This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Peak load limiter
#4
(07.12.2018, 21:19)Erwin van der Zwart Wrote: Hi,

I created this a while ago, maybe it could help you in your task.

Code:
-- Set adresses address_max = '1/1/2' address_hyst = '1/1/3' address_relais1 = '1/1/4' address_relais2 = '1/1/5' address_relais3 = '1/1/6' address_relais4 = '1/1/7' -- Get measured power power = event.getvalue() -- Get limit value max = grp.getvalue(address_max) -- Get Hysteresis hyst = grp.getvalue(address_hyst) -- Calculate floor value hyst_floor = math.floor((max - hyst) + 0.5) -- Check if chanels need to be turned on if power < hyst_floor then    -- get current state of relais 4  current_state_relais4 = grp.getvalue(address_relais4)  if current_state_relais4 == false then     grp.write(address_relais4, true)     -- exit script and after that cascade to chanel 3      return  end    -- get current state of relais 3  current_state_relais3 = grp.getvalue(address_relais3)  if current_state_relais3 == false then     grp.write(address_relais3, true)     -- exit script and after that cascade to chanel 2      return  end   -- get current state of relais 2  current_state_relais2 = grp.getvalue(address_relais2)  if current_state_relais2 == false then     grp.write(address_relais2, true)     -- exit script and after that cascade to chanel 1      return  end  -- get current state of relais 1  current_state_relais1 = grp.getvalue(address_relais1)  if current_state_relais1 == false then     grp.write(address_relais1, true)    -- exit script      return  end end -- Check if chanel 1 need to be turned off, after that cascade to chanel 2, then cascade to chanel 3 etcetera if power > max then  -- get current state of relais 1  current_state_relais1 = grp.getvalue(address_relais1)  if current_state_relais1 == true then    grp.write(address_relais1, false)  else      -- get current state of relais 2      current_state_relais2 = grp.getvalue(address_relais2)      if current_state_relais2 == true then        grp.write(address_relais2, false)    else           -- get current state of relais 3           current_state_relais3 = grp.getvalue(address_relais3)           if current_state_relais3 == true then             grp.write(address_relais3, false)         else               -- get current state of relais 4              current_state_relais4 = grp.getvalue(address_relais4)              if current_state_relais4 == true then                grp.write(address_relais4, false)              end           end      end  end end
BR,

Erwin

Thanks Erwin, this looks like it could work good as a startingpoint.
I'm new to LM5 and scripting, so trial and error will be nessesary, it's great to have some place to start.
Reply


Messages In This Thread
Peak load limiter - by tomnord - 07.12.2018, 15:41
RE: Peak load limiter - by buuuudzik - 07.12.2018, 17:13
RE: Peak load limiter - by tomnord - 07.12.2018, 21:25
RE: Peak load limiter - by Domoticatorino - 10.12.2018, 17:14
RE: Peak load limiter - by Domoticatorino - 12.12.2018, 20:09
RE: Peak load limiter - by BMA - 19.02.2021, 17:11
RE: Peak load limiter - by tomnord - 08.12.2018, 18:33

Forum Jump: