This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

limits when LM as Modbus TCP slave
#3
(25.11.2020, 10:22)admin Wrote: 125 registers is ModBus standard limit. But it only applies to a single request. If you want to read/write more then send several requests.
thanks! but what about addressing with multiple requests? will the address of the first register in the second request be 0 again? oh, understand Smile addressing continues
Reply