04.06.2020, 09:26
(04.06.2020, 08:00)thank you very muchwhen i tried this, i got error message on scripting - cannot open User script: No such file or directory stack traceback: why is this happening? admin Wrote: You need to modify the profile to allow raw value to be written to the control register.
Code:{ "name": "on_off_status_00", "bus_datatype": "bool", "type": "inputregister", "address": 2000, "value_bitmask": 0x0001}, { "name": "set_temp_status_00", "bus_datatype": "float16", "type": "inputregister", "address": 2002, "value_multiplier": 0.1, "units": "C" }, { "name": "act_temp_status_00", "bus_datatype": "float16", "type": "inputregister", "address": 2004, "value_multiplier": 0.1, "units": "C" }, { "name": "control_00", "bus_datatype": "uint16", "type": "register", "writable": 1, "write_only": true, "address": 2000 }, { "name": "set_mode_00", "bus_datatype": "uint8", "type": "register", "writable": 1, "write_only": true, "address": 2001 }, { "name": "set_temp_00", "bus_datatype": "float16", "type": "register", "writable": 1, "write_only": true, "value_multiplier": 0.1, "address": 2002, "units": "C"},
You will also need 3 objects: on/off (bool), fan direction (1 byte unsigned), fan volume (either bool or 1 byte unsigned depending on 2 or 3 step fan)
All objects must have the same tag assigned to them, then you need to create an event script attached to this tag.
Change group addresses as needed, 1/1/4 is the group that is mapped to control register of ModBus device.
Code:onoff = grp.getvalue('1/1/1') and 1 or 0 direction = grp.getvalue('1/1/2') volume = grp.getvalue('1/1/3') if direction > 7 or direction == 5 then direction = 6 end if type(volume) == 'boolean' then volume = volume and 1 or 5 elseif volume ~= 1 and volume ~= 3 and volume ~= 5 then volume = 1 end value = bit.bor( onoff, bit.lshift(6, 4), bit.lshift(direction, 8), bit.lshift(volume, 12) ) grp.update('1/1/4', value)