@tthamm, do you have the communication working via read test? The device documentation is very clear, you only have to convert addresses from hex to decimal for testing.
Try reading Active import with these settings:
- Function: Holding register (#3)
- Address: 20480
- Data type: uint64
- Read swap: Word
The read value is in 0.01KWh. If the value is incorrect then try using different read swap modes.