Calculate value to procent
(11.06.2021, 08:27)Tokatubs Wrote:
(11.06.2021, 08:11)admin Wrote: If min/max is common for all objects then you can use the same percentage formula after calculating the average by dividing the sum by the total number of objects.
If min/max is different then you can convert each value to a percentage and then calculate the average value from that.
Example:
Supply Vav 1: 200 m3h
Supply Vav 2: 300 m3h
Supply Vav 3: 400 m3h
Total airflow 900 m3h.
The extract Vav has min 100 m3h and 1000 m3h max.
Calculation show that this gives an output 90 % to the extract vav which will then open to 900 m3h.
So my wish is that using the "sum", putting the "sum" into the Range between min/max. And then calculate a % ouput in that range.
Hello. See if this might help. I'm using this to sum up supply dampers for controlling one exctract damper
value1 = grp.getvalue('203_VAV_T_PV1') value2 = grp.getvalue('202_VAV_T_PV1') valueTot = value1+value2 function VAVsum(totalIN, Vmin, Vmax)   local valueM3H = (totalIN * 3600)   local value = ((valueM3H - Vmin)/(Vmax - Vmin))*100   local result       if value < 0 then         result = 0       elseif value > 100 then         result = 100       else         result = math.floor(value)         end     return result end     valueOut=VAVsum(valueTot, 190, 370) log(valueOut) grp.write('201_VAV_A_SP', valueOut)
Calculate value to procent - by Tokatubs - 10.06.2021, 18:55
RE: Calculate value to procent - by Tokatubs - 11.06.2021, 08:05
RE: Calculate value to procent - by admin - 11.06.2021, 08:11
RE: Calculate value to procent - by Tokatubs - 11.06.2021, 08:27
RE: Calculate value to procent - by tomnord - 07.05.2022, 14:29
RE: Calculate value to procent - by admin - 02.05.2022, 13:08