Posts: 7331
Threads: 41
Joined: Jun 2015
Reputation:
420
There's no direct way of doing this. You can create a scheduled script that will push values to SQL database every minute or so. A better approach is to use a database that is meant for time-series data like InfluxDB.
Posts: 40
Threads: 14
Joined: Jun 2018
Reputation:
0
(19.11.2019, 09:49)admin Wrote: You can create a scheduled script that will push values to SQL database every minute or so.
I need to push values every 15 minutes to the database of almost 50 objects, but I'm not a programmer. If someone could help me would be great
Posts: 7331
Threads: 41
Joined: Jun 2015
Reputation:
420
Can you provide table structure and what data do you want to add there apart from object values (group address, name, date/time etc)?
Posts: 40
Threads: 14
Joined: Jun 2018
Reputation:
0
(19.11.2019, 12:06)admin Wrote: Can you provide table structure and what data do you want to add there apart from object values (group address, name, date/time etc)?
The structures could be like this:
- Table 1 "trending_definition" including [trending id, group address, object name, data type, date/time last update]
- Table 2 "trenging_values" including [value id, trending id, value, date/time]
I accept any advice or suggestion about the structure.
Posts: 7331
Threads: 41
Joined: Jun 2015
Reputation:
420
Example script. Map table keys are trend ID from external database, values are group addresses to get values from. Don't forget to change access details in connect function.
Code: require('luasql.mysql')
env = luasql.mysql()
dbcon, err = env:connect(DB_NAME, USERNAME, PASSWORD, MYSQL_SERVER_IP, MYSQL_SERVER_PORT)
if dbcon then
map = {
[1] = '1/1/1',
[2] = '1/1/2',
}
for id, addr in pairs(map) do
value = grp.getvalue(addr)
dbcon:execute('INSERT INTO trends_values (trend_id, value, created_at) VALUES (' .. id .. ', ' .. value .. ', NOW())')
dbcon:execute('UPDATE trends_definition SET updated_at=NOW() WHERE id=' .. id)
end
dbcon:close()
else
log('mysql connection failed ' .. tostring(err))
end
env:close()
Posts: 40
Threads: 14
Joined: Jun 2018
Reputation:
0
(19.11.2019, 14:07)admin Wrote: Example script. Map table keys are trend ID from external database, values are group addresses to get values from. Don't forget to change access details in connect function.
Code: require('luasql.mysql')
env = luasql.mysql()
dbcon, err = env:connect(DB_NAME, USERNAME, PASSWORD, MYSQL_SERVER_IP, MYSQL_SERVER_PORT)
if dbcon then
map = {
[1] = '1/1/1',
[2] = '1/1/2',
}
for id, addr in pairs(map) do
value = grp.getvalue(addr)
dbcon:execute('INSERT INTO trends_values (trend_id, value, created_at) VALUES (' .. id .. ', ' .. value .. ', NOW())')
dbcon:execute('UPDATE trends_definition SET updated_at=NOW() WHERE id=' .. id)
end
dbcon:close()
else
log('mysql connection failed ' .. tostring(err))
end
env:close()
This code creates the tables (trends_values, trends_definition) automatically or I must create it manually in the database?
Posts: 7331
Threads: 41
Joined: Jun 2015
Reputation:
420
You have to create tables manually and fill trends_definition table with data.
