Posts: 125
Threads: 16
Joined: May 2020
Reputation:
0
Hello
I have been trying to use wiser for KNX to connect to an MQTT broker (mosquitto) but am getting nothing.
The broker is running on my PC, I check the topics and they work, in the script I put the ip address of the pc where the broker runs and I have the addresses defined in the objects tab, but without result.
I don't know if wiser have what it takes to connect or if it is necessary to install libmosquitto.ipk, luamosquitto.ipk and luasockets.ipk as it comes in the Gbridge.io guide that I found in the forum.
Would someone be so kind as to tell me how to proceed?
Thank you.
a greeting
Posts: 4221
Threads: 21
Joined: Aug 2017
Reputation:
179
First we have to see your script. What fw do you use?
Have you seen this thread?
https://forum.logicmachine.net/showthread.php?tid=2628
------------------------------
Ctrl+F5
Posts: 125
Threads: 16
Joined: May 2020
Reputation:
0
20.05.2020, 13:55
(This post was last modified: 20.05.2020, 14:04 by JRP.)
(20.05.2020, 12:40)Daniel. Wrote: First we have to see your script. What fw do you use?
Have you seen this thread? Hi Daniel thanks for replying.
Wiser has the fw 2.4.0 as you can see in the following image.
I use the script that I publish Admin in this thread
https://forum.logicmachine.net/showthrea...light=mqtt
I have created the resident script at interval 0 and changed the IP address to the address of the pc where the mosquitto broker runs.
The object mapping I have used the same as a test.
Code: if not broker then
broker = '192.168.0.12'
function multiply(mult)
return function(value)
local num = tonumber(value)
if num then
return num * mult
else
return value
end
end
end
-- topic to object map
mqtt_to_object = {
['in/topic1'] = '32/1/1',
['in/topic2'] = '32/1/2',
}
-- object to topic map
object_to_mqtt = {
['1/1/1'] = 'out/topic1',
['1/1/2'] = 'out/topic2',
}
datatypes = {}
grp.sender = 'mq'
require('socket')
for addr, _ in pairs(object_to_mqtt) do
local obj = grp.find(addr)
if obj then
datatypes[ addr ] = obj.datatype
end
end
mclient = require('mosquitto').new()
mclient.ON_CONNECT = function(res, ...)
log('mqtt connect status', res, ...)
if res then
for topic, _ in pairs(mqtt_to_object) do
mclient:subscribe(topic)
end
else
mclient:disconnect()
end
end
mclient.ON_MESSAGE = function(mid, topic, payload)
local addr = mqtt_to_object[ topic ]
if addr then
local fn = mqtt_to_object_conv[ topic ]
if fn then
payload = fn(payload)
end
grp.write(addr, payload)
end
end
mclient.ON_DISCONNECT = function(...)
log('mqtt disconnect', ...)
mclientfd = nil
end
function mconnect()
local fd
mclient:connect(broker)
fd = mclient:socket()
-- fd ref is valid
if fd then
mclientfd = fd
end
end
mconnect()
function publishvalue(event)
-- message from us or client is not connected
if event.sender == 'mq' or not mclientfd then
return
end
local addr = event.dst
local dpt = datatypes[ addr ]
local topic = object_to_mqtt[ addr ]
-- unknown object
if not dpt or not topic then
return
end
local value = busdatatype.decode(event.datahex, dpt)
if value ~= nil then
if type(value) == 'boolean' then
value = value and 1 or 0
end
mclient:publish(topic, tostring(value))
end
end
lbclient = require('localbus').new(1)
lbclient:sethandler('groupwrite', publishvalue)
lbclientfd = socket.fdmaskset(lbclient:getfd(), 'r')
-- run timer every 5 seconds
timer = require('timerfd').new(5)
timerfd = socket.fdmaskset(timer:getfd(), 'r')
end
-- mqtt connected
if mclientfd then
mclientfdset = socket.fdmaskset(mclientfd, mclient:want_write() and 'rw' or 'r')
res, lbclientstat, timerstat, mclientstat =
socket.selectfds(10, lbclientfd, timerfd, mclientfdset)
-- mqtt not connected
else
res, lbclientstat, timerstat =
socket.selectfds(10, lbclientfd, timerfd)
end
if mclientstat then
if socket.fdmaskread(mclientstat) then
mclient:loop_read()
end
if socket.fdmaskwrite(mclientstat) then
mclient:loop_write()
end
end
if lbclientstat then
lbclient:step()
end
if timerstat then
-- clear armed timer
timer:read()
if mclientfd then
mclient:loop_misc()
else
mconnect()
end
end
Putting the log lines suggested in that same post, this is the result.
