This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus error CRC
#2
This usually means there's a problem on the physical bus level.
Make sure that parity and stop bits settings are correct. Check if GND is connected between LM and the Modbus device. A termination resistor might be needed as well. Also check AC polarity on both LM and the Modbus device. There was a report where one of the power supplies has AC polarity connected in reverse and this caused communication issues.
Reply


Messages In This Thread
Modbus error CRC - by CristianAgata - 19.02.2022, 14:30
RE: Modbus error CRC - by admin - 21.02.2022, 07:10