AHU MODBUS TCP VALUE
Hi, I try to connect to Schneider-electric Homelynx and get the airflow from an IVP AHU ventilation unit with a climactix controller.
I need to compare two values in order to control a mixing valve.
The valve opens and closes until the two values are as equal as possible.
The value is to be retrieved from a Holding register with the address 4x0055 and 4x0056.
But unfortunately I do not get any values, it seems that it does not connect or I have typed the wrong code to get the air value correctly.
require('luamodbus') if not mb then    mb = luamodbus.tcp()    mb:open('192.168.201.53')    mb:connect() end mb:setdebug(true) openvalue =  grp.getvalue('6/3/1') tfvalue = mb:readinputregisters(54) ffvalue = mb:readinputregisters(55) mb:close() if tfvalue > ffvalue then  if openvalue < 220 then    openvalue = openvalue + 25  end end if ffvalue < ffvalue then  if openvalue > 25 then    openvalue = openvalue - 25  end end grp.write('6/3/1', openvalue)
I would be very grateful if you can help me with this problem
/Tommy
AHU MODBUS TCP VALUE - by Elmyran - 01.11.2018, 19:42
RE: AHU MODBUS TCP VALUE - by CHOUAIBOU - 01.11.2018, 21:10
RE: AHU MODBUS TCP VALUE - by admin - 02.11.2018, 08:17