Posts: 1746
Threads: 6
Joined: Jul 2015
Reputation:
115
Hi,
Here is a script i created a few years ago that checks for tables and if not exist it creates them, maybe this can be helpful for you (:
Code: -- Check if MySQL connection is loaded and available otherwise perform DB connection loading
if not env or not dbcon then
-- Setup MySQL connection
require('luasql.mysql')
env = luasql.mysql()
-- Set database information and credentials, make sure remote access to MySQL server is enabled (see notes on bottom of this script)
DB_NAME = 'WiserforKNX'
USERNAME = 'root'
PASSWORD = 'MyPassword'
MYSQL_SERVER_IP = 'www.myserveraddress.com' -- remote access host
MYSQL_SERVER_PORT = 6033 -- remote access port (asymetric forwarding 6603 ext to 3306 internal to avoid internet MySQL known port scanning)
TIMEOUT = 3 -- timeout to avoid blocking when MySQL server could not be reached (set timeout in seconds)
-- Connect to MySQL database
dbcon, err = env:connect(DB_NAME, USERNAME, PASSWORD, MYSQL_SERVER_IP, MYSQL_SERVER_PORT, TIMEOUT)
-- Error handler
if err then
log(err)
env:close()
env = nil
alert('Connection to MySQL could not be established, system will try to restart connection')
return
end
if dbcon then
-- Set connected variable to true
connected = true
-- Set DB connection autocommit to true
dbcon:setautocommit(true)
-- Check if table for recording excist inside the database and holds data
cursor = dbcon:execute('SHOW TABLES LIKE "objectdata"')
-- Loop trough fetched data to see if rows are available
while true do
row = cursor:fetch({}, 'a')
if row then
-- do nothing
log("Table already exist, resuming script")
break
else
-- Drop DB table first before create new one
dbcon:execute('DROP TABLE objectdata')
-- Create DB table
cursor = dbcon:execute('CREATE TABLE objectdata (ID int AUTO_INCREMENT, address varchar(255) NOT NULL, name varchar(255) NOT NULL, value varchar(255) NOT NULL, updatetime int NOT NULL, timestamp varchar(255) NOT NULL, PRIMARY KEY (ID))')
log("Table for objectdata is created, resuming script")
break
end
end
else
-- Exit script for new try
return
end
end
-- Init client for listening to all KNX events
if not client then
require('genohm-scada.eibdgm')
--handler for all event types
eventhandler = function(event)
objectinfo = grp.find(event.dst)
-- fix for auto discovered objects without a name
if objectinfo.name == nil then
objectinfo.name = "unknown"
end
-- fix for new created objects without a having set value once
if objectinfo.value == nil then
objectinfo.value = "no value"
else
objectinfo.value = tostring(objectinfo.value)
end
-- fix for time object
if type(objectinfo.value) == "table" then
objectinfo.value = string.format("%02d", objectinfo.value.hour) .. ":" .. string.format("%02d", objectinfo.value.minute) .. ":" .. string.format("%02d", objectinfo.value.second)
end
-- fix for boolean object
if type(objectinfo.value) == "boolean" then
objectinfo.value = tostring(objectinfo.value)
end
-- calculate human readable timestamp
timestamp = os.date("%Y-%m-%d %H:%M:%S", objectinfo.updatetime)
-- write data to MySQL database
cursor, err = dbcon:execute('INSERT INTO objectdata (address, name, value , updatetime, timestamp) VALUES ("' .. objectinfo.address .. '", "' .. objectinfo.name .. '", "' .. objectinfo.value .. '", ' .. objectinfo.updatetime .. ', "' .. timestamp .. '")')
-- Get result of transaction
result = dbcon:commit()
-- Error handler
if not result or err then
if connected == true then
alert('Connection to MySQL is broken or data is not processed correct, system will buffer data until connection is restored')
end
connected = false
else
if not connected then
connected = true
end
end
end
-- Create client
client = eibdgm:new()
-- Set group communication handlers
client:sethandler('groupread', eventhandler)
client:sethandler('groupwrite', eventhandler)
client:sethandler('groupresponse', eventhandler)
end
-- Next cycle
client:step()
BR,
Erwin
Posts: 40
Threads: 14
Joined: Jun 2018
Reputation:
0
17.05.2020, 08:18
(This post was last modified: 17.05.2020, 08:56 by pentadom.)
