30.10.2020, 12:22
I have used LM5 as a bacnet gateway and have not had any issues.
But now there are some text in a contract that i am wondering if the LM5 can do. Text is as follows:
Device should support BACnet Standardized Device Profile (Annex L).
It should be used BIBB's standard for B-BC på BACnet IP, or B-AAC or B-ASC on
BACnet MS/TP.
- BACnet units should be BTL-sertified. Should be documented with BACnet PICS, or a certicicat that confirms to BIBB`s.
-The unit should adoptble to exciting sites with changeble Bacnet device ID and UDP port.
-The unit should support BACnet encoding type ISO 10646 (UCS-2) / ANSI X3.4
(US-ASCII), that is changeble after installation. Equipment on BACnet IP should also suppport BBMD.
But now there are some text in a contract that i am wondering if the LM5 can do. Text is as follows:
Device should support BACnet Standardized Device Profile (Annex L).
It should be used BIBB's standard for B-BC på BACnet IP, or B-AAC or B-ASC on
BACnet MS/TP.
- BACnet units should be BTL-sertified. Should be documented with BACnet PICS, or a certicicat that confirms to BIBB`s.
-The unit should adoptble to exciting sites with changeble Bacnet device ID and UDP port.
-The unit should support BACnet encoding type ISO 10646 (UCS-2) / ANSI X3.4
(US-ASCII), that is changeble after installation. Equipment on BACnet IP should also suppport BBMD.