This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus TCP connection datakom d-200 mk2
#8
The illegal data error seems to come from the device sending some extra byte when it should not. Unfortunately it's hard to tell why the connection stops working. Try this test script which discards any stale data before reading.
Code:
if not mb then   require('luamodbus')   mb = luamodbus.tcp()   mb:setresponsetimeout(5)   mb:open('10.36.0.25', 502)   res, err = mb:connect()   if res then          buffer = {}     mb:setdebug(function(msg)       buffer[ #buffer + 1 ] = msg     end)   else     log('modbus connect failed ' .. tostring(err))     mb:close()     mb = nil   end end if mb then   mb:flush()   reg10240, reg10241, reg10242, reg10243, reg10244, reg10245, reg10246, reg10247 = mb:readregisters(10240, 8)      if reg10240 then     mains_l1_voltage = reg10240 / 10     mains_l2_voltage = reg10242 / 10     mains_l3_voltage = reg10244 / 10     genset_l1_voltage = reg10246 / 10     log('voltage values', mains_l1_voltage, mains_l2_voltage, mains_l3_voltage, genset_l1_voltage)   else     log('modbus read failed ' .. tostring(reg10241))     mb:close()     mb = nil   end   log(table.concat(buffer))   buffer = {} end
Reply


Messages In This Thread
RE: Modbus TCP connection datakom d-200 mk2 - by admin - 25.02.2021, 15:25