This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Question on Daikin DIII net protocol
#4
You need to modify the profile to allow raw value to be written to the control register.
Code:
{ "name": "on_off_status_00", "bus_datatype": "bool", "type": "inputregister", "address": 2000, "value_bitmask": 0x0001},
{ "name": "set_temp_status_00", "bus_datatype": "float16", "type": "inputregister", "address": 2002, "value_multiplier": 0.1, "units": "C" },
{ "name": "act_temp_status_00", "bus_datatype": "float16", "type": "inputregister", "address": 2004, "value_multiplier": 0.1, "units": "C" },
{ "name": "control_00", "bus_datatype": "uint16", "type": "register", "writable": 1, "write_only": true, "address": 2000 },
{ "name": "set_mode_00", "bus_datatype": "uint8", "type": "register", "writable": 1, "write_only": true, "address": 2001 },
{ "name": "set_temp_00", "bus_datatype": "float16", "type": "register", "writable": 1, "write_only": true, "value_multiplier": 0.1, "address": 2002, "units": "C"},

You will also need 3 objects: on/off (bool), fan direction (1 byte unsigned), fan volume (either bool or 1 byte unsigned depending on 2 or 3 step fan)
All objects must have the same tag assigned to them, then you need to create an event script attached to this tag.

Change group addresses as needed, 1/1/4 is the group that is mapped to control register of ModBus device.
Code:
onoff = grp.getvalue('1/1/1') and 1 or 0
direction = grp.getvalue('1/1/2')
volume = grp.getvalue('1/1/3')

if direction > 7 or direction == 5 then
  direction = 6
end

if type(volume) == 'boolean' then
  volume = volume and 1 or 5
elseif volume ~= 1 and volume ~= 3 and volume ~= 5 then
  volume = 1
end

value = bit.bor(
  onoff,
  bit.lshift(6, 4),
  bit.lshift(direction, 8),
  bit.lshift(volume, 12)
)

grp.update('1/1/4', value)