08.06.2022, 08:22
(This post was last modified: 08.06.2022, 08:24 by davidchispas.)
(03.06.2022, 10:21)admin Wrote: I was referring to a physical hardware issue not firmware. But if you are saying that two devices are affected there might be something wrong with the installation. Start by checking the cables. Green LED on the gateway will blink when a new CAN message is received. Pressing the programming button twice will produce a message that can be used to check the communication. First check communication between GW2 and GW3. Then use CANx app monitor to check that messages are coming to LM. Also try a different line termination mode.
I have finally done the FW update to the devices before replacing the wiring. After 24 hours without incident, the problem seems to be solved.
I take this opportunity to ask you about the functioning of the ballast states and if it is possible to improve it in the future. When the on/off command is sent, the % status is momentary, but when working with percentage or regulation orders, this status is delayed enough, interfering with the user's operation. For example, when we have a button and we want to increase/decrease the intensity, with one press it would increase and with another it should decrease, but since the state is delayed so much, the order of direction does not change, so the value would continue to increase.