(11.12.2020, 10:08)Daniel. Wrote: If you still have the tx error then it is most likely broken interface.
Just to clarify, the partial scan is a scan which will find only devices which have no short address. If a ballast was already used elsewhere and programmed partial scan will not find it. DALI app for canX dali has more options for this.
Yes, I understand the partial scan, but doing a full search already assigns the short addresses to the ballasts again.
I'll do the test by substituting the LM for the one on the way.
The CANx gateways are much better, it even gives us states and it is a great work that saves. If I could replace the Logic M. with a CANX one and not have to look for the ballasts again it would be great, but this I understand that it cannot be done.