This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus TCP connection datakom d-200 mk2
#6
It's strange that you get "invalid data" first. This might indicate that the device is faulty.
I've made a mistake in the previous test script so it does not log communication in case of an error. Run this and post what you get in Logs tab:
Code:
if not mb then
  require('luamodbus')
  mb = luamodbus.tcp()

  mb:setresponsetimeout(5)
  mb:open('10.36.0.25', 502)

  res, err = mb:connect()
  if res then
    
    buffer = {}
    mb:setdebug(function(msg)
      buffer[ #buffer + 1 ] = msg
    end)
  else
    log('modbus connect failed ' .. tostring(err))
    mb:close()
    mb = nil
  end
end

if mb then
  reg10240, reg10241, reg10242, reg10243, reg10244, reg10245, reg10246, reg10247 = mb:readregisters(10240, 8)
  
  if reg10240 then
    mains_l1_voltage = reg10240 / 10
    mains_l2_voltage = reg10242 / 10
    mains_l3_voltage = reg10244 / 10
    genset_l1_voltage = reg10246 / 10
    log('voltage values', mains_l1_voltage, mains_l2_voltage, mains_l3_voltage, genset_l1_voltage)
  else
    log('modbus read failed ' .. tostring(reg10241))
    mb:close()
    mb = nil
  end

  log(table.concat(buffer))
  buffer = {}
end