(20.11.2019, 11:25)Erwin van der Zwart Wrote: Hi,
Here is a script i created a few years ago that checks for tables and if not exist it creates them, maybe this can be helpful for you (:
Code: -- Check if MySQL connection is loaded and available otherwise perform DB connection loading
if not env or not dbcon then
-- Setup MySQL connection
require('luasql.mysql')
env = luasql.mysql()
-- Set database information and credentials, make sure remote access to MySQL server is enabled (see notes on bottom of this script)
DB_NAME = 'WiserforKNX'
USERNAME = 'root'
PASSWORD = 'MyPassword'
MYSQL_SERVER_IP = 'www.myserveraddress.com' -- remote access host
MYSQL_SERVER_PORT = 6033 -- remote access port (asymetric forwarding 6603 ext to 3306 internal to avoid internet MySQL known port scanning)
TIMEOUT = 3 -- timeout to avoid blocking when MySQL server could not be reached (set timeout in seconds)
-- Connect to MySQL database
dbcon, err = env:connect(DB_NAME, USERNAME, PASSWORD, MYSQL_SERVER_IP, MYSQL_SERVER_PORT, TIMEOUT)
-- Error handler
if err then
log(err)
env:close()
env = nil
alert('Connection to MySQL could not be established, system will try to restart connection')
return
end
if dbcon then
-- Set connected variable to true
connected = true
-- Set DB connection autocommit to true
dbcon:setautocommit(true)
-- Check if table for recording excist inside the database and holds data
cursor = dbcon:execute('SHOW TABLES LIKE "objectdata"')
-- Loop trough fetched data to see if rows are available
while true do
row = cursor:fetch({}, 'a')
if row then
-- do nothing
log("Table already exist, resuming script")
break
else
-- Drop DB table first before create new one
dbcon:execute('DROP TABLE objectdata')
-- Create DB table
cursor = dbcon:execute('CREATE TABLE objectdata (ID int AUTO_INCREMENT, address varchar(255) NOT NULL, name varchar(255) NOT NULL, value varchar(255) NOT NULL, updatetime int NOT NULL, timestamp varchar(255) NOT NULL, PRIMARY KEY (ID))')
log("Table for objectdata is created, resuming script")
break
end
end
else
-- Exit script for new try
return
end
end
-- Init client for listening to all KNX events
if not client then
require('genohm-scada.eibdgm')
--handler for all event types
eventhandler = function(event)
objectinfo = grp.find(event.dst)
-- fix for auto discovered objects without a name
if objectinfo.name == nil then
objectinfo.name = "unknown"
end
-- fix for new created objects without a having set value once
if objectinfo.value == nil then
objectinfo.value = "no value"
else
objectinfo.value = tostring(objectinfo.value)
end
-- fix for time object
if type(objectinfo.value) == "table" then
objectinfo.value = string.format("%02d", objectinfo.value.hour) .. ":" .. string.format("%02d", objectinfo.value.minute) .. ":" .. string.format("%02d", objectinfo.value.second)
end
-- fix for boolean object
if type(objectinfo.value) == "boolean" then
objectinfo.value = tostring(objectinfo.value)
end
-- calculate human readable timestamp
timestamp = os.date("%Y-%m-%d %H:%M:%S", objectinfo.updatetime)
-- write data to MySQL database
cursor, err = dbcon:execute('INSERT INTO objectdata (address, name, value , updatetime, timestamp) VALUES ("' .. objectinfo.address .. '", "' .. objectinfo.name .. '", "' .. objectinfo.value .. '", ' .. objectinfo.updatetime .. ', "' .. timestamp .. '")')
-- Get result of transaction
result = dbcon:commit()
-- Error handler
if not result or err then
if connected == true then
alert('Connection to MySQL is broken or data is not processed correct, system will buffer data until connection is restored')
end
connected = false
else
if not connected then
connected = true
end
end
end
-- Create client
client = eibdgm:new()
-- Set group communication handlers
client:sethandler('groupread', eventhandler)
client:sethandler('groupwrite', eventhandler)
client:sethandler('groupresponse', eventhandler)
end
-- Next cycle
client:step()
BR,
Erwin
Dear Erwin,
How would be the code to create automatically the tables I need.
