Do you have any other scripts accessing the same port? Only a single script can access the port at any time.
Also the reading part does not seem correct. Usually the data should be read one byte at a time, at least to the point where a message starting point is found. But this all depends on how the protocol is designed. Do you have a protocol description for this device?