(02.03.2020, 15:33)Daniel. Wrote: If in profile value_multiplier": 0.1 works then you should do the same hereI figured out.
outside_te*0.1
I don't think the 65523 is a correct value. Usually such is send when No value or no sensor is on PLC side.
uint16 max value is 65535. If minus degrees, value is changed reversely.
65535-65523=12
12/10=1.2
1.2*-1=-1.2°C