01.04.2020, 11:57
No, I don't have and I believe none are required - is rather mechanical integration where script has to to open/close proportionally 0-10V valve (so scaling of valve opening) in relation to target temperatures. But I believe you are after some time target date measuring opening of the valve through duration Tx in relation of raising/dropping temperature
when I draw that on the board and tested on the valve 50% bypass/50% system - this opening is blending water that it drops 2degC from target within 2-4min, 80% system/20%bypass seems to be most effective and allows better control extending time of 2degC drop to fixed 5min
I hope that helps
when I draw that on the board and tested on the valve 50% bypass/50% system - this opening is blending water that it drops 2degC from target within 2-4min, 80% system/20%bypass seems to be most effective and allows better control extending time of 2degC drop to fixed 5min
I hope that helps