11.06.2021, 08:27
(11.06.2021, 08:11)admin Wrote: If min/max is common for all objects then you can use the same percentage formula after calculating the average by dividing the sum by the total number of objects.
If min/max is different then you can convert each value to a percentage and then calculate the average value from that.
Example:
Supply Vav 1: 200 m3h
Supply Vav 2: 300 m3h
Supply Vav 3: 400 m3h
Total airflow 900 m3h.
The extract Vav has min 100 m3h and 1000 m3h max.
Calculation show that this gives an output 90 % to the extract vav which will then open to 900 m3h.
So my wish is that using the "sum", putting the "sum" into the Range between min/max. And then calculate a % ouput in that range.