This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus TCP
#3
The first number before the address is function number: 1= coil, 3 = holding register, 4 = input register. The actual address might be in hex but you will have to check. You probably will have to subtract 1 from the address. Try reading register 0 or 1, it should contain the alarm status. But as Daniel said once you get addressing right using profile is more convenient.
Reply