02.06.2022, 13:03
(02.06.2022, 10:31)admin Wrote: You can try swapping GW 2 and 3 and see if it's still not working correctly. If it does not then maybe the hardware is faulty and must be replaced.
As for ballasts this can only be checked with an oscilloscope on the DALI line near the gateway. Then standard says that high level is from 9.5V to 22.5V and low level is below 6.5V. Value between 6.5V and 9.5V is undefined.
I have exchanged GW 2 and 3. The same equipment has disconnected again. So it could just be a hardware problem?