MQTT 20.05.2020 16:03:19
Resident script:130: bad argument #2 to 'selectfds' (number expected, got nil)
stack traceback:
[C]: in function 'selectfds'
Is it necessary to install a library or package?
The topics are published and the broker subscribed to them.
Thank you.
a greeting
Posts: 4221
Threads: 21
Joined: Aug 2017
Reputation:
179
In the link which I originally forgot to paste you can find how to use encrypted communication
https://forum.logicmachine.net/showthread.php?tid=2628
------------------------------
Ctrl+F5
Posts: 125
Threads: 16
Joined: May 2020
Reputation:
0
(20.05.2020, 13:59)Daniel. Wrote: In the link which I originally forgot to paste you can find how to use encrypted communication
https://forum.logicmachine.net/showthread.php?tid=2628 Hello
Thank you for responding.
In the broker I have not activated any user or password, as it is only a test for now.
I'm still wondering if it's necessary to install some library in wiser.
Greetings and thanks for helping
Posts: 1746
Threads: 6
Joined: Jul 2015
Reputation:
115
Hi,
There is already a lib in the Wiser 2.4 firmware however i don't think it's the most recent version as 2.4 is out for quite a while.
I'm currently testing on FW 2.5 that will be released (don't pinpoint me on it) somewhere around this summer, and all features that are in Daniels latest script work on FW 2.5 including the broker app.
So you need to wait a couple of weeks (:
BR,
Erwin
Posts: 4221
Threads: 21
Joined: Aug 2017
Reputation:
179
I just tried this script
https://forum.logicmachine.net/showthrea...6#pid16896
on SL with fw 2.4.0 and it works just fine. I used broker on LM.
------------------------------
Ctrl+F5
Posts: 125
Threads: 16
Joined: May 2020
Reputation:
0
21.05.2020, 10:40
(This post was last modified: 21.05.2020, 10:42 by JRP.)
(20.05.2020, 18:58)Erwin van der Zwart Wrote: Hi,
There is already a lib in the Wiser 2.4 firmware however i don't think it's the most recent version as 2.4 is out for quite a while.
I'm currently testing on FW 2.5 that will be released (don't pinpoint me on it) somewhere around this summer, and all features that are in Daniels latest script work on FW 2.5 including the broker app.
So you need to wait a couple of weeks (:
BR,
Erwin
(21.05.2020, 07:21)Daniel. Wrote: I just tried this script
https://forum.logicmachine.net/showthrea...6#pid16896
on SL with fw 2.4.0 and it works just fine. I used broker on LM. Hello
Thanks Erwin for the information on the fw update. While the update arrives I will do some more tests.
Hellol Daniel.
Thanks for answering.
I have activated user and password in the mosquito broker, I have copied the script that you indicate and changed ip, user, password and port (1883 is where mosquitto runs on my PC).
I use the MQTT.fx client and post both topic in / topic1 and out / topic1.
I subscribe with the same MQTT.fx and with mosquitto_sub and it works perfectly, but I don't see any changes in the wiser.
In the register tab I see that it does not connect to the broker, put this.
* string: mqtt connect failed Operation timed out
This is the script (I remove the password).
