(25.11.2020, 10:22)admin Wrote: 125 registers is ModBus standard limit. But it only applies to a single request. If you want to read/write more then send several requests.thanks! but what about addressing with multiple requests? will the address of the first register in the second request be 0 again? oh, understand addressing continues
limits when LM as Modbus TCP slave
|
|