAF(gateway, addr)
WriteValue = {}
WriteValue["red"] = RgbwSts[1]
WriteValue["white"] = RgbwSts[4]
WriteValue["blue"] = RgbwSts[3]
WriteValue["green"] = RgbwSts[2]
Also, I need the feedback for the on/off object and scale(0-100%)
regards,
Best Regards,
Posts: 7328
Threads: 41
Joined: Jun 2015
Reputation:
420
Posts: 296
Threads: 69
Joined: Jan 2021
Reputation:
0
(07.07.2021, 14:39)admin Wrote: See this: https://forum.logicmachine.net/showthrea...8#pid19988
thank you, admin
What is the right way to control a group of DALI Lights/short addresses at the same time?
Best Regards,
Posts: 7328
Threads: 41
Joined: Jun 2015
Reputation:
420
See this: https://forum.logicmachine.net/showthread.php?tid=133
I also recommend looking into our CANx-DALI gateway. It provides most of the features you need via UI instead of scripts.
Posts: 296
Threads: 69
Joined: Jan 2021
Reputation:
0
(08.07.2021, 10:57)admin Wrote: See this: https://forum.logicmachine.net/showthread.php?tid=133
I also recommend looking into our CANx-DALI gateway. It provides most of the features you need via UI instead of scripts.
Thank you, admin
I will, but for this project, we already bought the products and give a price for the customer, unfortunately we didn't test everything before
Best Regards,
|