Code: if not broker then
socket = require('socket')
json = require('json')
broker = '192.168.0.12'
port = 1883
username = 'wiser'
password = 'mypassword'
-- topic to object map
mqtt_to_object = {
['in/topic1'] = {
addr = '1/0/0',
convert = json.pdecode,
},
['in/topic2'] = {
addr = '1/0/19',
}
}
-- object to topic map
object_to_mqtt = {
['1/0/0'] = {
topic = 'out/topic1',
qos = 1,
retain = true,
convert = json.encode,
},
['1/0/19'] = {
topic = 'out/topic2',
}
}
datatypes = {}
grp.sender = 'mq'
for addr, _ in pairs(object_to_mqtt) do
local obj = grp.find(addr)
if obj then
datatypes[ addr ] = obj.datatype
end
end
mclient = require('mosquitto').new()
mclient.ON_CONNECT = function(res, ...)
log('mqtt connect status', res, ...)
if res then
for topic, _ in pairs(mqtt_to_object) do
mclient:subscribe(topic)
end
else
mclient:disconnect()
end
end
mclient.ON_MESSAGE = function(mid, topic, payload)
local map = mqtt_to_object[ topic ]
if map then
if map.convert then
payload = map.convert(payload)
end
grp.write(map.addr, payload)
end
end
mclient.ON_DISCONNECT = function(...)
log('mqtt disconnect', ...)
mclientfd = nil
end
function mconnect()
local status, rc, msg, fd
status, rc, msg = mclient:connect(broker, port)
if not status then
log('mqtt connect failed ' .. tostring(msg))
end
fd = mclient:socket()
if fd then
mclientfd = fd
end
end
mclient:tls_insecure_set(true)
mclient:login_set(username, password or '')
mconnect()
function publishvalue(event)
-- message from us or client is not connected
if event.sender == 'mq' or not mclientfd then
return
end
local addr = event.dst
local dpt = datatypes[ addr ]
local map = object_to_mqtt[ addr ]
-- unknown object
if not dpt or not map then
return
end
local value = busdatatype.decode(event.datahex, dpt)
if value ~= nil then
if map.convert then
value = map.convert(value)
elseif type(value) == 'boolean' then
value = value and 1 or 0
end
mclient:publish(map.topic, tostring(value), map.qos or 0, map.retain)
end
end
lbclient = require('localbus').new(1)
lbclient:sethandler('groupwrite', publishvalue)
lbclientfd = socket.fdmaskset(lbclient:getfd(), 'r')
-- run timer every 5 seconds
timer = require('timerfd').new(5)
timerfd = socket.fdmaskset(timer:getfd(), 'r')
end
-- mqtt connected
if mclientfd then
mclientfdset = socket.fdmaskset(mclientfd, mclient:want_write() and 'rw' or 'r')
res, lbclientstat, timerstat, mclientstat =
socket.selectfds(10, lbclientfd, timerfd, mclientfdset)
-- mqtt not connected
else
res, lbclientstat, timerstat =
socket.selectfds(10, lbclientfd, timerfd)
end
if mclientstat then
if socket.fdmaskread(mclientstat) then
mclient:loop_read()
end
if socket.fdmaskwrite(mclientstat) then
mclient:loop_write()
end
end
if lbclientstat then
lbclient:step()
end
if timerstat then
-- clear armed timer
timer:read()
if mclientfd then
mclient:loop_misc()
else
mconnect()
end
end
The port number should not be between ''?
He does not put them in the thread from which he copies it.
Thank you very much for the help.
Greetings
Posts: 4221
Threads: 21
Joined: Aug 2017
Reputation:
179
If you don't use encryption (port 1883)
Then change this
mclient:tls_insecure_set(true)
to
mclient:tls_insecure_set(false)
------------------------------
Ctrl+F5
Posts: 125
Threads: 16
Joined: May 2020
Reputation:
0
(21.05.2020, 10:42)Daniel. Wrote: If you don't use encryption (port 1883)
Then change this
mclient:tls_insecure_set(true)
to
mclient:tls_insecure_set(false) Hello
I have changed it and the same error continues.
Thanks for answering.
a greeting
Posts: 4221
Threads: 21
Joined: Aug 2017
Reputation:
179
This work with my broker so your issue is somewhere there. Can you connect to your broker by using MQTT Explorer client but from another machine?
------------------------------
Ctrl+F5
Posts: 125
Threads: 16
Joined: May 2020
Reputation:
0
(21.05.2020, 11:22)Daniel. Wrote: This work with my broker so your issue is somewhere there. Can you connect to your broker by using MQTT Explorer client but from another machine? Hello
I have tried with Mqtt explorer and MQtt.fx and neither of them connects from another pc. I put the IP of the pc where I have mosquitto installed and the username and password and nothing.
