23.09.2022, 09:44
(This post was last modified: 23.09.2022, 09:53 by davidchispas.)
(23.09.2022, 09:07)Daniel Wrote: Can you check bus voltage?
There are 4 KNX devices to a 160mA source, I temporarily made a change to a 640mA one with the same errors.
On the other hand and seeing the first answer of this thread. In this installation I have 2 LM installed on the same data network to different KNX Buses. In the elevator LM I have the filter table enabled and I only accept one knx address, which is the only one they share. But reviewing the parameters I have seen that they have the same multicast IP.
Will it have something to do with it?
(23.09.2022, 09:44)davidchispas Wrote:(23.09.2022, 09:07)Daniel Wrote: Can you check bus voltage?
There are 4 KNX devices to a 160mA source, I temporarily made a change to a 640mA one with the same errors.
On the other hand and seeing the first answer of this thread. In this installation I have 2 LM installed on the same data network to different KNX Buses. In the elevator LM I have the filter table enabled and I only accept one knx address, which is the only one they share. But reviewing the parameters I have seen that they have the same multicast IP.
Will it have something to do with it?
I just checked but changing the address does not work sending this knx object