(21.06.2019, 07:17)Daniel. Wrote:(20.06.2019, 15:19)davidchispas Wrote: Thanks for your answer.
I just detected another problem ... I have to include 3 more ballasts to the installation. I start partial scanning and it does not detect them. I have to go back to look for them all and there they appear. The drawback is that I have to redirect everything again. It is normal?
If ballast is brand new, never addressed then partial will find them. If for some reason they were used once already and addressed then partial scan will not find them and new scan is needed.
The ballasts are new and with the partial scan does not find them. I get one to find me, if I loose the rest. He finds it as dev-64 keeping the rest of the ballasts. After. I release that ballast and connect another with the same procedure. But that second ballast does not find it anymore. The only way you can find them all is by performing the full scan.
(21.06.2019, 07:46)administración Wrote: Partial scan does not set short addresses. If you run addressing again then all ballasts will get new address assigned at random, that's how DALI works. If you can connect only one ballast to LM then you can set short address via a script. Then you can connect all ballasts and run partial scan.
Thanks for your answer. As they explain to me, I have to connect a ballast alone, start a partial scan and I would like to give it as dev-64. Then through a script a short address is assigned. After repeating the same procedure with the rest. Is it like that?
Can you provide me with the script?