Surely the problem comes from here.
I have all the computers on the same network, I ping and they all respond.
If in MQtt.fx installed on the same pc as the broker, I put instead of address 127 ......., the ip address of the same pc 192.168.012. It connects and on netstat I see the connection to port 1883.
Will I be the router that blocks traffic? It is what occurs to me.
Thanks for the help.
a greeting
Posts: 4221
Threads: 21
Joined: Aug 2017
Reputation:
179
It is most likely your PC firewall.
------------------------------
Ctrl+F5
Posts: 125
Threads: 16
Joined: May 2020
Reputation:
0
(21.05.2020, 11:50)Daniel. Wrote: It is most likely your PC firewall. Hello
Eureka!
Effectively it is the w10 firewall that was blocking traffic, I have opened port 1883 and it has connected and worked the first time.
After writing the last message it occurred to me that it could be the firewall, but until you told me to try from another PC, the light bulb did not light up.
Thank you very much Daniel for your interest and your reconmedances.
a greeting
Posts: 133
Threads: 19
Joined: Apr 2018
Reputation:
0
Hello Erwin,
I have a SpaceLynk (V1.3 FW 2.7.0) that I would like to use as MQTT client and publish data to a cloud platform here in Belgium "Eniris". This device will serve only the purpose of MQTT client.
Could you or anyone assist me with the MQTT client script to be able to publish data in a certain json structured format?
The format should be like mentioned in the link below:
https://wiki.eniris.be/wiki/publicinform...3A%20MQTT/
In short something like this:
Topic = 'standart1/rp_one_m/T/userid/' and then in the data packet the following
Code: {
"time" : 1661506491 , --In Unix format
"extraTags" : {
"subId" : "T19"
},
"fields" : {
"temperature_degC" : 16.76 --this must be the value of the KNX object as a float datatype towards the broker)
}
}
I have tested the MQTT client script below and the connection with the broker is ok. And data is being published but not in the certain format sctructure their platform is expecting it.
Code: if not broker then
broker = 'mqtt.eniris.be'
username = 'xxx'
password = 'xxx'
socket = require('socket')
port = 1883
function multiply(mult)
return function(value)
local num = tonumber(value)
if num then
return num * mult
else
return value
end
end
end
-- topic to object map
mqtt_to_object = {
['Actual Temp/Hal A/S2'] = '4/0/1',
['Actual Temp/Hal B/S1'] = '4/0/2',
}
-- optional topic value conversion function
--mqtt_to_object_conv = {
-- ['in/topic1'] = multiply(100),
-- ['in/topic2'] = multiply(0.01),
--}
-- object to topic map
object_to_mqtt = {
['4/0/1'] = 'Actual Temp/Hal A/S2',
['4/0/2'] = 'Actual Temp/Hal B/S1',
}
datatypes = {}
grp.sender = 'mq'
require('socket')
for addr, _ in pairs(object_to_mqtt) do
local obj = grp.find(addr)
if obj then
datatypes[ addr ] = obj.datatype
end
end
mclient = require('mosquitto').new()
mclient.ON_CONNECT = function(res, ...)
log('mqtt connect status', res, ...)
if res then
for topic, _ in pairs(mqtt_to_object) do
mclient:subscribe(topic)
end
else
mclient:disconnect()
end
end
mclient.ON_MESSAGE = function(mid, topic, payload)
local addr = mqtt_to_object[ topic ]
if addr then
local fn = mqtt_to_object_conv[ topic ]
if fn then
payload = fn(payload)
end
grp.write(addr, payload)
end
end
mclient.ON_DISCONNECT = function(...)
log('mqtt disconnect', ...)
