PID in FB editor
I get no output at all. I also removed the PID in FB editor and tried with this info https://openrb.com/example-pid-thermostat-with-lm2/
added the PID to the User Libraries
PID = {   -- default params   defaults = {     -- invert algorithm, used for cooling     inverted = true,     -- minimum output value     min = 0,     -- maximum output value     max = 100,     -- proportional gain     kp = 0.25,     -- integral gain     ki = 0.42,     -- derivative gain     kd = 0.1,   } } -- PID init, returns new PID object function PID:init(params)   local n = setmetatable({}, { __index = PID })   local k, v   -- set user parameters   n.params = params   -- copy parameters that are set by user   for k, v in pairs(PID.defaults) do     if n.params[ k ] == nil then       n.params[ k ] = v     end   end   -- reverse gains in inverted mode   if n.params.inverted then     n.params.kp = -n.params.kp     n.params.ki = -n.params.ki     n.params.kd = -n.params.kd   end   return n end -- resets algorithm on init or a switch back from manual mode function PID:reset()   -- previous value   self.previous = grp.getvalue(self.params.current)   -- reset iterm   self.iterm = 0   -- last running time   self.lasttime = os.time()   -- clamp iterm   self:clampiterm() end -- clamps iterm value function PID:clampiterm()   self.iterm = math.max(self.iterm, self.params.min)   self.iterm = math.min(self.iterm, self.params.max) end -- clamp and set new output value function PID:setoutput()   local t, object, value   self.output = math.max(self.output, self.params.min)   self.output = math.min(self.output, self.params.max)   value = math.floor(self.output)   local t = type(self.params.output)   -- write to output if object is set   if t == 'string' or t == 'table' then     if t == 'string' then       self.params.output = { self.params.output }     end     for _, output in ipairs(self.params.output) do       grp.write(output, value, dt.scale)     end   end end -- algorithm step, returns nil when disabled or no action is required, output value otherwise function PID:run()   local result   -- get manual mode status   local manual = self.params.manual and grp.getvalue(self.params.manual) or false   -- in manual mode, do nothing   if manual then     self.running = false   -- not in manual, check if reset is required after switching on   elseif not self.running then     self:reset()     self.running = true   end   -- compute new value if not in manual mode   if self.running then     -- get time between previous and current call     local now = os.time()     self.deltatime = now - self.lasttime     self.lasttime = now     -- run if previous call was at least 1 second ago     if self.deltatime > 0 then       result = self:compute()     end   end   return result end -- computes new output value function PID:compute()   local current, setpoint, deltasc, deltain, output   -- get input values   current = grp.getvalue(self.params.current)   setpoint = grp.getvalue(self.params.setpoint)   -- delta between setpoint and current   deltasc = setpoint - current   -- calculate new iterm   self.iterm = self.iterm + self.params.ki * self.deltatime * deltasc   self:clampiterm()   -- delta between current and previous value   deltain = current - self.previous   -- calculate output value   self.output = self.params.kp * deltasc + self.iterm   self.output = self.output - self.params.kd / self.deltatime * deltain   -- write to output   self:setoutput()   -- save previous value   self.previous = current   return self.output end
and added the following script to the Resident Scripts
-- init pid algorithm if not p then   p = PID:init({     current = '2/2/8',     setpoint = '32/1/58',     output = '32/1/58'   }) end -- run algorithm p:run()
But my output stays 0.
I want to control a 3 way valve at the output to get a stable temperature at the valve for cooling.
Current is the measured flow temperature
Setpoint the requested flow temperature
and Output is 0-100% (0-10V)
PID in FB editor - by KoBra - 17.06.2021, 12:42
RE: PID in FB editor - by Daniel - 17.06.2021, 14:06
RE: PID in FB editor - by KoBra - 17.06.2021, 16:34
RE: PID in FB editor - by Daniel - 18.06.2021, 07:46
RE: PID in FB editor - by KoBra - 18.06.2021, 09:21