This is my code now:
Code: require('luasql.mysql')
env = luasql.mysql()
dbcon, err = env:connect(DB_NAME, USERNAME, PASSWORD, MYSQL_SERVER_IP, MYSQL_SERVER_PORT)
if dbcon then
map = {
[1] = '1/1/1',
[2] = '1/1/2',
}
for id, addr in pairs(map) do
value = grp.getvalue(addr)
dbcon:execute('INSERT INTO trends_values (trend_id, value, created_at) VALUES (' .. id .. ', ' .. value .. ', NOW())')
dbcon:execute('UPDATE trends_definition SET updated_at=NOW() WHERE id=' .. id)
end
dbcon:close()
else
log('mysql connection failed ' .. tostring(err))
end
env:close()
(19.11.2019, 14:07)admin Wrote: Example script. Map table keys are trend ID from external database, values are group addresses to get values from. Don't forget to change access details in connect function.
Code: require('luasql.mysql')
env = luasql.mysql()
dbcon, err = env:connect(DB_NAME, USERNAME, PASSWORD, MYSQL_SERVER_IP, MYSQL_SERVER_PORT)
if dbcon then
map = {
[1] = '1/1/1',
[2] = '1/1/2',
}
for id, addr in pairs(map) do
value = grp.getvalue(addr)
dbcon:execute('INSERT INTO trends_values (trend_id, value, created_at) VALUES (' .. id .. ', ' .. value .. ', NOW())')
dbcon:execute('UPDATE trends_definition SET updated_at=NOW() WHERE id=' .. id)
end
dbcon:close()
else
log('mysql connection failed ' .. tostring(err))
end
env:close()
I dont't want to modify the code every time I create a new object.
Is there any way to fill the map automatically when I create new objects in LM?
(19.11.2019, 09:49)admin Wrote: There's no direct way of doing this. You can create a scheduled script that will push values to SQL database every minute or so. A better approach is to use a database that is meant for time-series data like InfluxDB.
But if I push values directly from the objects and the connection with the database fails, this values will be lost. It's important to know that my database is in the cloud.
Can I push values from the trends. In this case I always have the values recorded locally in the LM and I do a backup once a day for example.
Posts: 1746
Threads: 6
Joined: Jul 2015
Reputation:
115
Hi,
Yes you can, you have seen the script for fetching the values from a trend, combine it with this script and modify the sql queries and you have what you need, it’s just a matter of creating a script with the samples you have..
BR,
Erwin
Posts: 40
Threads: 14
Joined: Jun 2018
Reputation:
0
17.05.2020, 14:57
(This post was last modified: 17.05.2020, 14:58 by pentadom.)
(17.05.2020, 11:52)Erwin van der Zwart Wrote: Hi,
Yes you can, you have seen the script for fetching the values from a trend, combine it with this script and modify the sql queries and you have what you need, it’s just a matter of creating a script with the samples you have..
BR,
Erwin
Thanks Erwin, it's difficult for me because I'm not a programmer but I'll try
I did a test fetching values from a trend with the next code:
Code: require('trends')
name = 'testswitch'
dates = {}
dates['start'] = { year = 2020, month = 5, day = 17 }
dates['end'] = { year = 2020, month = 5, day = 18 }
-- resolution (in seconds) is optional
-- default trend resolution is used when not set
resolution = nil
res = trends.fetch(name, dates, resolution)
log(res)
but I have an error when I run script:
Posts: 4216
Threads: 21
Joined: Aug 2017
Reputation:
178
Does this trend testswitch exist?
------------------------------
Ctrl+F5
Posts: 7331
Threads: 41
Joined: Jun 2015
Reputation:
420
Have you tried clicking Save before Run script?
Posts: 40
Threads: 14
Joined: Jun 2018
Reputation:
0
18.05.2020, 07:55
(This post was last modified: 18.05.2020, 07:57 by pentadom.)
(18.05.2020, 07:38)Daniel. Wrote: Does this trend testswitch exist?
Yes, here it is:
(18.05.2020, 07:50)admin Wrote: Have you tried clicking Save before Run script?
Yes. I tried "save" and "save and close"
I'm testing on the demo LM from openrb web. You can see all the configuration there if you want. The script called "SQL" is in the scheduled scripts.
Posts: 7331
Threads: 41
Joined: Jun 2015
Reputation:
420
Some features are disabled on demo LM so this might not work. Do you have another LM to test this?