mclientfd = nil
end
function mconnect()
local status, rc, msg, fd
status, rc, msg = mclient:connect(broker, port)
if not status then
log('mqtt connect failed ' .. tostring(msg))
end
fd = mclient:socket()
if fd then
mclientfd = fd
end
end
--mclient:tls_insecure_set(true)
mclient:login_set(username, password or '')
mconnect()
function publishvalue(event)
-- message from us or client is not connected
if event.sender == 'mq' or not mclientfd then
return
end
local addr = event.dst
local dpt = datatypes[ addr ]
local topic = object_to_mqtt[ addr ]
-- unknown object
if not dpt or not topic then
return
end
local value = busdatatype.decode(event.datahex, dpt)
if value ~= nil then
if type(value) == 'boolean' then
value = value and 1 or 0
end
mclient:publish(topic, tostring(value))
end
end
lbclient = require('localbus').new(1)
lbclient:sethandler('groupwrite', publishvalue)
lbclientfd = socket.fdmaskset(lbclient:getfd(), 'r')
-- run timer every 5 seconds
timer = require('timerfd').new(5)
timerfd = socket.fdmaskset(timer:getfd(), 'r')
end
-- mqtt connected
if mclientfd then
mclientfdset = socket.fdmaskset(mclientfd, mclient:want_write() and 'rw' or 'r')
res, lbclientstat, timerstat, mclientstat =
socket.selectfds(10, lbclientfd, timerfd, mclientfdset)
-- mqtt not connected
else
res, lbclientstat, timerstat =
socket.selectfds(10, lbclientfd, timerfd)
end
if mclientstat then
if socket.fdmaskread(mclientstat) then
mclient:loop_read()
end
if socket.fdmaskwrite(mclientstat) then
mclient:loop_write()
end
end
if lbclientstat then
lbclient:step()
end
if timerstat then
-- clear armed timer
timer:read()
if mclientfd then
mclient:loop_misc()
else
mconnect()
end
end
Thank you in advance for your responce.
Regards
Posts: 7339
Threads: 41
Joined: Jun 2015
Reputation:
420
If you don't have a lot of frequent updates you can use event script to publish new values then disconnect.
Add to Common functions and change username/password:
Code: function mqttpublish(topic, data)
local broker = 'mqtt.eniris.be'
local username = 'xxx'
local password = 'xxx'
local port = 1883
local mqtt = require('mosquitto')
local client = mqtt.new()
if type(data) == 'table' then
data = require('json').encode(data)
end
client.ON_CONNECT = function(status, rc, msg)
if status then
log('mqtt cloud connected')
client:publish(topic, data)
else
log('mqtt cloud connect failed ' .. tostring(msg))
client:disconnect()
end
end
client.ON_PUBLISH = function()
log('disconnecting')
client:disconnect()
end
client:login_set(username, password)
local status, rc, msg = client:connect(broker, port)
if status then
client:loop_forever()
else
log('cloud connect failed: ' .. tostring(msg))
end
end
Event script example:
Code: topic = 'Actual Temp/Hal A/S2'
data = {
time = os.time(),
extraTags = {
subId = 'T19'
},
fields = {
temperature_degC = event.getvalue()
}
}
mqttpublish(topic, data)
Posts: 133
Threads: 19
Joined: Apr 2018
Reputation:
0
(26.08.2022, 10:38)admin Wrote: If you don't have a lot of frequent updates you can use event script to publish new values then disconnect.
Add to Common functions and change username/password:
Code: function mqttpublish(topic, data)
local broker = 'mqtt.eniris.be'
local username = 'xxx'
local password = 'xxx'
local port = 1883
local mqtt = require('mosquitto')
local client = mqtt.new()
if type(data) == 'table' then
data = require('json').encode(data)
end
client.ON_CONNECT = function(status, rc, msg)
if status then
log('mqtt cloud connected')
client:publish(topic, data)
else
log('mqtt cloud connect failed ' .. tostring(msg))
client:disconnect()
end
end
client.ON_PUBLISH = function()
log('disconnecting')
client:disconnect()
end
client:login_set(username, password)
local status, rc, msg = client:connect(broker, port)
if status then
client:loop_forever()
else
log('cloud connect failed: ' .. tostring(msg))
end
end
Event script example:
Code: topic = 'Actual Temp/Hal A/S2'
data = {
time = os.time(),
extraTags = {
subId = 'T19'
},
fields = {
temperature_degC = event.getvalue()
}
}
mqttpublish(topic, data)
Hello Admin,
Thank you for the quick reply.
Unfortunately I will have to publish around 200 objects and its not that they come in the bus very frequently.
