This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

problem with logical script
#1
Greetings

I have problems with the script that I am attaching does not work, it only works if I stop it and restart it.
some of the group addresses have multiple tags could this be the problem?

Code:
-- POSSIBILITA DI FARE AND , OR , O MEDIE ASSEGANDO TAG PER IDENTIFICARE OPERANDI E METTERE USCITA SU INDIRIZZO DI GRUPPO if not client then     -- each group has 3 fields:   -- tag - status object tag   -- output - status output object   -- mode - calculate mode (and/or/avg)   groups = {     { tag = 'ORALM', output = '32/1/200', mode = 'or' },     { tag = 'ORINS', output = '32/1/201', mode = 'or' },     { tag = 'ORP', output = '0/2/100', mode = 'or' },     { tag = 'ORMOV', output = '32/2/5', mode = 'or' },     { tag = 'ORPN', output = '32/2/6', mode = 'or' },     { tag = 'ORPS', output = '32/2/7', mode = 'or' },     { tag = 'ERRV', output = '4/6/21', mode = 'and' },          --{ tag = 'my_group_avg', output = '1/1/5', mode = 'avg' },   }   -- time to wait between last telegram from any status in group and update   updatedelay = 0.5   -- object value cache   values = {}   -- object datatype cache   datatypes = {}   -- send update only when value changes   grp.checkupdate = function(alias, value)     if values[ alias ] ~= value then       grp.update(alias, value)     end   end   calc = {}   -- AVERAGE value   calc['avg'] = function(group)     local result, count, value = 0, 0     for _, address in ipairs(group.objects) do       value = values[ address ]       -- number must be in [0..100] range       if type(value) == 'number' then         result = result + value         count = count + 1       -- boolean true is 100%, false is 0%       elseif type(value) == 'boolean' then         if toboolean(value) then           result = result + 100         end         count = count + 1       end     end     if count > 0 then       result = math.floor(result / count + 0.5)       grp.checkupdate(group.output, result)     end   end   -- AND gate   calc['and'] = function(group)     local result = true     for _, address in ipairs(group.objects) do       result = result and toboolean(values[ address ])     end     grp.checkupdate(group.output, result)   end   -- OR gate   calc['or'] = function(group)     local result = false     for _, address in ipairs(group.objects) do       result = result or toboolean(values[ address ])     end     grp.checkupdate(group.output, result)   end   -- prepare each group   for _, group in ipairs(groups) do     object = grp.find(group.output)     -- cache output status object value and datatype     values[ object.address ] = object.data     datatypes[ object.address ] = object.datatype     group.output = object.address     -- group input status object list     group.objects = {}     -- find all status objects and cache values and datatypes     objects = grp.tag(group.tag)     for _, object in ipairs(objects) do       values[ object.address ] = object.data       datatypes[ object.address ] = object.datatype       table.insert(group.objects, object.address)     end     -- force update on first run     group.timer = 0     -- calc function reference     group.fn = calc[ group.mode ]   end   -- handle group writes   function eventhandler(event)     local dst, datatype     dst = event.dst     datatype = datatypes[ event.dst ]     -- unknown object, stop     if not datatype then       return     end     values[ dst ] = dpt.decode(event.datahex, datatype)     -- check if any group needs to be updated     for _, group in ipairs(groups) do       for _, address in ipairs(group.objects) do         if address == dst then           group.timer = updatedelay         end       end     end   end   require('genohm-scada.eibdgm')   client = eibdgm:new({ timeout = 0.25 })   client:sethandler('groupwrite', eventhandler) end tsec, tusec = os.microtime() client:step() delta = os.udifftime(tsec, tusec) -- check if any group has an active timer for _, group in ipairs(groups) do   timer = group.timer   if timer then     timer = timer - delta     -- timer expired, run calc function     if timer <= 0 then       group.fn(group)       timer = nil     end     group.timer = timer   end end

Thank you
Reply


Messages In This Thread
problem with logical script - by Frank68 - 16.06.2022, 08:34
RE: problem with logical script - by admin - 16.06.2022, 08:55
RE: problem with logical script - by Frank68 - 29.06.2022, 08:14
RE: problem with logical script - by admin - 29.06.2022, 08:14
RE: problem with logical script - by admin - 08.11.2022, 08:16

Forum Jump: