Conference room with 2 partition walls
There used to be a universal script but I can't find it.
Here's a working solution for any data type. Tag all input objects with the same tag and add an event script to it. Change group addresses as needed. You might need to remove two "not" statements before grp.getvalue depending on how open/closed status works. Right now it assumed that true means that the wall is closed.
inputs = { '32/1/1', '32/1/2', '32/1/3' } status = { '32/1/7', '32/1/8' } outputs = { '32/1/4', '32/1/5', '32/1/6' } for i, addr in ipairs(inputs) do   if addr == event.dst then     index = i   end end value = event.getvalue() writes = {} writes[ index ] = true open12 = not grp.getvalue(status[ 1 ]) open23 = not grp.getvalue(status[ 2 ]) if index == 1 then   if open12 then     writes[ 2 ] = true     writes[ 3 ] = open23   end elseif index == 2 then   writes[ 1 ] = open12   writes[ 3 ] = open23 elseif index == 3 then   if open23 then     writes[ 2 ] = true     writes[ 1 ] = open12   end end for i, addr in ipairs(outputs) do   if writes[ i ] then     grp.write(addr, value)   end end
RE: Conference room with 2 partition walls - by admin - 11.05.2021, 08:02