Posts: 40
Threads: 14
Joined: Jun 2018
Reputation:
0
(18.05.2020, 07:58)admin Wrote: Some features are disabled on demo LM so this might not work. Do you have another LM to test this?
No at the moment, I have it in my workplace. I'm confined because of the COVID-19
I supposed then it's because of a disabled feature really?
Posts: 4216
Threads: 21
Joined: Aug 2017
Reputation:
178
On my LM this script works fine.
------------------------------
Ctrl+F5
Posts: 40
Threads: 14
Joined: Jun 2018
Reputation:
0
(18.05.2020, 08:06)Daniel. Wrote: On my LM this script works fine.
Thank you so much for the information Daniel. I must test it on another LM.
Posts: 40
Threads: 14
Joined: Jun 2018
Reputation:
0
Hello,
I did some tests with the next code. I want to insert all the trending values in my SQL database. When I run the script all the code executes correctly without errors in the logs but in the database I don't see the new values..
Code: require('trends')
require("luasql.mysql");
--Get a list of all trendings
names = db:getlist('SELECT name FROM trends')
log (names)
--Defines a period of the last day
dates = {}
dates['start'] = os.date('*t')
dates['start'].day = dates['start'].day - 1
dates['end'] = os.date('*t')
env = luasql.mysql();
--DATABASE CONNECTION -> (DB_NAME, USERNAME, PASSWORD, MYSQL_SERVER_IP, MYSQL_SERVER_PORT)
dbcon, err = env:connect('CONFIDENTIAL', 'admin','CONFIDENTIAL', 'lm-database.CONFIDENTIAL.us-east-1.rds.amazonaws.com', '3306');
log(dbcon, err)
if dbcon then
-- Iterates all the trendings
for _, name in ipairs(names) do
-- Get all the trending values
data = trends.fetch(name, dates)
-- Iterates all the trending values
for id, val in pairs(data) do
-- Insert the trending values in the database.
dbcon:execute('INSERT INTO trending-definition (id, value) VALUES (id,val)')
end
end
else
log('mysql connection failed ' .. tostring(err))
end
dbcon:close()
env:close()
I'm not a programmer and It's my first time doing a script with LUA so I apologize in advance for the posible errors.
Posts: 7331
Threads: 41
Joined: Jun 2015
Reputation:
420
Use this table structure for data. trend_id will be the same id as in LM.
Code: CREATE TABLE `trends_data` (
`trend_id` int(11) NOT NULL,
`dt` datetime NOT NULL,
`value` double DEFAULT NULL,
PRIMARY KEY (`trend_id`,`dt`)
) ENGINE=InnoDB DEFAULT CHARSET=utf8;
Updated script:
Code: require('trends')
require('luasql.mysql')
env = luasql.mysql()
--DATABASE CONNECTION -> (DB_NAME, USERNAME, PASSWORD, MYSQL_SERVER_IP, MYSQL_SERVER_PORT)
dbcon, err = env:connect('CONFIDENTIAL', 'admin', 'CONFIDENTIAL', 'lm-database.CONFIDENTIAL.us-east-1.rds.amazonaws.com', 3306)
if dbcon then
items = db:getall('SELECT id, name FROM trends')
trends.NaN = 'NULL'
dates = {
['start'] = os.date('*t'),
['end'] = os.date('*t'),
}
dates.start.day = dates.start.day - 1
date = string.format('%04d-%02d-%02d',
dates.start.year, dates.start.month, dates.start.day)
for _, item in ipairs(items) do
id = item.id
data = trends.fetch(item.name, dates)
values = {}
if data and #data > 0 then
step = 1440 / #data -- in minutes
for i, val in ipairs(data) do
mins = (i - 1) * step
datetime = string.format('%s %02d:%02d:00',
date, math.floor(mins / 60), mins % 60)
values[ #values + 1 ] = string.format('(%d,"%s",%s)',
id, datetime, tostring(val))
end
end
if #values > 0 then
query = 'INSERT INTO trends_data (trend_id, dt, value) VALUES ' .. table.concat(values, ',')
dbcon:execute(query)
end
end
dbcon:close()
else
log('mysql connection failed ' .. tostring(err))
end
env:close()
|