This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

correct math for energy metering
#3
Hi Admin,

unfortunatelly such way not working for me :Sad

In attachment pictures with different datatypes I used with modbus LM reader... As I think my device - Gavazzi PM 340 gives out int32 format - as example 2341 (this is L1 phase voltage, real should be 234.1V). If I use float32 type I see something wrong...

But from documentation - I see smething not correct, in real received data should be divided by 10 not multiplied..

300001 0000h 2 V L1-N INT32 Value weight: Volt*10

What you can recommend?

Alex

.pdf   3-phase Modbus serial protocol EM and ET-rev.2.11.pdf (Size: 164.62 KB / Downloads: 16)
               