Is there and option to publish data every one minute? Like adding a resident script with sleep internal of 1min?
Regards,
Posts: 7339
Threads: 41
Joined: Jun 2015
Reputation:
420
Are all 200 objects temperature sensors or are there different values that affect the JSON message format? Is extraTags = { subId = 'T19' } common for all messages or not?
Posts: 133
Threads: 19
Joined: Apr 2018
Reputation:
0
(26.08.2022, 11:06)admin Wrote: Are all 200 objects temperature sensors or are there different values that affect the JSON message format? Is extraTags = { subId = 'T19' } common for all messages or not?
Hello Admin,
The following things are to be published.
WaterMeter
Data:
standard1/rp_one_m/waterMetrics/<username>
{
"time": <UNIX timestamp>,
"extraTags": {
"subId": <string>
}
"fields": {
"absVolume_m3": <float>,
"flow_m3ph": <float>
}
}
Weather Station
Data:
standard1/rp_one_m/weatherMetrics/<username>
{
"time": <UNIX timestamp>,
"extraTags": {
"subId": <string>
}
"fields": {
"outdoorTemperature_degC": <float>,
"outdoorBrightness_lux": <float>,
"windSpeed_kmph": <float>
}
}
GasMeter
Data:
standard1/rp_one_m/gasMetrics/<username>
{
"time": <UNIX timestamp>,
"extraTags": {
"subId": <string>
}
"fields": {
"absVolume_Nm3": <float>
}
}
Errors & Messages:
standard1/autogen/alarms/<username>
{
"time": <UNIX timestamp>,
"extraTags": {
"subId": <string>
}
"fields": {
"alarmActive": <boolean>,
"msg": <srtring>,
"mbusStatus": <int> //zero = OK otherwise alarm
}
}
Thank you again for the great support.
Posts: 7339
Threads: 41
Joined: Jun 2015
Reputation:
420
You can create a scheduled script that runs every minute and publishes all values. Each message has to specified manually due to a variable format. Add as many addmessage calls as needed and change grp.getvalue addresses. The script will automatically disconnect once all messages are published.
Code: broker = 'mqtt.eniris.be'
username = 'xxx'
password = 'xxx'
port = 1883
messages = {}
time = os.time()
function addmessage(topic, data)
messages[ #messages + 1 ] = {
topic = topic,
data = require('json').encode(data),
}
end
addmessage('standard1/rp_one_m/waterMetrics/' .. username, {
time = time,
extraTags = {
subId = 'T19',
},
fields = {
absVolume_m3 = grp.getvalue('1/1/1'),
flow_m3ph = grp.getvalue('1/1/2'),
}
})
addmessage('standard1/rp_one_m/weatherMetrics/' .. username, {
time = time,
extraTags = {
subId = 'T19',
},
fields = {
outdoorTemperature_degC = grp.getvalue('1/1/3'),
outdoorBrightness_lux = grp.getvalue('1/1/4'),
windSpeed_kmph = grp.getvalue('1/1/5'),
}
})
addmessage('standard1/rp_one_m/gasMetrics/' .. username, {
time = time,
extraTags = {
subId = 'T19',
},
fields = {
absVolume_Nm3 = grp.getvalue('1/1/6'),
}
})
mqtt = require('mosquitto')
client = mqtt.new()
mids = {}
pubcount = 0
client.ON_CONNECT = function(status, rc, msg)
if status then
log('mqtt cloud connected')
for _, message in ipairs(messages) do
local mid = client:publish(message.topic, message.data)
if mid then
pubcount = pubcount + 1
mids[ mid ] = true
end
end
if pubcount == 0 then
client:disconnect()
end
else
log('mqtt cloud connect failed ' .. tostring(msg))
client:disconnect()
end
end
client.ON_PUBLISH = function(mid)
if mids[ mid ] then
mids[ mid ] = nil
pubcount = pubcount - 1
if pubcount == 0 then
log('disconnecting')
client:disconnect()
end
end
end
client:login_set(username, password)
status, rc, msg = client:connect(broker, port)
if status then
client:loop_forever()
else
log('cloud connect failed: ' .. tostring(msg))
end
|